Home heating automation

Options
12223252728154

Comments

  • Registered Users Posts: 17,771 ✭✭✭✭keane2097


    Is there much/any difference in functionality between the tado Smart thermostat that has been mentioned here and the Netatmo smart thermostat that Energia install?

    The Netatmo is a lot more expensive but the tado seems to do all the same stuff from my reading of product descriptions...?


  • Closed Accounts Posts: 4,456 ✭✭✭The high horse brigade


    GarIT wrote: »
    Lots. Tado tracks your phone and prewarms the house when you are coming home while Netatmo only works off a schedule. Tado checks the forecast so it goes it little heavier or lighter on the heating in the morning depending on what the temperature and sunshine will be like. Tado turns off the heating if it detects an open door or window so it's not wasting heat.

    Netatmo has lots of those features, it learns how long the house takes to heat and adjusts depending on local weather, starts earlier on cold mornings etc


  • Registered Users Posts: 8,671 ✭✭✭GarIT


    Netatmo has lots of those features, it learns how long the house takes to heat and adjusts depending on local weather, starts earlier on cold mornings etc

    I didn't think it did, I might have been thinking of nest or something. After looking it up I found it did, that's why I deleted my post.


  • Registered Users Posts: 6,723 ✭✭✭deezell


    You have to be sharp deleting a post before someone else quotes you!
    IMHO, the Tado has just about every feature you could want. In addition to those mentiond, it has comprehensive graphing of zone temperatures with weather info, away mode and humidity graphing. It is interoperable with Alexa, Google, Homekit and IFTTT. It has highly configurable away functions, and also configurable manual boost settings, with timer, end at next event or next manual operation. The scheduling is almost infinite in flexibility with multiple events per zone per day available. For more tecchie installs with combi boilers it can interact with the boiler using digital OpenTherm protocols, and of course it can co-exist with and control ( or be controlled by) smart TRVs. It looks great too.


  • Registered Users Posts: 17,771 ✭✭✭✭keane2097


    Just looking at a few videos etc online I'm confused as to whether the tado Starter kit linked includes everything needed to remotely/smartly control my boiler or whether the extension kit is needed as well.


  • Advertisement
  • Registered Users Posts: 6,723 ✭✭✭deezell


    keane2097 wrote: »
    Just looking at a few videos etc online I'm confused as to whether the tado Starter kit linked includes everything needed to remotely/smartly control my boiler or whether the extension kit is needed as well.

    If you have a single home wall thermostat to control the heating of your home then the starter kit stat will replace this directly. If you have in addition some kind of timer/ controller for your heating then this can be set to always on, and the smart stat will take over the heating timing function.
    If you have a hot water cylinder and your hot water is heated, (a) only when the heating is on or, (b) according to its own seperate timing on an existing controller, with or without a cylinder thermostat, then your HW will continue to heat in the same manner. If ypur boiler is a combi or direct type HW is supplied on demand directly from the boiler.
    If you have a timer controlled HW setup and you want this function to be part of the Tado setup you require the extension kit.
    If your heating is controlled only by timing but without a wall thermostat you can use the extension kit to insert the Tado stat wirelessly into the heating control circuit. HW timing is optional.


  • Registered Users Posts: 17,771 ✭✭✭✭keane2097


    deezell wrote: »
    If you have a single home wall thermostat to control the heating of your home then the starter kit stat will replace this directly. If you have in addition some kind of timer/ controller for your heating then this can be set to always on, and the smart stat will take over the heating timing function.
    If you have a hot water cylinder and your hot water is heated, (a) only when the heating is on or, (b) according to its own seperate timing on an existing controller, with or without a cylinder thermostat, then your HW will continue to heat in the same manner. If ypur boiler is a combi or direct type HW is supplied on demand directly from the boiler.
    If you have a timer controlled HW setup and you want this function to be part of the Tado setup you require the extension kit.
    If your heating is controlled only by timing but without a wall thermostat you can use the extension kit to insert the Tado stat wirelessly into the heating control circuit. HW timing is optional.

