  • Registered Users Posts: 2,780 ✭✭✭Buffman


    I'll keep you posted, I need to find a suitable adaptor for the Leaf to connect to a Type 2 Zappi


    I saw something like that on adverts, not sure if it's available.


    https://www.adverts.ie/other/electric-vehicleswap-your-charger-from-type-2-type-1-32-amp/23750836

    Alternatively it could probably be used in a garage without any issues


    Ye, it would be fine indoors, or seal it with good quality sealant on the cracks and all around where it meets the wall.

    FYI, if you move to a 'smart' meter electricity plan, you CAN'T move back to a non-smart plan.

    You don't have to take a 'smart' meter if you don't want one, opt-out is available.

    Buy drinks in 3L or bigger plastic bottles or glass bottles to avoid the DRS fee.



  • Registered Users Posts: 13,450 ✭✭✭✭fits


    Tethered zappi plus hub is coming up just over 1k on myenergi just for units delivered. Has anyone who bought recently done better than that?


  • Registered Users Posts: 235 ✭✭Patmwgs


    fits wrote: »
    Tethered zappi plus hub is coming up just over 1k on myenergi just for units delivered. Has anyone who bought recently done

    there are other smart chargers out there with as much features as the zappi for alot less money. Eo mini pro, sync ev and more.


  • Registered Users Posts: 13,450 ✭✭✭✭fits


    Patmwgs wrote: »
    fits wrote: »
    Tethered zappi plus hub is coming up just over 1k on myenergi just for units delivered. Has anyone who bought recently done

    there are other smart chargers out there with as much features as the zappi for alot less money. Eo mini pro, sync ev and more.


    We want to install solar next year. We also have an air source heat pump and an induction hub. And I need to be able to schedule charging reliably. Can the others manage all that?


  • Registered Users Posts: 235 ✭✭Patmwgs


    fits wrote: »
    Patmwgs wrote: »


    We want to install solar next year. We also have an air source heat pump and an induction hub. And I need to be able to schedule charging reliably. Can the others manage all that?

    I have sync ev which has dynamic load management, with optional ct clamp for protection of main fuse. Scheduled charging which works for the id3, built in earthing, rfid card, dc leakage,
    Solar will be added this month with app update. Eo mini pro can do the same agin with ct clamp.


  • Advertisement
  • Registered Users Posts: 6,975 ✭✭✭nkay1985


    Got my EO Mini Pro installed yesterday. Ordered with Electric Ireland but you deal with KN Networks from then. Received two phone calls, as well as an email, in advance to confirm the details of the visit and screen for Covid issues. The installed was a lovely guy and did a nice, neat job. He was able to use the meter box, rather than having to go through the wall and into the main fuse board. Said that change only came in two weeks ago. Ideal!

    Gave it a little test charge last night as the car was fully charged when I picked it up. Thanks for the advice.


  • Registered Users Posts: 6,975 ✭✭✭nkay1985


    Got my EO Mini Pro installed yesterday. Ordered with Electric Ireland but you deal with KN Networks from then. Received two phone calls, as well as an email, in advance to confirm the details of the visit and screen for Covid issues. The installed was a lovely guy and did a nice, neat job. He was able to use the meter box, rather than having to go through the wall and into the main fuse board. Said that change only came in two weeks ago. Ideal!

    Gave it a little test charge last night as the car was fully charged when I picked it up. Thanks for the advice.

    554187.jpg


  • Moderators, Society & Culture Moderators Posts: 39,039 Mod ✭✭✭✭Gumbo


    nkay1985 wrote: »
    Got my EO Mini Pro installed yesterday. Ordered with Electric Ireland but you deal with KN Networks from then. Received two phone calls, as well as an email, in advance to confirm the details of the visit and screen for Covid issues. The installed was a lovely guy and did a nice, neat job. He was able to use the meter box, rather than having to go through the wall and into the main fuse board. Said that change only came in two weeks ago. Ideal!

    Gave it a little test charge last night as the car was fully charged when I picked it up. Thanks for the advice.

    Nice neat job.
    That regulation was clarified in the March Safe Electric newsletter.
    Get yourself a little hook to hang the excess cable from.


  • Registered Users Posts: 6,975 ✭✭✭nkay1985


    Gumbo wrote: »
    Nice neat job.
    That regulation was clarified in the March Safe Electric newsletter.
    Get yourself a little hook to hang the excess cable from.

    Yeah, I thought one might have been provided when I went for the tethered version but seemingly not. I'll have to figure something out.


  • Moderators, Sports Moderators Posts: 18,940 Mod ✭✭✭✭slave1


    Cheap can of white spray paint currently in Lidl/Aldi and I’d spray the isolator switch totally white, but that’s just me...

    My stuff for sale on Adverts inc. EDDI, hot water cylinder, roof rails...

