Immersion thermostat keeps needing reset

Options
  • 16-01-2016 2:14pm
    #1
    Registered Users Posts: 45


    Hi,

    My immersion boiler thermostat keeps needing the reset button pressed.

    I got a new boiler, it has 3-terminals

    B & S & T

    One end of the thermostat is connected the T terminal and the other to the neutral connection of the wall switch, the NOUT connection.

    The B terminal is connected to the L1 of the wall switch
    The S terminal is connected to the L2 of the wall switch

    The common L is connected to the LOUT of the wall switch.

    I suppose my main question is if I have the thermostat connected correctly by connecting it to NEUTRAL ?

    Thanks.


Comments

  • Registered Users Posts: 2,637 ✭✭✭brightspark


    Is the immersion heated by another source (oil or gas central heating?)

    Is the immersion heater cap being covered with clothing etc?


  • Registered Users Posts: 45 VidaLoca


    Is the immersion heated by another source (oil or gas central heating?)

    Is the immersion heater cap being covered with clothing etc?

    At the moment its only being heated by the electric. Nothing in the press at all.


  • Registered Users Posts: 2,637 ✭✭✭brightspark


    What reset button needs to be pressed?


  • Registered Users Posts: 45 VidaLoca


    What reset button needs to be pressed?


    The little one on the thermostat, it works great for about 4 hours and then needs to be reset to start again.


  • Registered Users Posts: 2,637 ✭✭✭brightspark


    How hot is the water?

    What is the temperature control stat set to?


  • Advertisement
  • Registered Users Posts: 45 VidaLoca


    How hot is the water?

    What is the temperature control stat set to?

    65'C


  • Registered Users Posts: 45 VidaLoca


    How hot is the water?

    What is the temperature control stat set to?

    65'C

    You think it all sounds correct with the Neutral connected to the thermostat ?

    Could it be just faulty ?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    There are a few possibilities:
    1) The high temperature cut out may be faulty
    2) The stat may be faulty allowing the water to overheat (you could try turning it down)
    3) the immersion heating element may be on the way out. I have seen this cause the water temperature to rise rapidly before the stat turns it off.


  • Registered Users Posts: 45 VidaLoca


    2011 wrote: »
    There are a few possibilities:
    1) The high temperature cut out may be faulty
    2) The stat may be faulty allowing the water to overheat (you could try turning it down)
    3) the immersion heating element may be on the way out. I have seen this cause the water temperature to rise rapidly before the stat turns it off.

    Nice one , Ill try lowering the temperature on it.

    Its all new out of the box only 2 weeks.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    If the water never gets to what would appear to be too hot then #1 above is the most likley IMHO.


  • Advertisement
  • Registered Users Posts: 4,745 ✭✭✭meercat


    Any chance of a pic.
    I'm a bit confused by your original post


  • Registered Users Posts: 45 VidaLoca


    meercat wrote: »
    Any chance of a pic.
    I'm a bit confused by your original post

    can't, I'm only new


  • Registered Users Posts: 45 VidaLoca


    Hi,

    A quick update.

    I left the cap (the round metal) off the boiler over the weekend and the thermostat didn't need resetting once.


  • Registered Users Posts: 736 ✭✭✭jsd1004


    Dodgy thermostat. Get one without the reset button. Had the same problem.. replaced mine with a blue one without the reset button and all good.


  • Registered Users Posts: 2,637 ✭✭✭brightspark


    jsd1004 wrote: »
    Dodgy thermostat. Get one without the reset button. Had the same problem.. replaced mine with a blue one without the reset button and all good.


    Dangerous advice! :eek:

    The cut-off stats are there for safety, so not "all good" :rolleyes:


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    There is also the slight possibility of being incorrectly connected at the switch, which can have the immersion stat bypassed. Unusual though, but possible.


  • Registered Users Posts: 45 VidaLoca


    Bruthal wrote: »
    There is also the slight possibility of being incorrectly connected at the switch, which can have the immersion stat bypassed. Unusual though, but possible.

    How would that happen ?

    It was all good the last few days but neded to be reset again today. Im thinking it my be a faulty one.

    I might replace it and see how that goes.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    VidaLoca wrote: »
    How would that happen ?

    It was all good the last few days but neded to be reset again today. Im thinking it my be a faulty one.

    I might replace it and see how that goes.

    Neutral mixed up with bath or sink wires which then leaves the immersion temperature control stat out of the circuit depending on selector switch position.