    At the moment our setup is that we have a gas boiler with no thermostat. We have one of these:

    IMM24.jpg

    downstairs that controls the radiators, and another one of them upstairs in the hotpress that controls the hot water.

    If I'm following you rightly, the tado starter kit would replace the downstairs timer switch yoke and I would be able to control my radiator heating using the app and smart thermostat.

    My hot water in that scenario would be on the upstairs timer as it is currently.

    I could then replace the upstairs timer with the tado extension kit and then control the HW via the app and whatever hardware comes with the extender separately?


  • Registered Users Posts: 6,723 ✭✭✭deezell


    keane2097 wrote: »
    At the moment our setup is that we have a gas boiler with no thermostat. We have one of these:

    IMM24.jpg

    downstairs that controls the radiators, and another one of them upstairs in the hotpress that controls the hot water.

    If I'm following you rightly, the tado starter kit would replace the downstairs timer switch yoke and I would be able to control my radiator heating using the app and smart thermostat.

    My hot water in that scenario would be on the upstairs timer as it is currently.

    I could then replace the upstairs timer with the tado extension kit and then control the HW via the app and whatever hardware comes with the extender separately?

    Spot on. Tado stat will be wired directly to the cable from downstairs timer. I'm assuming its in an open location to give a general measurement of room temperature, not in a press or in the utility room. Do this for starters. The ext. Kit can later replace the upstairs HW timer. I'm assuming the HW timer also fires the gss boiler for HW, and is not just a timer for an electric immersion heater. There are many installations out there where the gas only heats the HW cylinder while heating the house, and during the summer people use the immersion. I say this because the ext. kit can't switch enough current to power an immersion element.
    With the ext kit you can optionally locate the stat wirelessly anywhere, the kit has two relays, the one for heating would need to be connected to where the downstairs timer wires return back to the boiler, so wiring is a little more involved as the ext kit then has to connect to the wires from both timers.


  • Registered Users Posts: 17,771 ✭✭✭✭keane2097


    deezell wrote: »
    Spot on. Tado stat will be wired directly to the cable from downstairs timer. I'm assuming its in an open location to give a general measurement of room temperature, not in a press or in the utility room. Do this for starters.

    Yeah the timer downstairs is just sitting on the wall. So if I replace this with the smart thermostat, my heating will then to a greater or lesser extent be taking its cue from whatever the temperature happens to be in that location?
    deezell wrote: »
    The ext. Kit can later replace the upstairs HW timer. I'm assuming the HW timer also fires the gas boiler for HW, and is not just a timer for an electric immersion heater. There are many installations out there where the gas only heats the HW cylinder while heating the house, and during the summer people use the immersion. I say this because the ext. kit can't switch enough current to power an immersion element.

    I'm pretty sure the upstairs timer fires the boiler, I will have to double check. If the upstairs timer is controlling the immersion only I presume I will have to find some other solution for that side of it?
    deezell wrote: »
    With the ext kit you can optionally locate the stat wirelessly anywhere, the kit has two relays, the one for heating would need to be connected to where the downstairs timer wires return back to the boiler, so wiring is a little more involved as the ext kit then has to connect to the wires from both timers.

    The bit in bold, this would allow me to essentially use the temperature in some other part of the house as the cue for the different heating plans to kick in etc?

    Sorry for repeating what you are saying back to you, just want to make sure I'm understanding properly.


  • Registered Users Posts: 6,723 ✭✭✭deezell


    Yes, yes and yes. You've got it.


  • Advertisement
  • Registered Users Posts: 1,858 ✭✭✭dball


    Deezell = Legend!


  • Registered Users Posts: 17,771 ✭✭✭✭keane2097


    deezell wrote: »
    Yes, yes and yes. You've got it.

    Thanks indeed, you're very good.

    I've just checked and it looks like the switch upstairs only handles the immersion, no firing of the boiler.

