Identifying root cause of water ingress from outer to inner leaf - cavity wall

  • 17-05-2016 01:55PM
    #1
    Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭


    Have a scenario with my house whereby there’s water ingress from outer leaf to inner leaf due to defective external rendering. Have had this verified professionally – and in a claims scenario. As part of that process, I need to go one step further and open up a section of the gable wall – and try to identify specifically how the water is transferring from outer to inner leaf. Engineer has indicated it may be for one of the following reasons;

    - It’s simply getting through the render and transferring across via the wall ties.
    - There are mortar snots in the cavity/on the ties and this is resulting in the transfer of water
    - The insulation is not fitted properly to the inner leaf – resulting in the transfer of water.

    Naturally, I’ll be having the engineer examine wall once it’s been opened. Notwithstanding that, I’d like to be as well informed myself as Ì possibly can be as to how the precise defect can be identified and proven beyond doubt.
    If it’s the first item listed above, how do I demonstrate this i.e. that water is simply running along the ties? The second one (mortar snots) seems pretty straightforward. As regards the insulation, what am I looking for there? I’ve a feeling this won’t come into play as I *think* it's bead insulation as opposed to rigid polystyrene (can see beads when I check the ESB meter on that wall).

    Are there any other causes that I can look for other than the three listed above?


«13

Comments

  • Registered Users, Registered Users 2 Posts: 18,920 ✭✭✭✭_Brian


    Two things strike me as likely.
    Mad you say through messy brickwork the mortar a its on wall ties is carrying significant water across.

    It may be beaded insulation but there were limits as to the application of this on standard walls. In areas of the country where driving rain is common it isn't recommended for use for this reason. From memory there is a map showing areas where it shouldn't be used.


  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    If there are no mortar snots on the ties then look to see if there is a "drip" on them (a kink in the middle) - there probably isn't if it's a full fill insulation but if there is one it's unlikely the water is crossing the ties. You could drop some water onto them yourself and see do the water drips fall towards the outside of the tie or the inside.

    The beaded insulation is not recommended for brick outer leaf walls in areas with high driving rain index. If your render is poor your block wall could be porous like a brick one and essentially be subject to the same conditions. Having said that I have seen brick walls in areas of quite high driving rain with bead pumped into the cavity where it shouldn't have been and there hasn't been any water crossing the cavity.

    What way is the water crossing the cavity manifesting inside and at what locations is the problem happening?


  • Registered Users, Registered Users 2 Posts: 13,302 ✭✭✭✭Calahonda52


    What way is the water crossing the cavity manifesting inside and at what locations is the problem happening?

    This is key as well as what OP means by this:
    Have had this verified professionally.
    With an unopened wall, thats a mighty call:D

    What about faulty DPC detailing around windows/lintels etc?

    Whats the roofing detail, overhang or barge?

    The one thing about water is that the entry and exit points are never close together.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    Barges, parapet walls, unsealed stonework, poor cavity trays ... projections such as conservatories etc. There's a lot of ways water can get in without the render necessarily being faulty.

    And even in the absence of any external render you're not guaranteed to have water crossing the cavity.

    Can you let us know how it shows up inside OP?


  • Registered Users, Registered Users 2 Posts: 1,024 ✭✭✭Coles


    I don't see how you have had anything 'verified professionally' when you aren't clear even what kind of insulation is in the cavity. That's a key fact.

    I agree with Calahonda52. More likely to be DPC detailing (parapet wall, lintels etc.). I'd be very surprised if the render alone was the culprit.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭makeorbrake


    _Brian wrote: »
    It may be beaded insulation but there were limits as to the application of this on standard walls. In areas of the country where driving rain is common it isn't recommended for use for this reason. From memory there is a map showing areas where it shouldn't be used.
    It's manifesting on the gable wall of the house only - the one that gets the full force of wind n' driving rain. If you (or anyone reading this) happen to have a link re. map, I'd be keen to check that out.
    The beaded insulation is not recommended for brick outer leaf walls in areas with high driving rain index.
    Would you happen to have a link to any documentation on that?
    What way is the water crossing the cavity manifesting inside and at what locations is the problem happening?
    The internal surface of that wall is bubbling up - with efflorescence marks evident from a height of 6ft to the base of the wall - in both the living room and kitchen (both on the internal surface of that gable wall). On the exterior, there are a series of long horizontal cracks in the render - a few metres in length for each - about 5 or 6 of them.
    Nothing is evident on the upstairs wall internal surface but then that complete surface is tiled - so difficult to assess.
    This is key as well as what OP means by this:
    Have had this verified professionally.
    With an unopened wall, thats a mighty call:D

    What about faulty DPC detailing around windows/lintels etc?