    Very unlikely the cause here though. Probably the overheat stat cutting out too early.


  • Registered Users Posts: 45 VidaLoca


    Bruthal wrote: »
    Neutral mixed up with bath or sink wires which then leaves the immersion temperature control stat out of the circuit depending on selector switch position.

    Very unlikely the cause here though. Probably the overheat stat cutting out too early.

    I only have the single Neutral going into one side of the thermostat . The live for bath goes to the "B" post on the boiler and the other live for the sink goes to the "S" post on the boiler.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    VidaLoca wrote: »
    I only have the single Neutral going into one side of the thermostat . The live for bath goes to the "B" post on the boiler and the other live for the sink goes to the "S" post on the boiler.

    Like I was saying, its unliky to be wrong. It's at the switch the mistake is possible. But very unliky.

    The overheat cutout is likely operating too early.

    Other causes are air trapped at top of immersion element, again very unlikely. Or a limescale covered element if its in a decent amount of time.


  • Advertisement
  • Registered Users Posts: 736 ✭✭✭jsd1004


    Bruthal wrote: »
    Like I was saying, its unliky to be wrong. It's at the switch the mistake is possible. But very unliky.

    The overheat cutout is likely operating too early.

    Other causes are air trapped at top of immersion element, again very unlikely. Or a limescale covered element if its in a decent amount of time.

    My house has still not burnt down. I still think the dodgy thermostat caused the problem! Water nice and warm..No resetting required


  • Registered Users Posts: 736 ✭✭✭jsd1004


    Dangerous advice! :eek:

    The cut-off stats are there for safety, so not "all good" :rolleyes:

    I certify european CE equipment so if you regard it as unsafe maybe you might explain to me why? I am a real engineer by the way!


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    jsd1004 wrote: »
    I certify european CE equipment so if you regard it as unsafe maybe you might explain to me why? I am a real engineer by the way!

    The high temperature cut out stats are safety devices. If fitted with a reset then operation of the device has to be investigated (rather than automatically resetting) which mitigates the risk of the underlying problem developing into something more serious.

    By the way this was CE marked by an engineer:

    MeltedSwitchFuse.jpg


  • Registered Users Posts: 2,637 ✭✭✭brightspark


    jsd1004 wrote: »
    I certify european CE equipment so if you regard it as unsafe maybe you might explain to me why? I am a real engineer by the way!



    If you are a real engineer I shouldn't have to explain why modifying equipment and bypassing safety devices is unsafe.

    And do you really think that it's ok for unqualified people to modify equipment?


  • Registered Users Posts: 736 ✭✭✭jsd1004


    If you are a real engineer I shouldn't have to explain why modifying equipment and bypassing safety devices is unsafe.

    And do you really think that it's ok for unqualified people to modify equipment?

    But I never advocated modifying or bypassing anything. The alternative thermostat has a built in high temp cut out it just does not have a reset option..


  • Registered Users Posts: 736 ✭✭✭jsd1004


    2011 wrote: »
    The high temperature cut out stats are safety devices. If fitted with a reset then operation of the device has to be investigated (rather than automatically resetting) which mitigates the risk of the underlying problem developing into something more serious.

    By the way this was CE marked by an engineer:

    MeltedSwitchFuse.jpg[/quote

    Yes. But the problem is 90% caused by a dodgy thermostat that is activating the high temp cut out unnecessarily. The easy solution is to change the stat to one with an integrated high end cut out and see if it solves the problem. A cheap and easy option.


  • Registered Users Posts: 2,637 ✭✭✭brightspark


    jsd1004 wrote: »
    But I never advocated modifying or bypassing anything. The alternative thermostat has a built in high temp cut out it just does not have a reset option..

    What alternative did you suggest?
    jsd1004 Dodgy thermostat. Get one without the reset button. Had the same problem.. replaced mine with a blue one without the reset button and all good.

    You do know that not all blue ones have a high temp cut out?

    E.g. The ones linked below

    https://www.tlc-direct.co.uk/Main_Index/Wiring_Accessories_Menu_Index/Therostats_All/Immersion_Heaters_2/index.html

    And a high temp cut off that doesn't need to be reset? How would that be safe?


  • Registered Users Posts: 4,745 ✭✭✭meercat


    Point 3 in link below.

    I believe some fatalities may have been prevented if an overheat trip were in place.

    As others have pointed out earlier
    It's never a good idea to bypass a safety device.

    http://www.hse.gov.uk/services/localgovernment/hotwatersystems.htm