Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Zone changing resistance intermittently..

Options
  • 07-10-2018 12:12pm
    #1
    Registered Users Posts: 96 ✭✭


    Europlex/Signet 200 w a zone through an expander whose resistance fluctuates between 2k2, 3k9, 4k6, all the way to 25k when I "Monitor" the zone. (at the moment I have it isolated to prevent false alarms).

    It doesn't seem to be the expander because I put a resistor across the terminals and it stayed stable.

    Something in the zone, somewhere in the hidden cabling.

    Anyone come across this before and any idea of what I shoukd be looking for? It seems odd (maybe it's not?)that a cable would "float" like this...


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators Posts: 24,789 Mod ✭✭✭✭KoolKid


    Its either a faulty sensor,contact or connection on that zone.
    Disconnect the zone from the expander & remove any end of line resistors,
    Set you meter to continuity and connect the pair to the 2 meter leads.

    Make a note of the reading in ohms. One by one tap every sensor & open and close every contact. After a tap or an open close the resistance should return to the around the same value. If it does not disconnect that device , close of the pair wired into it & move on. Replace any units that are faulty.


Advertisement