Home heating automation

Options
14647495152154

Comments

  • Registered Users Posts: 17,771 ✭✭✭✭keane2097


    deezell wrote: »
    Just check the ratings on your immersion. You imply it is a dual immersion, with sink/bath switch. See can you read the wattage or current consumption in Bath mode on the immersion casing .The FSTWifi is rated at 13A, A 230v 3Kw element is right on the limit of this. I would be a little uncomfortable with the switch working at its current limits.

    On further inspection it looks like I have two elements as a sticker on the tank says Immersion Heater 2/2.85kW 220V, and there's another sticker with

    Blue Neutral/Stat
    Brown Live/Sink
    Black Live/Bath
    Green/Yellow Earth

    Since I have no switch to specify whether I'm using the sink or bath element - just the standard Apt timer - I presume this means somebody tied off one or other of the wires for one of the elements or something?


  • Registered Users Posts: 6,722 ✭✭✭deezell


    keane2097 wrote: »
    deezell wrote: »
    Just check the ratings on your immersion. You imply it is a dual immersion, with sink/bath switch. See can you read the wattage or current consumption in Bath mode on the immersion casing .The FSTWifi is rated at 13A, A 230v 3Kw element is right on the limit of this. I would be a little uncomfortable with the switch working at its current limits.

    On further inspection it looks like I have two elements as a sticker on the tank says Immersion Heater 2/2.85kW 220V, and there's another sticker with

    Blue Neutral/Stat
    Brown Live/Sink
    Black Live/Bath
    Green/Yellow Earth

    Since I have no switch to specify whether I'm using the sink or bath element - just the standard Apt timer - I presume this means somebody tied off one or other of the wires for one of the elements or something?

    If it's just using the bath element, then that would be the 2.85Kw element, which consumes a tad shy of 3kw here because our voltage is 230V. This will pull a full 13a. If only the 2Kw sink element is used, this will pull 9 amps, within the limit of the Wi-Fi relay.
    You'd know of you only had sink element as only the top part of the tank would heat. It's possible though unlikely that both have been strapped together, requiring a hefty 22 amps.


  • Registered Users Posts: 6,722 ✭✭✭deezell


    Howya,

    My heating system consists of a combi-boiler for the water - no hot water tank - and 2 zones for the heating with a stat in each zone, upstairs and downstairs. I'm interested in installing Nest to control the system. What do I need to get? I assume 2 stats and a heatlink? Does each stat come with a heatlink?
    Learning Thermostat or Thermostat E?
    Each stat has. A heatlink, E heatlink has no HW control, which you don't need, so either stat will do.


  • Registered Users Posts: 2,710 ✭✭✭kaisersose77


    I have a 2 zone and hot water setup with best and noticed today that there was no hot water (have it scheduled for each morning). Then I realised the heating wasn't working either even though it appeared to be on the nests. When I checked the boiler nothing had tripped but I noticed that there was no light on at the fuse socket. I can't say I ever paid attention to whether the light ever came on but the boiler doesn't seem to power on as there are no lights on at all on it. I replaced the fuse but made no difference. The boiler is a baxi 35/80.

    What else could be up if the fuse light is not coming on? Can the best itself have any impact on stopping the boiler powering on? I pressed the heatsink buttons manually but made no difference.


  • Registered Users Posts: 6,722 ✭✭✭deezell


    I have a 2 zone and hot water setup with best and noticed today that there was no hot water (have it scheduled for each morning). Then I realised the heating wasn't working either even though it appeared to be on the nests. When I checked the boiler nothing had tripped but I noticed that there was no light on at the fuse socket. I can't say I ever paid attention to whether the light ever came on but the boiler doesn't seem to power on as there are no lights on at all on it. I replaced the fuse but made no difference. The boiler is a baxi 35/80.

    What else could be up if the fuse light is not coming on? Can the best itself have any impact on stopping the boiler powering on? I pressed the heatsink buttons manually but made no difference.
    Check your main house circuit breaker board. The breaker that supplies the boiler and it's fused socket may have tripped.


  • Advertisement
  • Registered Users Posts: 2,710 ✭✭✭kaisersose77


    Sorry should be clearer in my last post. Yes I checked that but nothing had tripped so am a bit dumbfounded.


