Problem with large load from hifi power amp

Options
  • 24-01-2017 8:22pm
    #1
    Registered Users Posts: 126 ✭✭


    Hiya!

    I'm got a hifi system with a number of components that use lots of power. Specifically a 200w power amp and a pre amplifier. If I turn them on at the same time the trip switch goes, and i lose power. So I have to turn them on one by one.

    Thats grand, but I want to add some automation and use a smart plug to turn it on. I could get lots of smart plugs and try and do a delay using software I guess, but I'd love to get a practical solution. Is it possible to just upgrade a fuse to a higher amperage/load?

    I don't really know what I'm talking about, would really appreciate some pointers!

    Cheers!
    Gary


Comments

  • Registered Users Posts: 73,459 ✭✭✭✭colm_mcm


    If you're tripping a breaker, upgrading a fuse isn't going to do anything.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    Hi Gary, can you post a picture of the device that is tripping and I may be able to assist?


  • Registered Users Posts: 203 ✭✭ptogher14


    The in rush current of them all switching on together is tripping them. It would be possible to build a small device with a couple of time delay relays to help the problem. Another option, if you don't need them portable would be hard wire them to a fused spur unit. This way you could put them on a suitable breaker on the board


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    I doubt that the MCB is tripping, 200 W is a small load for a socket outlet (the average kettle is 3000 W). Edit: Unless the amplifier is faulty!
    A photo would confirm what device is tripping.

    I would suspect that it is the RCD that is tripping. If this is the case the solution would be to put the socket circuit concerned on a dedicated RCD.


  • Registered Users Posts: 126 ✭✭ruaneg


    Thanks for the replies!

    It's definitely something with the power amplifier. I had a 400w amp before this one and it didn't cause the problem.

    Should I attach a picture of the back of the amp?

    Cheers!


  • Advertisement
  • Registered Users Posts: 2,236 ✭✭✭deandean


    Those large power amplifiers can have a massive inrush current.

    You possibly have a B-curve MCB installed. e.g. is the legend on the MCB 'B20'?

    If you were to get this changed to a C-curve MCB ( e.g. 'C20'), this handles a higher inrush current and probably would not trip.

    Best of luck.


  • Registered Users Posts: 126 ✭✭ruaneg


    This is the amp, not it's powering 6ft tall speakers that are very power hungry. So as you guys are saying there is no doubt a rush of current. Its in a Cabinet so it's difficult to take a real world photo.


  • Registered Users Posts: 126 ✭✭ruaneg


    And the fuse board...(probably got the name of that wrong!)


  • Registered Users Posts: 126 ✭✭ruaneg


    Better quality pic... B20 e61


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    ruaneg wrote: »
    Better quality pic... B20 e61

    Ok, I was wrong. It appears to be an MCB that is tripping.
    I would guess that the amplifier is faulty.
    Although it would have an inrush current I would not expect the current to be of sufficient magnitude to trip a 20 amp B type MCB.

    The fact that it is supplying 6 foot speakers is not relevant as the connected load is 200 watts. Or is it? Perhaps the Load is 2000 W (2 kW) ??


  • Advertisement
  • Registered Users Posts: 2,236 ✭✭✭deandean


    I had a huge amp like that about 20 years ago, a Realistic IIRC. It weighted about 30kg and most of that weight is from the enormous power suppy comoonents. The room light used to dim for a fraction of a second when I turned it on!
    More modern amps, but not all, have 'soft start' to limit inrush current.


  • Moderators, Category Moderators, Entertainment Moderators, Sports Moderators Posts: 22,584 CMod ✭✭✭✭Steve


    It's inrush, would bet on it. You need a C or D rated MCB.


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,595 Mod ✭✭✭✭2011


    Steve wrote: »
    It's inrush, would bet on it. You need a C or D rated MCB.

    You reckon?
    I have a larger amp, Marantz NR1606. It is 250 W and I have no issues with anything tripping.


  • Moderators, Category Moderators, Entertainment Moderators, Sports Moderators Posts: 22,584 CMod ✭✭✭✭Steve


    2011 wrote: »
    You reckon?
    I have a larger amp, Marantz NR1606. It is 250 W and I have no issues with anything tripping.

    My experience is it depends on the power supply - Switch-mode psu's tend to trip RCD's wheras traffo based psu's tend to trip mcb's. I only have experience in panel building and that's what I base my answer on. :)


  • Registered Users Posts: 1,936 ✭✭✭whizbang


    If thats a BEHRINGER A500 then its known for having a large inrush current. I believe there's info on the web somewhere about building a soft-start circuit for it.


  • Registered Users Posts: 36,167 ✭✭✭✭ED E


    whizbang wrote: »
    If thats a BEHRINGER A500

    The image 100% is. From its Amazon listing. Thats a 2x 300W not a 200W though so not sure if the OP posted the wrong image. Spec: 3.6A(230VAC, 50Hz)


    I know bigger PA amps (2KW) often do a self/loop test for 1-2s on powerup before powering on the amp channels. Not sure how this is done electrically but maybe thats causing the inrush?


  • Registered Users Posts: 1,936 ✭✭✭whizbang


    Softstarts are usually just a resistor inline with the mains supply to the main transformer. Bypassed with a relay on a 2 sec timer.


  • Registered Users Posts: 126 ✭✭ruaneg


    From the spec on the page where i bought it, it states:

    2x 185 Watt RMS @ 4 Ohms, 2x 125 Watt RMS@ 8 Ohms
    https://www.thomann.de/ie/behringer_a500_studioendstufe.htm

    Im using big Magnepan planar speakers that probable use around 4/5 Ohms on average I believe.


  • Registered Users Posts: 126 ✭✭ruaneg


    thanks Whizbang! thats fantastic, Ill do some googling on soft-start circuits:)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    I remember a local shop a few years ago, after a power cut, MCB supplying 4 freezer units would trip when reset due to all 4 trying to start compresors at the same instant. Plugging 3 out then reset, plug back in one at a time and no problem. During g normal operation they will never try to start compressors at same instant.