    So the tado starter kit would do the job for my heating, and from reading around if I want to control the immersion remotely then I will need something like this:

    https://www.amazon.co.uk/Optimum-OP-SBWF01-Enabled-Socket-Switch/dp/B07843J914


  • Registered Users Posts: 6,723 ✭✭✭deezell


    Or this for a tenner. Needs to ne able to switch 16A for an immersion element.
    https://www.amazon.co.uk/Boger-Wireless-Control-Consumption-Measurement/dp/B0769DG75Z
    Similar query back in post #704 in regard to using a Nest stat.


  • Registered Users Posts: 17,771 ✭✭✭✭keane2097


    deezell wrote: »
    Or this for a tenner. Needs to ne able to switch 16A for an immersion element.
    https://www.amazon.co.uk/Boger-Wireless-Control-Consumption-Measurement/dp/B0769DG75Z
    Similar query back in post #704 in regard to using a Nest stat.

    Brilliant, have ordered one of these - much obliged.

    I had read through some of the last few pages a couple of days ago but they were like Greek to me at the time, it's amazing the difference with a small (tiny!) bit of knowledge :D


  • Registered Users Posts: 1,276 ✭✭✭slayerking


    I looking to replace my existing thermostats with Nests but struggling to find out how to do it given the setup I have.
    I have an air to water (electricity based) 2 zone heating system controlled by an EPH controls programmer (an R27 2 zone programmer with 2 x CM3 thermostats).

    Zone 1: downstairs heating
    Zone 2: upstairs heating

    We have hot water also but this is not controlled via a visible thermostat, its always hot and apparently how it supposed to be with a2w systems. Theres also a joule cylinder then in the hot press.

    I know I'll need to wire up the heat link somewhere, possibly where the programmer is and then wire in the thermostats.

    Has anyone set up a Nest on anything like this?


  • Registered Users Posts: 6,723 ✭✭✭deezell


    slayerking wrote: »
    I looking to replace my existing thermostats with Nests but struggling to find out how to do it given the setup I have.
    I have an air to water (electricity based) 2 zone heating system controlled by an EPH controls programmer (an R27 2 zone programmer with 2 x CM3 thermostats).

    Zone 1: downstairs heating
    Zone 2: upstairs heating

    We have hot water also but this is not controlled via a visible thermostat, its always hot and apparently how it supposed to be with a2w systems. Theres also a joule cylinder then in the hot press.

    I know I'll need to wire up the heat link somewhere, possibly where the programmer is and then wire in the thermostats.

    Has anyone set up a Nest on anything like this?

    To replace a single thermostat neatly with a Nest requires disconnecting the stat wire pair from the controller and boiler/zone valve and connecting to the heatlink for each nest stat. The controller can be programmed to be always on or removed altogether. The Nest stats will communicate wirelessly with their respective heatlinks, powered by small phone style adaptors. You can power the nest stats from the heatlink directly by removing the CM3 stats, installing the Nest in the same location and reusing the disconnected mains wires to and from the old stats to carry the low voltage power from the heatlink (also carries a wired version of the wireless digital signal) directly to the Nest. CM3 stats may also have a third Neutral wire connected which can be taped up. This must be carried out correctly or you risk accidentally putting mains into the Nest and frying it. The Nest stat has no mains relay built in, only terminals for low voltage power/digital signalling over a single pair.
    Tado, Hive or Netatmo would be a far simpler install especially as HW control is not required. All these stats have internal mains relays which will directly replace the CM3s on the wall, setting the R27 to always on on both zones. The 2 wires from terminals 1 and 2 on the CM3 are simply connected to Com and N/O on the smart stats, if there is a Neutral wire to the CM3 this is taped up or parked. 2 Nests will cost a bit more than 2 of the other stats also.