    Whats the roofing detail, overhang or barge?

    The one thing about water is that the entry and exit points are never close together.
    This is key as well as what OP means by this:
    Have had this verified professionally.
    With an unopened wall, thats a mighty call:D

    What about faulty DPC detailing around windows/lintels etc?

    Whats the roofing detail, overhang or barge?

    The one thing about water is that the entry and exit points are never close together.
    Coles wrote: »
    I don't see how you have had anything 'verified professionally' when you aren't clear even what kind of insulation is in the cavity. That's a key fact.

    I agree with Calahonda52. More likely to be DPC detailing (parapet wall, lintels etc.). I'd be very surprised if the render alone was the culprit.
    Yup - ok, I guess I wanted to get across the point that I've had an engineer carry out an initial assessment (so that people understood I had taken that step). There are a series of horizontal cracks - over a few metres in length evident on that gable wall - they're a few mm wide. He is not verifying HOW the water crosses - but is indicating a failure of the render itself. That's the reason for the opening up works.

    I take your points re. DPC detailing and roofing detail (overhang - not barge). There's only one window on that gable wall - small bathroom window. How can that be assessed for water ingress?? As regards the main dpc, I assume that can be ruled out if damp is showing at a height of 6ft inside?


  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    Two quick questions -

    What height are the external cracks at?

    And what type of roof do you have - hip or gable ended?

    Edit: Those cracks might be indicative of a problem rather than the root problem.


  • Registered Users, Registered Users 2 Posts: 13,302 ✭✭✭✭Calahonda52


    OP: any chance of a few pictures of the cracked gable.
    Op: back to this: there’s water ingress from outer leaf to inner leaf due to defective external rendering. Have had this verified professionally
    and
    He is not verifying HOW the water crosses

    I think that you may be over interpreting what he is saying, let me put it this way, this would not last 2 mins under defence council cross examination.

    You may have a structural issue which MT is alluding to: hip roof, no ring beam, not enough ties, cavity too wide, etc
    and the other clue is:
    Tiled wall in room above suggests a bathroom, suggests imbedded pipework suggests....leaks, [perhaps I have too much vino for Tuesday:)]

    While I don't expect it, do first floor joists embed in gable wall?

    The internal surface of that wall is bubbling up - with efflorescence marks

    That a lot of water to jump across, but am happy to be wrong.

    My final point here is that opening up a cavity wall gable with bead insulation is a world of hurt and might show zip, costing money that might be better spent on remedial rather than destructive work.

    Let me put it this way, if you had no one to sue, or if the builder has gone ^^ up, would you still open up?
    Getting a judgement against a sole trader or a man of straw is worthless

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    Calahonda52 said exactly what I was thinking but didn't have the balls to say out loud!!!

    Look for leaks and/or structural problems before whacking a big hole in your wall.

    Would love to see some pictures too!


  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    Would you happen to have a link to any documentation on that?

    Just to answer this (although I'm not sure it's relevant in this case) it will be given in the agrement cert for the bead in question.

    So find out what brand of bead is in the wall (or if you don't know for investigative purposes you can pick a roughly similar one) and then google "XYZ Brand Bead NSAI Agrement Certificate" and read the section relating to exposure.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭makeorbrake


    Two quick questions -
    What height are the external cracks at?
    And what type of roof do you have - hip or gable ended?
    Edit: Those cracks might be indicative of a problem rather than the root problem.
    See pics below
    OP: any chance of a few pictures of the cracked gable.
    Sure - see below.
    Op: back to this: there’s water ingress from outer leaf to inner leaf due to defective external rendering. Have had this verified professionallyand He is not verifying HOW the water crosses
    I think that you may be over interpreting what he is saying, let me put it this way, this would not last 2 mins under defence council cross examination.
    So the opinion of a professional engineer doesn't carry any credibility? He maintains that there is no other moisture source resulting in the internal damage. The other party has not demonstrated otherwise.
    My final point here is that opening up a cavity wall gable with bead insulation is a world of hurt and might show zip, costing money that might be better spent on remedial rather than destructive work.
    It grates my gears that I have to go to this length - I feel it's unnecessary. The other party maintains that the rendering is NOT necessary to insure the watertightness of the dwelling. They maintain that I have not demonstrated specifically HOW the water is finding its way to the inside surface. This is going a certain direction - and I have to nail things down before proceeding to the next step. Do I want to do it - most definitely not.
    Let me put it this way, if you had no one to sue, or if the builder has gone ^^ up, would you still open up?
    Getting a judgement against a sole trader or a man of straw is worthless
    No on the first question. On the man of straw, this isn't a 'man of straw' but a party to matters that has responsibilities - the essence of which being that I shouldn't have been sold a defective property.

