Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Leaking rad valve

  • 11-05-2016 7:14am
    #1
    Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭


    Noticed a pool of water under downstairs rad last night (central heating has been off for a few weeks)
    It's coming from one of the flow valves . I have the nut a turn clockwise with the spanner last night but the towel underneath was wet this morning.
    Will I try that again (I'm afraid of over tightening it ) or just call a plumber


Comments

  • Moderators, Home & Garden Moderators Posts: 6,305 Mod ✭✭✭✭Wearb


    Is this a valve that you regularly turn on and off ? Usually a little turn on that brass nut cures it.

    If not get a bit (about 70/80mm) of ptfe tape and twist it around its axis to change it from ribbon shape to string shape. Remove the nut and pack the ptfe around the spindle. Replace the nut and gently tighten.

    As with all such jobs: Have lots of towels handy and know how to turn off the heating water supply before working on it. Thing do go wrong sometimes and it's best to be prepared.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 17,157 ✭✭✭✭Sleeper12


    Can you post a photo


  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Wearb wrote: »
    Is this a valve that you regularly turn on and off ? Usually a little turn on that brass nut cures it.

    If not get a bit (about 70/80mm) of ptfe tape and twist it around its axis to change it from ribbon shape to string shape. Remove the nut and pack the ptfe around the spindle. Replace the nut and gently tighten.

    As with all such jobs: Have lots of towels handy and know how to turn off the heating water supply before working on it. Thing do go wrong sometimes and it's best to be prepared.

    Had been turning most rads on and off for first last few years until I noticed a slight leak in a diff one before so I stopped doing that
    So this would not really have been touched this year.
    Left towel under it last night and it's wet this morning so prob need to sort it this evening .
    One thing I noticed is that the spindle nuts on this rad appear much more corroded than any of the others
    Also it's a sealed pressurized system if that makes a difference to switching off water supply ?


  • Moderators, Home & Garden Moderators Posts: 6,305 Mod ✭✭✭✭Wearb


    Doesn't make a difference that it's sealed. You will be so glad that you can turn it off if needed that a little water on a few towels won't matter.

    As sleeper said, post a pic.

    My ptfe solution should work and doesn't cost much to try. Btw you don't need water off to do that, just know how to turn it off .... just in case.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Wearb wrote: »
    Doesn't make a difference that it's sealed. You will be so glad that you can turn it off if needed that a little water on a few towels won't matter.

    As sleeper said, post a pic.

    My ptfe solution should work and doesn't cost much to try. Btw you don't need water off to do that, just know how to turn it off .... just in case.
    Ok thanks I'll try and nip home and post a pic in an hour or two
    Should i also turn the valve to off?
    I left it in the middle as in the off the pressure was building up behind it anyway


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Where should I be looking at turning off heating water supply ? Is it in the hot press


  • Registered Users, Registered Users 2 Posts: 394 ✭✭mrskinner


    You need to watch "how to repair a leaking radiator valve" on YouTube. It probably is not the compression nut that needs attention but the spindle. Just tighten this a tiny bit and see if leak is cured. :D


  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    mrskinner wrote: »
    You need to watch "how to repair a leaking radiator valve" on YouTube. It probably is not the compression nut that needs attention but the spindle. Just tighten this a tiny bit and see if leak is cured. :D

    It is up around the spindle that it's coming alright I believe


  • Moderators, Home & Garden Moderators Posts: 6,305 Mod ✭✭✭✭Wearb


    mrskinner wrote: »
    You need to watch "how to repair a leaking radiator valve" on YouTube. It probably is not the compression nut that needs attention but the spindle. Just tighten this a tiny bit and see if leak is cured. :D

    Isn't that what I have been writing about ....

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Wearb wrote: »
    Isn't that what I have been writing about ....

    :D it is
    Going to try that this evening but will post pics first and also post pic of what I think is the water heating cut off valve if I can find it !


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    That is the offending valve


  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    This the valve on the other side which also appears to have had a dribble of water at some point but not as much

    Also the CH pipes in immersion
    There is no red stop cock. Maybe it is in attic as the two cross cross pops go up the way
    The only red stop cock is on opposite side on a pipe running from bottom of immersion up


  • Registered Users, Registered Users 2 Posts: 17,157 ✭✭✭✭Sleeper12


    It looks like the gland nut needs tightening. Just a pinch, maybe a quarter turn.


  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Sleeper12 wrote: »
    It looks like the gland nut needs tightening. Just a pinch, maybe a quarter turn.

    Will try that so
    I'm afraid of damaging it though !
    Quarter turn clockwise ?
    Just to be doubly sure this is the one in question


  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    This one


  • Registered Users, Registered Users 2 Posts: 17,157 ✭✭✭✭Sleeper12


    km79 wrote: »
    Will try that so
    I'm afraid of damaging it though !
    Quarter turn clockwise ?
    Just to be doubly sure this is the one in question

    Yes, clockwise. Just a tiny bit. If still leaking then a tiny bit more etc.