  • Registered Users Posts: 1,276 ✭✭✭slayerking


    Thank you deezell for the amazingly detailed advice. Still weighing up what to do. I've installed the Nest hello smart door bell, so I'm 'in bed' with them and I really like the thermostats. Hard to know whether it's worth it though.


  • Registered Users Posts: 9,482 ✭✭✭irishgeo


    ok,

    what i am planning to do is the following. currently its an oil boiler with 1 zone (whole house) with a 7 day timer.

    What i want to do is the following.

    split the house into 3 zones, downstairs , upstairs and hot water. its 2 double rads downstairs and 4 upstairs.

    I want the hot water in the summer but no rads as we only have an immersion

    what i am stuck at is the following, the smart thermostat to be used to get all to work . I should add i have a google home so it would be good to link into that.

    So what do you recommend for the setup i plan to have. getting the SEI grant.


  • Registered Users Posts: 6,723 ✭✭✭deezell


    irishgeo wrote: »
    ok,

    what i am planning to do is the following. currently its an oil boiler with 1 zone (whole house) with a 7 day timer.

    What i want to do is the following.

    split the house into 3 zones, downstairs , upstairs and hot water. its 2 double rads downstairs and 4 upstairs.

    I want the hot water in the summer but no rads as we only have an immersion

    what i am stuck at is the following, the smart thermostat to be used to get all to work . I should add i have a google home so it would be good to link into that.

    So what do you recommend for the setup i plan to have. getting the SEI grant.
    Do you currently have a HW/ CH switch setting on your 7 day timer.
    Make and model of timer.
    Is the Oil boiler an indoor model. Does it have HW CH switch on the front? I'm trying to establish if your system has a separate gravity feed to heat the cylinder (upstairs?) without heating any of the radiators. In a typical simple installation the HW cylinder was plumbed from the downstairs boiler though an open gravity loop, with all the radiators fed through a seperate pumped loop. The timer then in general fired the boiler giving HW, and the wall stat turned on the pump to heat the rads, so you could have summer HW only, either by turning down the stat or by throwing a small switch on the timer to HW only, which cut the pump but not the boiler. Is there a wall thermostat downstairs? To get a 3 zoned system from a single zone will require either a fair amount of zone valve plumbing, This may not even be feasable if the existing plumbing is not laid out in seperate loops allowing the insertion of the zone valves. The alternative is to insert smart TRVs on each radiator, which can be grouped into zones and when all closed will allow the boiler to hear HW only. This would satisfy the smart zoning requirements of the seai grant scheme.


  • Registered Users Posts: 9,482 ✭✭✭irishgeo


    deezell wrote: »
    irishgeo wrote: »
    ok,

    what i am planning to do is the following. currently its an oil boiler with 1 zone (whole house) with a 7 day timer.

    What i want to do is the following.

    split the house into 3 zones, downstairs , upstairs and hot water. its 2 double rads downstairs and 4 upstairs.

    I want the hot water in the summer but no rads as we only have an immersion

    what i am stuck at is the following, the smart thermostat to be used to get all to work . I should add i have a google home so it would be good to link into that.

    So what do you recommend for the setup i plan to have. getting the SEI grant.
    Do you currently have a HW/ CH switch setting on your 7 day timer.
    Make and model of timer.
    Is the Oil boiler an indoor model. Does it have HW CH switch on the front? I'm trying to establish if your system has a separate gravity feed to heat the cylinder (upstairs?) without heating any of the radiators. In a typical simple installation the HW cylinder was plumbed from the downstairs boiler though an open gravity loop, with all the radiators fed through a seperate pumped loop. The timer then in general fired the boiler giving HW, and the wall stat turned on the pump to heat the rads, so you could have summer HW only, either by turning down the stat or by throwing a small switch on the timer to HW only, which cut the pump but not the boiler. Is there a wall thermostat downstairs? To get a 3 zoned system from a single zone will require either a fair amount of zone valve plumbing, This may not even be feasable if the existing plumbing is not laid out in seperate loops allowing the insertion of the zone valves. The alternative is to insert smart TRVs on each radiator, which can be grouped into zones and when all closed will allow the boiler to hear HW only. This would satisfy the smart zoning requirements of the seai grant scheme.
    No it doesn't have a HW switch.