    external
    internal1
    internal2
    So find out what brand of bead is in the wall (or if you don't know for investigative purposes you can pick a roughly similar one) and then google "XYZ Brand Bead NSAI Agrement Certificate" and read the section relating to exposure.
    Thanks for that. Is it not highly relevant - if it was proven an inappropriate material had been used (resulting in this whole issue)?


  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    Have you posted here before OP - I think I've seen those photographs before!

    We're not allowed give structural advice here but I am going to give some gambling advice. If I was a betting man I would place a nice wager that when you open up the wall those horizontal cracks are caused by some sort of issue with the wall ties. Possibly they are rusty or otherwise compromised. There's a publication by BRE called "Cracking in Buildings" - ask your Engineer if he can access it. Chapter 6 describes an issue with horizontal cracking very like your own.

    As for the moisture ingress - it could be related to the wall tie issue. It could be mortar snots or it may be something completely different.

    Is there a radiator behind that sofa?

    Have you physically seen the cavity insulation at any opening in the wall - meter box or similar?

    Is it not highly relevant - if it was proven an inappropriate material had been used (resulting in this whole issue)?
    Your wall is rendered. It is not inappropriate to use it in your case. It was just part of a general discussion that if moisture somehow got past the render then based on inference from the certs discussed it MAY be possible for water to cross the pumped cavity. As I said - I've never seen it happen - even in walls that have no render! Your wall is "rendered" (note the inverted commas!) so there's no argument that appropriately certified pumped bead would be inappropriate.


  • Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭makeorbrake


    Have you posted here before OP - I think I've seen those photographs before!
    You're quite right - good memory. Posted some time ago. I'm a little bit further on than I was back then - progress has been very slow in between times (but I'll get there).
    We're not allowed give structural advice here but I am going to give some gambling advice. If I was a betting man I would place a nice wager that when you open up the wall those horizontal cracks are caused by some sort of issue with the wall ties. Possibly they are rusty or otherwise compromised. There's a publication by BRE called "Cracking in Buildings" - ask your Engineer if he can access it. Chapter 6 describes an issue with horizontal cracking very like your own.
    Thanks for the tip on that. Should the opening be made along one of those cracks then?
    As for the moisture ingress - it could be related to the wall tie issue. It could be mortar snots or it may be something completely different.
    I guess that's the difficulty - i.e. that I may not find specifically what's needed but then I need to try - as it would rule out a lot of uncertainty if this ends up in litigation.
    Is there a radiator behind that sofa?
    No rad. There's a rad in the Kitchen - along that wall alright - but not the front room. If the rad was an issue, surely the moisture wouldn't defy gravity (as it's up as far as head height?
    Have you physically seen the cavity insulation at any opening in the wall - meter box or similar?
    Nope. I've just seen some 'beads' fall out when accessing the ESB meter (that's fixed into the side of the wall).
    Your wall is rendered. It is not inappropriate to use it in your case. It was just part of a general discussion that if moisture somehow got past the render then based on inference from the certs discussed it MAY be possible for water to cross the pumped cavity. As I said - I've never seen it happen - even in walls that have no render! Your wall is "rendered" (note the inverted commas!) so there's no argument that appropriately certified pumped bead would be inappropriate.
    Ok, but IF they concede that there's an issue with the render - and claim that render has no function when it comes to watertightness, would the combination of compromised render together with the use of that material mean that I only need to prove that the render is defective? Is it a case that whilst it's suggested that certain bead insulation shouldn't be used in some areas, it's ok to use in said areas if the dwelling is rendered?