  • Registered Users Posts: 6,722 ✭✭✭deezell


    Sorry should be clearer in my last post. Yes I checked that but nothing had tripped so am a bit dumbfounded.
    Next step is to check if there is power in the " fused socket" as you describe it. Do you mean a hardwired power cable point like this?

    cma052.jpg


  • Registered Users Posts: 2,710 ✭✭✭kaisersose77


    Yes like that but has no switch. Light is not coming on.

    Fuse is not blown and have tried other ones but made no difference.


  • Registered Users Posts: 6,722 ✭✭✭deezell


    Yes like that but has no switch. Light is not coming on.

    Fuse is not blown and have tried other ones but made no difference.

    If the neon is not lit then you have a break from your main circuit breaker board to the fused connector. Next step is to open it, pull out and using a phase tester screwdriver, check for mains on the incoming cable, and prior to this check if that cable hasn't popped out of its screw clamp terminal on the back side. Careful now, if you're not up to it call a sparks or phone a friend. There isn't by any chance a wall switch near or above this, as the connector itself is unswitched, it would be normal enough to have a switch before it.


  • Registered Users Posts: 2,710 ✭✭✭kaisersose77


    No switch around it just normal plug sockets and switches for washing machine etc. I didn't press any switches out of the ordinary prior to me noticing the issue. Looks I will have to get someone to have a look.

    Can the nest itself have any effect on power being sent to the hardwired power cable point?


  • Advertisement
  • Registered Users Posts: 6,722 ✭✭✭deezell


    No switch around it just normal plug sockets and switches for washing machine etc. I didn't press any switches out of the ordinary prior to me noticing the issue. Looks I will have to get someone to have a look.

    Can the nest itself have any effect on power being sent to the hardwired power cable point?

    The nest heatlink relay is rated quite low current, designed to trigger the boiler which itself is already powered always on. In your case you have 3 zones, so the nests will operate the zone valves, which in turn have relays which are all combined to call the boiler via its switched live call for heat terminal. Very old oil boilers might be powered directly from a timer/stat/valve relay , in which case the boiler only has power when the above call for heat. Modern boilers need a permanent mains supply, with a live out/ switched live return to instruct it to fire. If there is no power to the boiler, the relays on the valves won't power it as they should take their live from the boiler circuit, but they don't always. Either way they can't fire an unpowered boiler.


  • Registered Users Posts: 2,710 ✭✭✭kaisersose77


    Would the baxi 35/80 be considered a modern boiler? I asked a family member to have a look at he said there is power coming out of the fuse box but no power going into the unswitched fused socket.


  • Registered Users Posts: 6,722 ✭✭✭deezell


    If it's a gas boiler it will have permanent mains. Only some really old oil boilers could operate as hard on/off devices, no post purge after stat opens etc.
    If there's no power going in, rig a temporary power source via a nearby socket, put a 3 pin plug on the lead from boiler to the wall connection. Turn off power to nests/valves when doing in this, in case a live SL from a valve leaks back up the boiler wiring. They should all be powered from the one mains breaker anyway.
    Did you drill any holes in walls recently? Must be some reason the power is gone. We're there any other sockets or equipment on the same breaker as the boiler? Check if they are live. Wiring to multiple points is often daisy chained, wires can come loose at the back of a socket in the chain before the boiler.


  • Registered Users Posts: 2,710 ✭✭✭kaisersose77


    No drilling or anything that I can think of that might have affected power. Only started using nests again last week after 5/6 months without using them for heating (was using them for hot water only). Heating seemed to work fine in the evenings I had it on until the other morning I realised there was no hot water. Will ask a family member to check out what you suggested as he would be more technical than me. Breaker was for heating only. Haven't noticed any other power issues other than boiler.

    Thanks for the help.


  • Registered Users Posts: 664 ✭✭✭Fishy1


    Hi,
    Our heating system needs a new timer, old one packed in yesterday.
    We have a gas boiler with 3 zones (downstairs heating, upstairs heating & hot water tank).
    Any experts out there willing to recommend a solution? Hive or Nest, or something else? Don’t really want to have to pay monthly subscriptions (can’t recall, but I think one app requires this?)
    Am under pressure to decide as plumber will be calling!
    We’re with Electric Ireland if that’s any help!