    Public Profile active ads for slave1 (adverts.ie)



  • Advertisement
  • Registered Users Posts: 848 ✭✭✭mun1


    Anyone got details of a good installer in limerick area , could they drop me a PM please. probably hoping to go for Zappi


  • Registered Users Posts: 11,257 ✭✭✭✭the_amazing_raisin


    Has anyone ever heard of an EV charger causing false alarms from smoke detectors?

    We've had an EO Mini for s few years which charges the Leaf without issues.

    However, I've noticed that since I got the ID.4, the smoke alarms seem to go off at some point while it's charging

    To be clear, it's a false alarm, there's no fire or smoke and every time I've checked the charger and fuse panel and they aren't overheating. Also, the alarm that goes off is in the hallway, nowhere near either the charger or the fuse panel

    The only major difference is that the ID.4 charges at 32A while the Leaf charges at 16A. But the cables and fuses are all rated for that, so it shouldn't be a problem

    My theory is that between the charger and the heat pump, the house is drawing a lot of current. Not enough to trip fuses but I'm wondering will it cause a voltage drop for a moment which might be interfering with the fire alarms?

    It's quite possible it's all a coincidence, and the fire alarm is just busted, but my worry is that if I replace it now the problem won't go away

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Moderators, Society & Culture Moderators Posts: 39,039 Mod ✭✭✭✭Gumbo


    Has anyone ever heard of an EV charger causing false alarms from smoke detectors?

    We've had an EO Mini for s few years which charges the Leaf without issues.

    However, I've noticed that since I got the ID.4, the smoke alarms seem to go off at some point while it's charging

    To be clear, it's a false alarm, there's no fire or smoke and every time I've checked the charger and fuse panel and they aren't overheating. Also, the alarm that goes off is in the hallway, nowhere near either the charger or the fuse panel

    The only major difference is that the ID.4 charges at 32A while the Leaf charges at 16A. But the cables and fuses are all rated for that, so it shouldn't be a problem

    My theory is that between the charger and the heat pump, the house is drawing a lot of current. Not enough to trip fuses but I'm wondering will it cause a voltage drop for a moment which might be interfering with the fire alarms?

    It's quite possible it's all a coincidence, and the fire alarm is just busted, but my worry is that if I replace it now the problem won't go away

    Have you narrowed it down to one particular detector or is it them all?


  • Registered Users Posts: 12,116 ✭✭✭✭KCross


    Has anyone ever heard of an EV charger causing false alarms from smoke detectors?

    Probably just needs a new battery. Did you check that?


  • Registered Users Posts: 11,257 ✭✭✭✭the_amazing_raisin


    Gumbo wrote: »
    Have you narrowed it down to one particular detector or is it them all?

    Seems to be the hallway one every time, they're interlinked so when they go off I have to turn the one off that detected smoke

    As I said, it's most likely that the smoke alarm has gone bad. The problem is that if I replace it I have to replace them all because they're linked

    Before I spend that money I'd like to try and narrow down the problem first

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 235 ✭✭Patmwgs


    Has anyone ever heard of an EV charger causing false alarms from smoke detectors?

    We've had an EO Mini for s few years which charges the Leaf without issues.

    However, I've noticed that since I got the ID.4, the smoke alarms seem to go off at some point while it's charging

    To be clear, it's a false alarm, there's no fire or smoke and every time I've checked the charger and fuse panel and they aren't overheating. Also, the alarm that goes off is in the hallway, nowhere near either the charger or the fuse panel

    The only major difference is that the ID.4 charges at 32A while the Leaf charges at 16A. But the cables and fuses are all rated for that, so it shouldn't be a problem

    My theory is that between the charger and the heat pump, the house is drawing a lot of current. Not enough to trip fuses but I'm wondering will it cause a voltage drop for a moment which might be interfering with the fire alarms?

    It's quite possible it's all a coincidence, and the fire alarm is just busted, but my worry is that if I replace it now the problem won't go away

    Have you load balancing setup on the charger? Check out screenshot below.


  • Registered Users Posts: 11,257 ✭✭✭✭the_amazing_raisin


    Patmwgs wrote: »
    Have you load balancing setup on the charger? Check out screenshot below.

    No load balancing, my charger doesn't have that yet

    I saw the same thing, around the time it happened last night, the charger, heat pump and probably the dishwasher were on, which was probably pushing the house supply closer to the limit

    The heat pump in particular would have some inductive loads, so I guess it could cause some voltage spiking when switching on and off

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 235 ✭✭Patmwgs


    No load balancing, my charger doesn't have that yet

    I saw the same thing, around the time it happened last night, the charger, heat pump and probably the dishwasher were on, which was probably pushing the house supply closer to the limit

    The heat pump in particular would have some inductive loads, so I guess it could cause some voltage spiking when switching on and off

    You could test the theory with the heat pump off and then back on while charging.