  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    Thanks for the tip on that. Should the opening be made along one of those cracks then?
    It wouldn't be right for me to give advice in that regard because I don't know anywhere near enough about the house and even if I did give advice you shouldn't follow it because I could be any auld crank on the internet. You have engaged a structural engineer - he/she is the one to give advice on that.
    I guess that's the difficulty - i.e. that I may not find specifically what's needed but then I need to try - as it would rule out a lot of uncertainty if this ends up in litigation.
    Yes and no. If you open up with a view to litigation you should have a whole fleet of people present to make it of any use. Sample list:

    1. You
    2. Your engineer.
    3. The contractor/developer/vender
    4. An engineer working for the contractor/developer/vendor
    5. An engineer working for your home insurance company
    6. An engineer working for the contractor/developer/vendor's insurers
    7. A Homebond representative if they are involved.

    If you just open it up on your own you leave yourself open to claims that you made the problem worse by your activities.

    No rad. There's a rad in the Kitchen - along that wall alright - but not the front room. If the rad was an issue, surely the moisture wouldn't defy gravity (as it's up as far as head height?
    The reason I asked is that moisture will condense and behave differently directly above a rad because the heat from the rad rises warming the blocks, wall and air directly above the radiator to a higher temperature than the surrounding areas. If you look at poorly ventilated properties you sometimes see discolouration and mould growth above the radiators. I was just wondering if heat could be an issue that is feeding into the dampness you see on your wall. I don't have the answer - just asking the question!

    Nope. I've just seen some 'beads' fall out when accessing the ESB meter (that's fixed into the side of the wall).
    Hmmm ... there's better informed posters than I around here who might be helpful to you with regards to what you should and shouldn't see.

    Ok, but IF they concede that there's an issue with the render - and claim that render has no function when it comes to watertightness, would the combination of compromised render together with the use of that material mean that I only need to prove that the render is defective?
    This comes down to the wording of the agrement cert. It lists the types of walls in which the bead can be used in both exposed and not so exposed areas. Read it carefully and have your engineer read it. Where are you based?
    Is it a case that whilst it's suggested that certain bead insulation shouldn't be used in some areas, it's ok to use in said areas if the dwelling is rendered?
    Yes - pretty much. The bead can be used in X, Y and Z wall type in some areas whereas in other it can only be used in X and Y wall type.


  • Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭makeorbrake


    It wouldn't be right for me to give advice in that regard because I don't know anywhere near enough about the house and even if I did give advice you shouldn't follow it because I could be any auld crank on the internet. You have engaged a structural engineer - he/she is the one to give advice on that.
    Understand totally. I guess I couldn't help myself but to ask. It's kind of important to me that this saga ends well...and with that, I'm trying to educate myself as best I can (in addition to taking professional advice).
    Yes and no. If you open up with a view to litigation you should have a whole fleet of people present to make it of any use. Sample list:

    1. You
    2. Your engineer.
    3. The contractor/developer/vender
    4. An engineer working for the contractor/developer/vendor
    5. An engineer working for your home insurance company
    6. An engineer working for the contractor/developer/vendor's insurers
    7. A Homebond representative if they are involved.

    If you just open it up on your own you leave yourself open to claims that you made the problem worse by your activities.
    It really only involves 1,2 & 7 - informed by 7 that It's incumbent on me to go that route and prove my case beyond doubt - whilst also giving them access for their own assessment.
    The reason I asked is that moisture will condense and behave differently directly above a rad ...I don't have the answer - just asking the question
    Yup, and I appreciate you asking the question rather than not.
    This comes down to the wording of the agrement cert. It lists the types of walls in which the bead can be used in both exposed and not so exposed areas. Read it carefully and have your engineer read it. Where are you based?
    Yes - pretty much. The bead can be used in X, Y and Zwall type in some areas whereas in other it can only be used in X and Y wall type.
    I'm based in the West of Ireland. Checked one Agrement Cert just now (of course, I don't know if its the right one) for beaded insulation and their map shows I'm located in a severe exposure area...but just like you said, as long as its rendered and a minimum cavity gap of 90mm, then it's ok to use....but then if the render was defective....
    Edit: Checked another one and they say 'minimum 40mm cavity'.
    This is a pic of the meter box - which seems to suggest bead fill - unless that was just used around the box itself?


  • Registered Users, Registered Users 2 Posts: 628 ✭✭✭tedimc


    Not offering any structural advice, but just a thought before you go cutting sections out of your wall.

