Electrical first fix help

Options
  • 13-09-2015 1:34am
    #1
    Registered Users Posts: 8


    If an Electrician could help me out with a query Id greatly appreciate it.

    I am doing first fix electricials at the moment. The metal back boxes being installed for switches/sockets are 12.5mm too shallow meaning there will be a gap between the back boxes and the faces of switches/sockets.
    The boxes are 50mm and I am putting a 62.m insulated slab on the external walls. Is the gap acceptable under current regulations??

    I have been told by someone that the gap will create a fire hazzsrd as if a wire sparks the insulation could catch fire.

    Thank you


Comments

  • Registered Users Posts: 907 ✭✭✭rampantbunny


    Buddy15 wrote: »
    If an Electrician could help me out with a query Id greatly appreciate it.

    I am doing first fix electricials at the moment. The metal back boxes being installed for switches/sockets are 12.5mm too shallow meaning there will be a gap between the back boxes and the faces of switches/sockets.
    The boxes are 50mm and I am putting a 62.m insulated slab on the external walls. Is the gap acceptable under current regulations??

    I have been told by someone that the gap will create a fire hazzsrd as if a wire sparks the insulation could catch fire.

    Thank you

    Hi Buddy..I can't answer your question but you might have better luck in the Electrical forum. You could ask a mod to move this post there.


  • Registered Users Posts: 8 Buddy15


    Ok thank you I will try that


  • Moderators, Society & Culture Moderators Posts: 39,484 Mod ✭✭✭✭Gumbo


    Who is supervising the build?
    Why is your registered electrical contractor not making these decisions?


  • Boards.ie Employee Posts: 12,597 ✭✭✭✭✭Boards.ie: Niamh
    Boards.ie Community Manager


    Moved from Construction & Planning.


  • Registered Users Posts: 8 Buddy15


    hi Kceire, i have asked my engineer but he is putting it back on the electrician. The electrician has said there is no problem with it and that it happens in lots of houses. The person who told me this gap was not permitted was saying this based on an engineer in another property making the electrician change boxes to make sure there was no gap.


  • Advertisement
  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Buddy15 wrote: »
    If an Electrician could help me out with a query Id greatly appreciate it.

    I am doing first fix electricials at the moment. The metal back boxes being installed for switches/sockets are 12.5mm too shallow meaning there will be a gap between the back boxes and the faces of switches/sockets.
    The boxes are 50mm and I am putting a 62.m insulated slab on the external walls. Is the gap acceptable under current regulations??

    I have been told by someone that the gap will create a fire hazzsrd as if a wire sparks the insulation could catch fire.

    Thank you

    Put squares of plasterboard as spacers behind the 50mm switch boxes, and screw the boxes to the wall through them.


  • Registered Users Posts: 2,039 ✭✭✭Cerco


    Bruthal wrote: »
    Put squares of plasterboard as spacers behind the 50mm switch boxes, and screw the boxes to the wall through them.

    So simple and yet so effective. Clever solution.