    It's an outdoor firebird boiler. The guy who priced it up for me gave me 3k and told it was possible to zone into 3 zones and told me I didn't need trv on the rads.


  • Advertisement
  • Registered Users Posts: 6,723 ✭✭✭deezell


    irishgeo wrote: »
    No it doesn't have a HW switch.

    It's an outdoor firebird boiler. The guy who priced it up for me gave me 3k and told it was possible to zone into 3 zones and told me I didn't need trv on the rads.

    The boiler has no bearing on the number of zones. This is determined by the number of seperate heating circuits your plumbing is configured with. Is this an existing system or are you just planning it? If you've paid 3k for installation of a new Firebird thats fine, but it has nothing to do with zones, it's just the heat source. Zones require separate pipe runs for each zone, and these are turned on and off by zone valves. 3 required for 3 zones, though you can get away with one less is the HW is always on. If you already have a single zone system with no clear distinction between the pipework for upstairs heating, downstairs and cylinder, then splitting into 3 won't be a trivial plumbing job. Despite the individual cost of smart TRVs it could work out less expensive to use a number of them on the rads, allowing you to have as many zones as there are TRVs, but easily grouped in 2-3 zones. Smart thermostats can't work magic, they can't heat just the downstairs or bedrooms or HW, there have to be valves or pumps to turn on and off the flow to each zone. I'm guessing the 3K didn't include that?


  • Registered Users Posts: 9,482 ✭✭✭irishgeo


    deezell wrote: »
    The boiler has no bearing on the number of zones. This is determined by the number of seperate heating circuits your plumbing is configured with. Is this an existing system or are you just planning it? If you've paid 3k for installation of a new Firebird thats fine, but it has nothing to do with zones, it's just the heat source. Zones require separate pipe runs for each zone, and these are turned on and off by zone valves. 3 required for 3 zones, though you can get away with one less is the HW is always on. If you already have a single zone system with no clear distinction between the pipework for upstairs heating, downstairs and cylinder, then splitting into 3 won't be a trivial plumbing job. Despite the individual cost of smart TRVs it could work out less expensive to use a number of them on the rads, allowing you to have as many zones as there are TRVs, but easily grouped in 2-3 zones. Smart thermostats can't work magic, they can't heat just the downstairs or bedrooms or HW, there have to be valves or pumps to turn on and off the flow to each zone. I'm guessing the 3K didn't include that?

    its an old house with an existing system, i am just upgrading the system

    the quote i have has this and its about 2k, bumping it up is a new hw cylinder and the actual control unit.
    Advanced Heating Controls Upgrade:
    • Motorised valves to separate heating "zones" within your home, including a completely
    independent hot water zone
    • Thermostats (room and cylinder) for automatic control of the heating of each individual
    zone
    • 7 day, digital programmer for full heating system with individual zone control. Various
    timer and "boost" options as standard for each zone
    • Optional programmers with remote access are available, for full control of your heating
    system via your computer or Smartphone application
    • Boiler interlock to prevent unnecessary boiler cycling
    • Timer with auto shut-off for your immersion heater
    • Pipe lagging for pipes in your hot-press if required
    • Electrical bonding of all pipes within your hot-press. This is a safety measure and is
    carried out as standard with our heating controls packages if needed
    • Installation fully compliant with relevant Building Regulations and industry best practices


  • Registered Users Posts: 4,586 ✭✭✭enfant terrible




  • Registered Users Posts: 6,723 ✭✭✭deezell


    Thats good enough to switch boilers, pumps and motorised valves. Thermostat contacts generally rated 3a which is plenty. Your connector block can be the same for neatness.


