Astec 49DV Fault

Options
  • 09-02-2016 9:59pm
    #1
    Registered Users Posts: 148 ✭✭


    Hi,

    My Astec 49DV has been going off in the last two days for no apparent reason. It's not showing any fault in the display and it's the same zone that's going off.

    I have put it into engineering mode and pressed 11 to see if it showed any faults there but it shows everything working.

    Any ideas on what it can be?

    Thanks.


«1

Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Probably a faulty sensor or contact on that zone. What does it show on the screen when you disarm it after an activation.
    In engineer press 10 and go back through the log.


  • Registered Users Posts: 148 ✭✭Ivan E


    Thanks Koolkid for the reply.

    It says Zone 1 contact. So I know what's setting it off. Just not sure why. I was assuming maybe the contact is faulty but i would have thought I'd see an error on the panel indicating a fault.

    Going through the log I also see this:

    2 set F3 telecom
    1 set FTC
    1 set F6

    Not sure if that means anything or just that it went off and made the call.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    FTC is Fail To Communicate . Meaning the call was not made successfully.
    A faulty contact or sensor will not show up in open zones etc as the fault is intermittent its ok when you set the alarm but the alarm may activate a while after being set.
    If the log is saying zone 1 contact all the time there is a faulty device on connection on that zone.


  • Registered Users Posts: 148 ✭✭Ivan E


    So just replace the contact then?

    I presume that's straight forward enough. That a generic contact (ebay) will do and I just replace the existing one with that?

    Do I need to completely shut down the alarm to replace it if that's the case?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    To use a standard contact with Astec you need to wire a 680ohm resistor across the contact. 340 ohm if its an entry zone.
    Is there only one contact on that zone? I would also be checking all connections & joins on that loop.
    No need to power down the system when replacing a contact.


  • Advertisement
  • Registered Users Posts: 148 ✭✭Ivan E


    Yeah, I think there's only one contact on the zone and yes it's an entry zone. The contact was put in around 3-4 years ago by someone who knew what he was doing.

    So I am just trying to gauge is it something i can do myself easily. I managed to follow the instructions in here on how to replace the battery previously. Hoping this is as straight forward. I was thinking I could just reuse the existing resistor there assuming there is one. But I suppose that could easily be the source of the issue too.

    Steps then would:
    1. Unscrew existing contact.
    2. Connect the new contact the same way.
    3. Check any other connections on that route.

    or is there something else I need to watch for that could do damage?


  • Registered Users Posts: 148 ✭✭Ivan E


    Yeah, I think there's only one contact on the zone and yes it's an entry zone. The contact was put in around 3-4 years ago by someone who knew what he was doing.

    So I am just trying to gauge is it something i can do myself easily. I managed to follow the instructions in here on how to replace the battery previously. Hoping this is as straight forward. I was thinking I could just reuse the existing resistor there assuming there is one. But I suppose that could easily be the source of the issue too.

    Steps then would:
    1. Unscrew existing contact.
    2. Connect the new contact the same way.
    3. Check any other connections on that route.

    or is there something else I need to watch for that could do damage?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Pretty much yeah.
    If the existing contact is an Astec one then the resistors are built in so no so easy to re use them.


  • Registered Users Posts: 11,715 ✭✭✭✭altor


    Ivan E wrote: »
    Yeah, I think there's only one contact on the zone and yes it's an entry zone. The contact was put in around 3-4 years ago by someone who knew what he was doing.

    So I am just trying to gauge is it something i can do myself easily. I managed to follow the instructions in here on how to replace the battery previously. Hoping this is as straight forward. I was thinking I could just reuse the existing resistor there assuming there is one. But I suppose that could easily be the source of the issue too.

    Steps then would:
    1. Unscrew existing contact.
    2. Connect the new contact the same way.
    3. Check any other connections on that route.

    or is there something else I need to watch for that could do damage?

    If using a global contact to replace you will need to use a 340 ohm resistor across the contact.


  • Registered Users Posts: 148 ✭✭Ivan E


    Thanks Altor. It was actually you who installed it 3 or 4 years back I think :)

    I removed the cover and I see 4 wires with two of them going into some sort of blue block in the contact. I am not sure if that's the resistor. I have a picture of it which I can try and post later. Not sure if you remember that type of contact.


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    If it's the blue blocks sitting to the side they are usually just spare block connectors. Astec sensors would have the resistors built in.
    Anyway if you post up a picture we can tell you for sure.


  • Registered Users Posts: 11,715 ✭✭✭✭altor


    Ivan E wrote: »
    Thanks Altor. It was actually you who installed it 3 or 4 years back I think :)

    I removed the cover and I see 4 wires with two of them going into some sort of blue block in the contact. I am not sure if that's the resistor. I have a picture of it which I can try and post later. Not sure if you remember that type of contact.

    If its an Astec system then more than likely the one with a blue dot.
    You would need to post a picture t be sure.


  • Registered Users Posts: 148 ✭✭Ivan E


    Not sure of the quality of this but hopefully it gives you some idea

    303gvf5.jpg


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Yes that is an Astec contact. If you are replacing this with a standard contact you must wire a 680 ohm resistor across the contact terminals.
    If you stuck for sourcing one give me a shout. I've bags of them.


  • Registered Users Posts: 11,715 ✭✭✭✭altor


    Ivan E wrote: »
    Not sure of the quality of this but hopefully it gives you some idea

    303gvf5.jpg

    Its an Astec contact alright.
    The only way of knowing if the sensor is faulty is by using a mutlimeter to test.


  • Registered Users Posts: 148 ✭✭Ivan E


    KoolKid wrote: »
    If you stuck for sourcing one give me a shout. I've bags of them.

