Horstmann HRT3 not working right

Options
  • 04-12-2016 7:21pm
    #1
    Registered Users Posts: 40


    Iv a problem with my thermostat. It doesn't seem to b working right as in not reading the temperature. The wires are brown, black and gray. Brown to 1, gray to 3 and black to 4. Any help out there


Comments

  • Registered Users Posts: 62 ✭✭Gashmuncher


    Lots. More info required to give proper opinion, can you post a photo?


  • Registered Users Posts: 40 TimTam82


    Here are a few pics. I used a phase tester and all have power going through (1,3,4)


  • Registered Users Posts: 62 ✭✭Gashmuncher


    Here is the link to the instructions and wiring for the room stat.
    https://www.manualslib.com/manual/478253/Horstmann-Hrt3.html

    Terminal 1. Live / Power in. Brown Wire
    Terminal 3. Live / Power out. Grey Wire

    Terminal 4 Neutral Connection. Black Wire

    Does the stat make a clicking sound when you turn it up and down from one extreme to the other? This click is the contacts opening and closing. If there is no click the stat is most Lilkey faulty.
    If you short out terminal 1 and 3 ie. brown and grey the system should run. If the system runs when you create the short you have confirmed the stat is faulty.
    If the phase tester is lighting up on the black, it indicates that the neutral is disconnected. These stats will work with no neutral connected but won't be as accurate as if the neutral was in place.

    See how this goes


  • Registered Users Posts: 40 TimTam82


    Ok thanks for that! How would I create a short?? Where would the neutral b connected to?


  • Registered Users Posts: 62 ✭✭Gashmuncher


    The questions you are asking indicate that you don't have the basic knowledge necessary to safely identify the fault. Please be very carefull as mains electricity can kill.
    You do not need to do anything with the neutral. You need to get a short piece of "insulated" cable the same size as the cables connected in the stat.

    Turn off the power to the heating circuit. If you are in any way unsure of which circuit it is on, turn off the main switch at the distribution board.

    Strip a small bit of the insulation to expose the copper at each end of the cable. Very carefully and not touching any copper part, loosen the screw and put one end of the stripped cable into terminal 3 (beside the grey wire) and then put the other end into terminal 1 (beside the brown wire). This will allow the power to flow through the stat and when you turn back on the power should start the system. If the system starts, the stat is faulty.
    Don't try this unless you fully understand what you are doing.