Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Pipe stat setting

  • 24-11-2018 11:28am
    #1
    Registered Users Posts: 560 ✭✭✭


    Hi,
    Have a pipe stat in hot press that turns on the circulation pumps to send the hot water around the house, using a grant 50/70 boiler and Stanley Tara back boiler stove,
    Wondering what would the optimal temp setting for the pipe stat be?
    Cheers!


Comments

  • Registered Users, Registered Users 2 Posts: 429 ✭✭Blowheads


    robclay26 wrote: »
    Hi,
    Have a pipe stat in hot press that turns on the circulation pumps to send the hot water around the house, using a grant 50/70 boiler and Stanley Tara back boiler stove,
    Wondering what would the optimal temp setting for the pipe stat be?
    Cheers!

    I assume you mean the pipe stat is on the hot flow from the stove? If yes then it should be as close as physically possible to the stove
    Should be set in the 55-60 range in general. To hot and the stove will boil the water before the 55 degrees hits the stat and turns on the pump, to low and I heard it sweats the stove which is not good either

    If we light a better then will have to turn down the stat to bring on the pump and circulate the water, as soon as it starts to flow can turn it up again. Obviously the hotter the stat the warmer the water and rads so you might need to play around to find the optimal number in your set up