    The contacts or the resistors?
    altor wrote: »
    The only way of knowing if the sensor is faulty is by using a mutlimeter to test.

    What exactly am I looking for here? It seems to work for a while and then just go off.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    You would need to check the resistance on that whole zone using a multimeter.
    Remove the end of line resistor.
    Connect the leads from the multimeter to the pair for that zone at the panel.
    Set the meter to 200 ohms and make a note of the reading. If there is nothing else onon that zone and it's only a short run the zone should read no more than a few ohms.
    If you open and close the door and tap the sensor it should always return to the same value. If reading sticks up at a higher level or jump around disconnect the device and close off thethe pair at the sensor. If the reading then drops back it's the device that's at fault.


  • Registered Users Posts: 11,715 ✭✭✭✭altor


    Ivan E wrote: »
    What exactly am I looking for here? It seems to work for a while and then just go off.

    You wont be able to visually see anything. Only using a meter can you test the contact. Id follow the above but as its a contact tapping the sensor will have no bearing on the reading. Opening and closing the door is what you should be looking to do while testing the contact with the meter.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    altor wrote: »
    but as its a contact tapping the sensor will have no bearing on the reading.
    It will if the contact is faulty. On a good contact you may see no change but I have found plenty of faulty contacts by tapping them while checking the resistance.


  • Registered Users Posts: 148 ✭✭Ivan E


    Thanks lads, I’ll try that tonight.

    If it is the contact, can you still get Astec contacts or is it a case of just going with the standard ones and using a resistor?


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    A standard contact with a resistor is probably your only option.


  • Registered Users Posts: 148 ✭✭Ivan E


    Sorry, stupid questions to follow:
    KoolKid wrote: »
    You would need to check the resistance on that whole zone using a multimeter.
    Remove the end of line resistor.
    Where would I find that? Is that the blue block inside the contact?
    Connect the leads from the multimeter to the pair for that zone at the panel.
    There are two wires connected into the zone in the panel. Do I turn the alarm off, remove the battery contact and take the two wires out of the panel?
    Set the meter to 200 ohms and make a note of the reading. If there is nothing else onon that zone and it's only a short run the zone should read no more than a few ohms.
    If you open and close the door and tap the sensor it should always return to the same value. If reading sticks up at a higher level or jump around disconnect the device and close off thethe pair at the sensor. If the reading then drops back it's the device that's at fault.

    I took a look today when I came in. There's two wires, blue and yellow going into the panel at the zone causing the trouble. These wires seem to go into the contact then. If I check for a reading off these wires at the panel, I am not getting anything but I didn't remove the end of line resistor so either it's that or I am doing it completely wrong.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    If you didn't remove the end of line resistor then the meter will have to be set at 2k rather than 200 to get a reading.
    If you remove the end of line resistor & wire the 2 cables to each side of the block then disconnect the pair & the panel and meter it out at 200 ohms you will get a much more accurate reading.


  • Registered Users Posts: 148 ✭✭Ivan E


    Right, it's just I don't know where the end of line resistor is?

    Also I should be removing the wires from the panel and measuring there? I also should be turning off the alarm and battery?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    If the resistor is not in the panel or that sensor then there is probably other devices on that zone. You disconnect the zone from the panel to measure the resistance.


  • Registered Users Posts: 11,715 ✭✭✭✭altor


    Ivan E wrote: »
    Sorry, stupid questions to follow:



    I took a look today when I came in. There's two wires, blue and yellow going into the panel at the zone causing the trouble. These wires seem to go into the contact then. If I check for a reading off these wires at the panel, I am not getting anything but I didn't remove the end of line resistor so either it's that or I am doing it completely wrong.

    Are you sure that is the only sensor on that zone if the Resistor is not in the sensor or the panel?


  • Registered Users Posts: 11,715 ✭✭✭✭altor


    Ivan E wrote: »
    Also I should be removing the wires from the panel and measuring there? I also should be turning off the alarm and battery?

    Yes, the wires need to be removed from the zone in the panel and connected to the meter.

    There is no need to down power the system to do this, if the alarm activates just enter your user code to turn off the alarm or put the system in engineer mode using the engineer code before opening anything.


  • Registered Users Posts: 148 ✭✭Ivan E


    Sorry lads, I just copped something. I was looking at the original install notes attached to the panel. I have forgotten I had got a new window put in since. Looking into it, it looks as if the new sensor attached to that window is in zone 1 too.

    357n8g3.jpg

    I have some sort of junction box beside the front door and it looks as if the phone line comes into that. But also the entry contact to the door that I think is faulty and the shock sensor going to the window. I presume this is then attached to the panel.

    How does this change things? Can I just disconnect the sensors from here and check the resistance?


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Ivan E wrote: »

    How does this change things? Can I just disconnect the sensors from here and check the resistance?

    You can. But ideally you still need to locate the end of line resistor & test the resistance on the complete loop. This would also check the connections going through that junction etc.


  • Advertisement
  • Registered Users Posts: 11,715 ✭✭✭✭altor


    Ivan E wrote: »
    Sorry lads, I just copped something. I was looking at the original install notes attached to the panel. I have forgotten I had got a new window put in since. Looking into it, it looks as if the new sensor attached to that window is in zone 1 too.

    357n8g3.jpg

    I have some sort of junction box beside the front door and it looks as if the phone line comes into that. But also the entry contact to the door that I think is faulty and the shock sensor going to the window. I presume this is then attached to the panel.

    How does this change things? Can I just disconnect the sensors from here and check the resistance?

    You would need to test the loop as a whole as apposed to just checking the individual devices. A bad connection or a problem with the cable would also cause the false alarms.