  • Registered Users Posts: 10 paul g 1


    Fishy1 wrote: »
    Hi,
    Our heating system needs a new timer, old one packed in yesterday.
    We have a gas boiler with 3 zones (downstairs heating, upstairs heating & hot water tank).
    Any experts out there willing to recommend a solution? Hive or Nest, or something else? Don’t really want to have to pay monthly subscriptions (can’t recall, but I think one app requires this?)
    Am under pressure to decide as plumber will be calling!
    We’re with Electric Ireland if that’s any help!

    Nest won't work too many zones, I think
    Climote is the one with monthly fee but it's only like 6.00 I think.
    Haven't looked into hive
    EPH controller is another version, no monthly fee


  • Registered Users Posts: 533 ✭✭✭chuck eastwood


    Fishy1 wrote: »
    Hi,
    Our heating system needs a new timer, old one packed in yesterday.
    We have a gas boiler with 3 zones (downstairs heating, upstairs heating & hot water tank).
    Any experts out there willing to recommend a solution? Hive or Nest, or something else? Don’t really want to have to pay monthly subscriptions (can’t recall, but I think one app requires this?)
    Am under pressure to decide as plumber will be calling!
    We’re with Electric Ireland if that’s any help!

    Give electric Ireland sales line a ring. The often have specials on controls but at the very least they can tell you what is compatible with your system. Your plumber will probably only fit like for like, a sparks would be a better option for changing control setups


  • Registered Users Posts: 6,722 ✭✭✭deezell


    Are you looking for smart controls, remote app, schedules etc. Hive, Nest, Tado, Drayton Wiser can all control 2 CH and 1 HW zone. Electric Ireland may have deals for one stat with HW, you'll have to see what the second zone will add, but smart grants will cover a lot of it.


  • Registered Users Posts: 664 ✭✭✭Fishy1


    Thanks all,
    Crisis averted, plumber managed to fix the timer! Not sure how long the fix will last for, but it will give me time to research our options properly.


  • Registered Users Posts: 52 ✭✭comfort


    I finally got my boiler amended to have 3 zones (2 Heating, 1 hot water) where it was all 1 zone even though there were 3 controllers attached to the tank in the hot press.
    I stayed with the Hive system as had hive in operating the 1 complete zone as was able to operate with iPhone.

    Now I have the 3 zones and using Hive to operate all. Totally delighted for now :)


  • Advertisement
  • Registered Users Posts: 1,136 ✭✭✭maxamillius


    Hi Guys,

    I’m back on this again and am looking at pulling the trigger on a Nest.

    Current setup is;

    Oil boiler with integral analogue timeclock

    Analogue wall stat to control circulating pump

    Water can be heated either by gravity or by the pump.

    Is Nest a good option here? Straightforward to setup?

    Cheers


  • Registered Users Posts: 6,722 ✭✭✭deezell


    Hi Guys,

    I’m back on this again and am looking at pulling the trigger on a Nest.

    Current setup is;

    Oil boiler with integral analogue timeclock

    Analogue wall stat to control circulating pump

    Water can be heated either by gravity or by the pump.

    Is Nest a good option here? Straightforward to setup?

    Cheers

    Heres how to wire the nest heatlink receiver for your gravity HW/pumped CH system
    https://www.boards.ie/vbulletin/showpost.php?p=108836423&postcount=998

    Edit: your boiler is currently called I presume only by its timer, which must be on so CH will work when the stat calls the pump. Its unlikely the stat is wired back into the boiler. You will need to connect the boiler to whichever relay (nest, Tado) you chose, so that the boiler is fired only by the call from the relay. This is usually achieved at a terminal inside the boiler whic has a link from the Timer/Always on switch. removing this link and connecting to the Nest heatlink relay SL (switched live) will pass control of the boiler firing to the heatlink, for HW and CH events. You may need assistance with this step if you cannot identify the boiler SL input terminal


  • Registered Users Posts: 1,136 ✭✭✭maxamillius


    deezell wrote: »
    Heres how to wire the nest heatlink receiver for your gravity HW/pumped CH system
    https://www.boards.ie/vbulletin/showpost.php?p=108836423&postcount=998

    Edit: your boiler is currently called I presume only by its timer, which must be on so CH will work when the stat calls the pump. Its unlikely the stat is wired back into the boiler. You will need to connect the boiler to whichever relay (nest, Tado) you chose, so that the boiler is fired only by the call from the relay. This is usually achieved at a terminal inside the boiler whic has a link from the Timer/Always on switch. removing this link and connecting to the Nest heatlink relay SL (switched live) will pass control of the boiler firing to the heatlink, for HW and CH events. You may need assistance with this step if you cannot identify the boiler SL input terminal

    That’s right, Boiler is either on all the time, or on using the boilers time clock.