  • Registered Users Posts: 20,021 ✭✭✭✭Cyrus


    Seems to be the hallway one every time, they're interlinked so when they go off I have to turn the one off that detected smoke

    As I said, it's most likely that the smoke alarm has gone bad. The problem is that if I replace it I have to replace them all because they're linked

    Before I spend that money I'd like to try and narrow down the problem first

    It's most likely a bad alarm had something similar are you sure you need to change them all, I know ours are linked but have had a few replaced


  • Moderators, Society & Culture Moderators Posts: 39,039 Mod ✭✭✭✭Gumbo


    Seems to be the hallway one every time, they're interlinked so when they go off I have to turn the one off that detected smoke

    As I said, it's most likely that the smoke alarm has gone bad. The problem is that if I replace it I have to replace them all because they're linked

    Before I spend that money I'd like to try and narrow down the problem first

    Remove the one in the hall and see if it still happens. Or swap it with one from another room.

    The interlinking is just the connected wiring. You can replace one. You may have to disconnect the connector and wire the 2 cables into the connector of the new detector though.

    I had to do this at home as my landing one was faulty and they had stopped making them. The interlinked system will still work as it’s just a signal wire.


  • Advertisement
  • Registered Users Posts: 11,257 ✭✭✭✭the_amazing_raisin


    Gumbo wrote: »
    Remove the one in the hall and see if it still happens. Or swap it with one from another room.

    The interlinking is just the connected wiring. You can replace one. You may have to disconnect the connector and wire the 2 cables into the connector of the new detector though.

    I had to do this at home as my landing one was faulty and they had stopped making them. The interlinked system will still work as it’s just a signal wire.

    That's good to know, I had assumed the signalling was proprietary between vendors, didn't realise it was so simplistic

    I might swap it with the living room one and run some tests during the week. Or leave it in battery mode for the short term as it won't set off the other alarms then

    I'll probably end up replacing the hallway alarm. Was speaking to the neighbours and they've also had issues with false alarms. All of the alarms were installed by the builder and are the same brand

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 117 ✭✭Coill1


    Anyone bought / or used the Irish Verde Ev charger? It’s available for €299 + VAT. I’d like to buy an Irish one preferably, as long as it runs ok..
    Thanks


  • Registered Users Posts: 11,257 ✭✭✭✭the_amazing_raisin


    Coill1 wrote: »
    Anyone bought / or used the Irish Verde Ev charger? It’s available for €299 + VAT. I’d like to buy an Irish one preferably, as long as it runs ok..
    Thanks

    Never heard of it

    I'd personally be wary about choosing a brand which isn't well established, support might not be great down the line

    I'm all for buying Irish, but there's plenty of Irish copanies specialising in the install of well know chargers who might be better suited to you

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 454 ✭✭robbie_63


    Hi Folks,

    We are looking at doing a deal on a new Skody Enyaq 60 in the next few days, should be ready to collect in the next month or so,

    Would the normal Untethered charger from Electric Ireland work fine for this?

    I know Skoda have their own brand chargers but I wanted to check if the normal one would work fine as I know they are quicker than trying to get Skoda to do it,

    Cheers

    R


  • Registered Users Posts: 20,021 ✭✭✭✭Cyrus


    robbie_63 wrote: »
    Hi Folks,

    We are looking at doing a deal on a new Skody Enyaq 60 in the next few days, should be ready to collect in the next month or so,

    Would the normal Untethered charger from Electric Ireland work fine for this?

    I know Skoda have their own brand chargers but I wanted to check if the normal one would work fine as I know they are quicker than trying to get Skoda to do it,

    Cheers

    R

    any type 2 charger will be fine.


  • Registered Users Posts: 454 ✭✭robbie_63


    Perfect thanks


  • Registered Users Posts: 12,116 ✭✭✭✭KCross


    robbie_63 wrote: »
    Would the normal Untethered charger from Electric Ireland work fine for this?

    Any untethered charge point will work.

    Do consider tethered though as messing around with a cable (in and out of your boot in the rain etc) will get tiresome but it is a personal preference as some people dont like the look of the cable.


  • Registered Users Posts: 454 ✭✭robbie_63


    Only reason I was thinking of untethered is so we can change the cable if it gets damaged or take it with us in the car


  • Registered Users Posts: 12,116 ✭✭✭✭KCross


    robbie_63 wrote: »
    Only reason I was thinking of untethered is so we can change the cable if it gets damaged or take it with us in the car

    Neither of those are good reasons! :)

    A cable should be supplied with the car and you leave it in the car permanently for when you are travelling. Use the tethered cable for daily charging.

    The cables are robust enough and can be replaced if you do happen to damage the tethered one. No major/common reason for it to be damaged though.


  • Advertisement
  • Registered Users Posts: 454 ✭✭robbie_63


    Yeah your probably right just overthinking it with Kids & Dog I don't want to have to get an electrician out if they do manage to break it,

    Any idea what length the cable is on the tethered cable? I don't see any mention on the Electric Ireland site