Shower cord pull cord neon

Options
  • 17-07-2019 1:53pm
    #1
    Registered Users Posts: 1


    I am replacing a shower pull cord but the neon light wires broke off from the pre terminated terminals. Just wondering if i wired one of the cables from the neon light into the live load terminal( outgoing) and the other wire from the neon into the netural load terminal ( outgoing ) this should light up the neon safely once the cord is pulled to the on position?


Comments

  • Registered Users Posts: 208 ✭✭keithdub


    Yes some brands are wired like that but all are 230v


  • Registered Users Posts: 1,936 ✭✭✭whizbang


    There is probably a resistor inline, on one of the Neon wires. try to keep it intact.