    You can now get pin-hole cameras very cheap online(with built in LED lighting) - you could always drill a few small holes (10mm) into the cavity and have a look around using a camera, before identifying the best point to open up a large inspection hole. It may help for example to spot mortar snots, rusted wall-ties, misplaced insulation, etc.


  • Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭makeorbrake


    @tedimc: Appreciate that - and I guess it makes a lot more sense. That said, this is what the other party has been insisting on (and for reasons I won't go into, it's taken forever to get to this point).

    Would the cameras still function where there's bead insulation in place in the cavity? i.e. is it still possible to view ties, etc with the bead in the way?


  • Registered Users, Registered Users 2 Posts: 628 ✭✭✭tedimc


    Oh yeah - I think you will end up opening up a section of the wall to prove the point, but I think it would be hit or miss and you don't want to end up cutting more of the block than is absolutely necessary out.

    The camera may help you from the perspective of knowing exactly where to cut/open. And 20 10mm holes are easier to fill/patch than a single large 200mm hole.

    It should be able to push the bead out of the way, but you probably wouldn't have a lot of control over the direction once you enter the cavity. However, some of the 'professional' options have the ability to direct the probe/camera I think. The types used in drain inspections may be too large, but smaller ones may be used for engine or machinery inspection.

    Alternatively - a thermal imaging camera may give some clues without the need to drill at all? It wouldn't be very detailed, but may help identify a particular area, or even where the wall ties are located?

    On another note - if worst comes to the worst and you don't get any joy with this course of action, there are renders/paints that claim to be "waterproof" and are supposed to help keep driving rain out. I went with a Sto render on my house which is silicone based. I'm not sure if it helps or not (time will tell) but I know I does appear to repel water somewhat. You can see it bead on the surface a run down the face of the wall. They do offer better more expensive options also. Just a fall back option worth investigating if you don't have any joy.


  • Registered Users, Registered Users 2 Posts: 13,302 ✭✭✭✭Calahonda52


    Would not recommend any waterproof sealing on the external wall, the wall needs to breath from a vapour diffusion perspective

    Thats a big gable so lets ask how it is orientated?

    If it is south facing then solar moisture drive, coupled with lots of water getting in via the cracks could be a contributing factor.
    some links
    http://www.nbec.net/documents/LABORATORYDEMONSTRATIONOFSOLARDRIVENINWARDVAPOURDIFFUSIONINAWALLASSEMBLY-W.MAREF.pdf
    http://www.cosella-dorken.com/bvf-ca-es/pdf/articles/Solar-Driven_Moisture_Proceedings.PDF
    http://jen.sagepub.com/content/early/2016/01/19/1744259115624183.abstract

    While this is normally more discussed in TF construction I am posing it as a possible contributor here.

    The beads will not the the carriers of the vapour here, the vapour pressure will just drive the vapour laden air through: the argument thus far has focused on the transfer of water.

    Water vapour transfer and water transfer are two entirely different problems.

    Just reading the posts here, the legal approach seems to be that they want you to prove that the cracks in the wall and the internal damage are related.
    First up, as MT has intimated, that wall is unfit for purpose as is and you may have a structural "failure issue" as opposed to it just being leaky.
    So you need to ensure that the gable is structurally sound.

    You are going cause and effect here: I am saying wall is structurally unsound so let's boogie on that point as a standalone.

    Next up, if the render is not needed for waterproofing, then what did they think its is there for?

    What does your engineer say about that.

    Thats bXXXXXX

    Final question, is the inner leave just skimmed internally in the room on the block, no dry-lining.

    Again my instinct is not to open up,
    iff, thats if and only if, the wall is structurally sound, I would propose installing a ventilated rain shield over the gable end, its a nice clean area to work on.

    For example: rendered, on nylon mesh, concrete board on pressure treated timber battens, ventilated top and bottom and no horz "noggins"

    This will solve both the solar drive and water ingress problem and will cost a fraction of the cost of opening up etc, not to mind the legal costs.

    This could also be done in conjunction with chemical fixings through the wall to solve the structural issues which made be tie related.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭makeorbrake


    Thats a big gable so lets ask how it is orientated?
    It's South facing.
    Next up, if the render is not needed for waterproofing, then what did they think its is there for?

    What does your engineer say about that.

    Thats bXXXXXX
    Well, I'm no engineer but that was the first thing I thought of i.e. why the hell bother with an outer leaf then. He's of a mind that its structural and there should be no need to take this step.