    Stat looks to be switching the live to the pump.


  • Registered Users Posts: 23,516 ✭✭✭✭ted1


    paul g 1 wrote: »
    Nest won't work too many zones, I think
    Climote is the one with monthly fee but it's only like 6.00 I think.
    Haven't looked into hive
    EPH controller is another version, no monthly fee

    Nest will work but requires 2 of them. Electric Ireland will do a deal


  • Registered Users Posts: 6,722 ✭✭✭deezell


    That’s right, Boiler is either on all the time, or on using the boilers time clock.

    Stat looks to be switching the live to the pump.

    Wire up as per that diagram and it will work perfectly. You can set water heating slots, and it will also heat when CH called.


  • Registered Users Posts: 1,136 ✭✭✭maxamillius


    deezell wrote: »
    Wire up as per that diagram and it will work perfectly. You can set water heating slots, and it will also heat when CH called.

    Great stuff thanks for that Deezel


  • Registered Users Posts: 1,136 ✭✭✭maxamillius


    deezell wrote: »
    Wire up as per that diagram and it will work perfectly. You can set water heating slots, and it will also heat when CH called.

    Presumably I just link the live and switched live at the current wall stat and then set up the nest as wireless?


  • Registered Users Posts: 6,722 ✭✭✭deezell


    Presumably I just link the live and switched live at the current wall stat and then set up the nest as wireless?

    You'll need to do a bit more than that. Your current stat does no more than turning the pump on and off, and you have to manually turn or time the boiler on and off. To get the nest to turn boiler and pump on for CH, and boiler only for HW, requires wiring the nest relay (Heatlink) box into the boiler, to fire it instead of its built in timer. You set up the new timer schedules on the nest. The SL for CH goes straight to the pump, replacing the old stat live and SL, which are redundant.
    Now the nest is powered by a small adaptor like a phone charger, and you can plug it in and sit it on a stand anywhere, it's wireless to the heatlink. If you want to wall mount the nest, you need to run this power to it. If you mount the nest where the old stat was, you can reuse the now redundant live and SL wires from the old stat to bring power from the 12v low voltage terminals on the heatlink box to the wall plate of the nest, making a very neat job of it. These wires will also carry a wired digital version of the wireless connection, so distance/walls to the heatlink is no longer an issue. It's critical that If you reuse these wires that they are identified at the pump/boiler end, isolated and disconnected from any mains (at either end), or you could end up frying the nest. Terminals marked T1 and T2 12v are the ones.


  • Registered Users Posts: 1,136 ✭✭✭maxamillius


    deezell wrote: »
    You'll need to do a bit more than that. Your current stat does no more than turning the pump on and off, and you have to manually turn or time the boiler on and off. To get the nest to turn boiler and pump on for CH, and boiler only for HW, requires wiring the nest relay (Heatlink) box into the boiler, to fire it instead of its built in timer. You set up the new timer schedules on the nest. The SL for CH goes straight to the pump, replacing the old stat live and SL, which are redundant.
    Now the nest is powered by a small adaptor like a phone charger, and you can plug it in and sit it on a stand anywhere, it's wireless to the heatlink. If you want to wall mount the nest, you need to run this power to it. If you mount the nest where the old stat was, you can reuse the now redundant live and SL wires from the old stat to bring power from the 12v low voltage terminals on the heatlink box to the wall plate of the nest, making a very neat job of it. These wires will also carry a wired digital version of the wireless connection, so distance/walls to the heatlink is no longer an issue. It's critical that If you reuse these wires that they are identified at the pump/boiler end, isolated and disconnected from any mains (at either end), or you could end up frying the nest. Terminals marked T1 and T2 12v are the ones.

    Got ya, I think I’d remove the old wall stat and mount the nest in place, so basically then I’m using the old live/sw live to carry the 12v from the heat link terminals.

    Think that all makes sense!