    The gland nut can loosen from turning valve on & off over the years.


  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Sleeper12 wrote: »
    Yes, clockwise. Just a tiny bit. If still leaking then a tiny bit more etc.

    The gland nut can loosen from turning valve on & off over the years.

    Ok will try that again so
    Also bought some plumbers tape
    Regarding the water switch off is that likely to be in the attic now ? May as well figure it out now While I'm at it


  • Registered Users, Registered Users 2 Posts: 17,157 ✭✭✭✭Sleeper12


    km79 wrote: »
    Ok will try that again so
    Also bought some plumbers tape
    Regarding the water switch off is that likely to be in the attic now ? May as well figure it out now While I'm at it

    I think you said its a closed pressurized system? The water should already be off if this is the case.


  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Sleeper12 wrote: »
    I think you said its a closed pressurized system? The water should already be off if this is the case.

    Yes closed pressurized system
    To top up I need to open 2 valves beside boiler
    That's what I was hoping was the case but someone else mentioned I had to switch it off somewhere else


  • Moderators, Home & Garden Moderators Posts: 6,305 Mod ✭✭✭✭Wearb


    Post a pic of the two valves. One usually does the job.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Wearb wrote: »
    Post a pic of the two valves. One usually does the job.
    Wearb wrote: »
    Post a pic of the two valves. One usually does the job.

    There is a red mains stop cock
    And then one black one under gauge to control the flow into the system I think
    I've topped it up occasionally before
    Pressure has now dropped to near zero so will have to bleed etc I assume
    Monitoring the rad for a few hours/ days first as leak seems to have stopped ........


  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Leak is now just an occasional drop
    Maybe one every half hour or son
    Not fully sorted but improved
    However the nut is fairly stiff. I really don't think I should force it anymore ........
    Is it possible the leak has only stemmed because the water pressure in the system is now so low ?


  • Moderators, Home & Garden Moderators Posts: 6,305 Mod ✭✭✭✭Wearb


    Will probably leak a bit more when pressure is increased. There really isn't a need for the red valve in that situation. The black valve should be used as on and off and the opposite end of that assembly should be adjusted so that when the black valve is fully opened, the pressure doesn't go past 1.5 bar or there abouts. That way when bleeding a radiator, you can leave the black valve open until finished. The pressure will be controlled (if set correctly) by the valve and all that needs to be done is to turn off the black end when finished.

    The need for regular bleeding will damage your heating system and the cause should be sorted, as you are now doing.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Wearb wrote: »
    Will probably leak a bit more when pressure is increased. There really isn't a need for the red valve in that situation. The black valve should be used as on and off and the opposite end of that assembly should be adjusted so that when the black valve is fully opened, the pressure doesn't go past 1.5 bar or there abouts. That way when bleeding a radiator, you can leave the black valve open until finished. The pressure will be controlled (if set correctly) by the valve and all that needs to be done is to turn off the black end when finished.

    The need for regular bleeding will damage your heating system and the cause should be sorted, as you are now doing.

    Thanks
    I had needed to bleed regularly before as I had stupidly been opening and closing the refs in various rooms for a few years until I spotted one of them leaking when it was off so I stopped doing it

    As regards this valve now . The nut is very tight. I'm really reluctant to try and force it anymore . Maybe I'll go for the tape assuming I can take the nut off without the place flooding ?
    Or else call a plumber !


  • Moderators, Home & Garden Moderators Posts: 6,305 Mod ✭✭✭✭Wearb


    Removing that nut wont flood the place unless something VERY unusual happens. You now know where to turn it off anyway and as said have a few towels ready. You may have to do the ptfe thing a few times until it stops it, but is is quick and easy to do.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Wearb wrote: »
    Removing that nut wont flood the place unless something VERY unusual happens. You now know where to turn it off anyway and as said have a few towels ready. You may have to do the ptfe thing a few times until it stops it, but is is quick and easy to do.
    Those stop cocks are always set to off so therefore the central heating water supply is always off is my understanding ?
    I'll give it a go at the weekend I think
    Many thanks to ye both for all the help


  • Moderators, Home & Garden Moderators Posts: 6,305 Mod ✭✭✭✭Wearb


    km79 wrote: »
    Those stop cocks are always set to off so therefore the central heating water supply is always off is my understanding ?

    Yes, then it's always off, as it should be.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 48,256 ✭✭✭✭km79


    Successfully stopped leak in that valve
    However there is a leak in the other one too
    I repacked it as I did the other one BUT the nut on top won't thread back in properly
    After inspecting it I think one of the threads on it may be damaged
    Is it possible to buy nut or doni need to buy entire valve ?