    I'm only going along with this as I want to nail things down as much as I possibly can - should this go legal.
    Final question, is the inner leave just skimmed internally in the room on the block, no dry-lining.
    Yes, skimmed on the block - no dry-lining.
    You are going cause and effect here: I am saying wall is structurally unsound so let's boogie on that point as a standalone.
    Yup - that's the second thing I want to prove.

    I started out thinking that just a re-render and internal decorate were required. Now, it's looking like a much bigger job.

    Hoping to have someone in to open up wall later this week so hope to know more then.


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 13,302 ✭✭✭✭Calahonda52


    Well, I'm no engineer but that was the first thing I thought of i.e. why the hell bother with an outer leaf then. He's of a mind that its structural and there should be no need to take this step.

    The above makes no sense, I was talking about the render, not the outer leaf.

    Anyway my mula is on solar moisture drive.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭makeorbrake


    The above makes no sense, I was talking about the render, not the outer leaf.
    To clarify, they suggest that the render has no role to play in keeping the dwelling watertight.

    Anyway my mula is on solar moisture drive.
    It's a new one on me - thanks for the info. Just got back in - will read the info you linked to a little bit later.


  • Registered Users, Registered Users 2 Posts: 1,117 ✭✭✭PMBC


    That's what plastering is for!
    Regarding water transfer across snots on ties, surely you would see damp spots at each tie location, if that was the case. Perhaps that's complicated by the use of full fill-insulation.


  • Registered Users, Registered Users 2 Posts: 13,302 ✭✭✭✭Calahonda52


    To clarify, they suggest that the render has no role to play in keeping the dwelling watertight.

    Well then : what is it for?

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭makeorbrake


    Well then : what is it for?
    Good question! I'm just getting the run around - I'll go along with the opening up but ultimately, I'm going to nail them down on this.


  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    To be fair an unrendered cavity wall with clean wall ties that have an appropriate drip should be completely rain resistant. "Porous" brick outer leafs have been installed to cavity walls in this context for many years.

    1. Problem number 1 is that what we call a cavity wall in many cases no longer has a cavity - it is fully filled with insulation. So if you do, for some reason, have water penetrating the outer block you are relying on the insulation not to transmit the water across. This is specifically considered in the agrement testing for the full fill beads - hence the recommendation regarding driving rain indeces and unrendered walls.

    2. I think in many less than well thought out constructions the cementitious render (which does apply some water water-proofing to the wall) is being relied upon for a level of water proofing beyond its "design." I don't think it should not be relied up to do so.


  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    To add:

    If the moisture you see makeorbrake is definitely coming across the cavity (I'm not fully convinced it is although I don't see an alternative path) then the rainscreen proposed by Calahonda would be the perfect low impact solution.

    But I personally would not like to install this without first determining the cause of your horizontal cracks - have they been measured for their width?


  • Registered Users, Registered Users 2 Posts: 1,117 ✭✭✭PMBC


    To add:

    If the moisture you see makeorbrake is definitely coming across the cavity (I'm not fully convinced it is although I don't see an alternative path) then the rainscreen proposed by Calahonda would be the perfect low impact solution.

    But I personally would not like to install this without first determining the cause of your horizontal cracks - have they been measured for their width?

    good idea, a few crack monitors wouldnt go astray


  • Registered Users, Registered Users 2 Posts: 4,676 ✭✭✭makeorbrake


    Openings have been made. Have not had time to spend any time on this other than a cursory glance - and not going to disturb anything until engineer has a look. However, 2 things confirmed so far - insofar as I can see.

    1. Bonded bead being used as cavity infill in an area where all bonded bead Agrement Certs say - ok to use but only with rendered finish (and if the rendered finish is compromised, then it's rational conclusion to arrive at - for me to suggest that's very much an issue and the render by default is responsible for water transfer - or at the least is a component in that process) in areas of severe exposure (which is the case in this instance).

    2. One tie exposed thus far - and it shows mortar dabs. See pic below. Bead is particularly wet the touch around this area.


    Mortar snot on wall tie.



    Will see what the professional evaluation throws up...


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,727 ✭✭✭Metric Tensor


    Finding it hard to figure out what angle I'm looking at there! Do you have any a little more zoomed out for context?

    Thanks for posting btw - interesting stuff!