  • Registered Users Posts: 4,586 ✭✭✭enfant terrible


    deezell wrote: »
    Thats good enough to switch boilers, pumps and motorised valves. Thermostat contacts generally rated 3a which is plenty. Your connector block can be the same for neatness.

    Thanks for tge the help appreciated.


  • Registered Users Posts: 23,516 ✭✭✭✭ted1


    slayerking wrote: »
    I looking to replace my existing thermostats with Nests but struggling to find out how to do it given the setup I have.
    I have an air to water (electricity based) 2 zone heating system controlled by an EPH controls programmer (an R27 2 zone programmer with 2 x CM3 thermostats).

    Zone 1: downstairs heating
    Zone 2: upstairs heating

    We have hot water also but this is not controlled via a visible thermostat, its always hot and apparently how it supposed to be with a2w systems. Theres also a joule cylinder then in the hot press.

    I know I'll need to wire up the heat link somewhere, possibly where the programmer is and then wire in the thermostats.

    Has anyone set up a Nest on anything like this?
    I wouldn’t have thought that Nests would work well with heat pumps


  • Registered Users Posts: 6,723 ✭✭✭deezell


    ted1 wrote: »
    I wouldn’t have thought that Nests would work well with heat pumps

    Nest like any smart stat is just that, a stat. It doesn't 'know' what the heat source is, it just expects it to respond to a call for heat, then expects measured temperature to rise. This will depend on the usual factors, size if space, output of source, insulation and outside temperature. The smart part kicks in when it begins to record and evaluate the responses over time. It will use this to predict demand and modulate output to optimise the response. If the heat source has OpenTherm digital control the Nest ( or Tado) can fully address the capabilities of the heat source, not just switching it on but modulating the output flow and temperature, so that there are no peaks and dips in room temperature. And ordinary mechanical stat can have swings of plus or minus 3° mostly due to mechanical delay and thermal lead and lag in the system.


  • Registered Users Posts: 1,858 ✭✭✭dball


    If i have my smart thermostat set at 21 degrees (Tado) and i call for heat at 22 or above on any radiator with a smart TVR.

    Will i get the heat or do i need to have the smart thermostat above 21

    Thanks


  • Registered Users Posts: 6,723 ✭✭✭deezell


    dball wrote: »
    If i have my smart thermostat set at 21 degrees (Tado) and i call for heat at 22 or above on any radiator with a smart TVR.

    Will i get the heat or do i need to have the smart thermostat above 21

    Thanks
    TRVs will call the boiler via the smart stat regardless of its setting. If the radiators heating the smart stat area are not themselves fitted with TRVs, then this area will be heated though it's temperature target is already achieved, which may result in slight overheating of the main stat zone until the TRVs close and release the call for heat. Ideally all rads would have smart TRVs, to give exact room control, but in the case where you have only a few (or no) TRVs, even temperature is at best a compromise. Heating can be balanced the old fashioned way by trimming non TRV rads with the lockshield valve. This will tend to favour the radiators with TRVs so they close first before the main stat reaches target. If they are closed due to timer settings, (say bedrooms off during the day but living areas heated), then the flow to the non TRV rads is increased when the main stat calls.


  • Advertisement
  • Registered Users Posts: 10,952 ✭✭✭✭Stoner


    deezell wrote:
    TRVs will call the boiler via the smart stat regardless of its setting. If the radiators heating the smart stat area are not themselves fitted with TRVs, then this area will be heated though it's temperature target is already achieved, which may result in slight overheating of the main stat zone until the TRVs close and release the call for heat. Ideally all rads would have smart TRVs, to give exact room control, but in the case where you have only a few (or no) TRVs, even temperature is at best a compromise. Heating can be balanced the old fashioned way by trimming non TRV rads with the lockshield valve. This will tend to favour the radiators with TRVs so they close first before the main stat reaches target. If they are closed due to timer settings, (say bedrooms off during the day but living areas heated), then the flow to the non TRV rads is increased when the main stat calls.

    Would you not need at least one rad with no TRV on it