Help with Thermostat Wiring Diagram

Options
  • 12-02-2020 6:46pm
    #1
    Registered Users Posts: 225 ✭✭


    Hi all

    one of the thermostats in the house is gone so went to Heat Merchants to get a replacement. i figured replacing it would be simple as changing a light switch or power outlet but i cant figure out these wiring diagrams!!!


    this is the wiring diagram of the current broken thermostat (Towerstat RS)
    https://live.staticflickr.com/2726/4422369290_24ca4b85b5_b.jpg


    and this is the new EPH CM2
    https://www.ephcontrols.com/wp-content/uploads/2017/05/20171129_CM_-_DS_JW.pdf


    can someone tell me how these two diagrams line up with each other?
    interesting to note that my current thermostat has 3 wires connected whereas the diagram for the new one only seems to use 2. maybe i've got the wrong model?


Comments

  • Registered Users Posts: 4,745 ✭✭✭meercat


    In your old thermostat use cables connected to 1&3 and connected them to 1&2 in your new thermostat. Not sure if your 3rd cable is a neutral or earth (post photo or say where it’s connected ). If it’s a neutral then it’s not required for your new stat.


  • Registered Users Posts: 225 ✭✭gaza4


    meercat wrote: »
    In your old thermostat use cables connected to 1&3 and connected them to 1&2 in your new thermostat. Not sure if your 3rd cable is a neutral or earth (post photo or say where it’s connected ). If it’s a neutral then it’s not required for your new stat.


    thanks for the reply, here is a pic of the old thermostat still wiring up to the wall, hope that helps



    85146749_10218345199116243_4377970090205773824_o.jpg?_nc_cat=109&_nc_ohc=okOmVKCkOdsAX8xXh5M&_nc_ht=scontent.fdub4-1.fna&_nc_tp=6&oh=7d99b09e3d92a196a5948db8dcb67afa&oe=5ED1BE13


  • Registered Users Posts: 4,745 ✭✭✭meercat


    The blue wire is not required but can be connected into N of your new thermostat


  • Registered Users Posts: 3,514 ✭✭✭John.G


    Would the old towerstat have a heat anticipator whereas the CM2 doesn't?.


  • Registered Users Posts: 225 ✭✭gaza4


    John.G wrote: »
    Would the old towerstat have a heat anticipator whereas the CM2 doesn't?.

    What is the function of a heat anticipator?


  • Advertisement
  • Registered Users Posts: 3,514 ✭✭✭John.G


    Its to stop too rapid switching and over/undershoot of a thermostat, probably not seen that often in roomstats since the room temperature changes at a relatively slow rate.

    The neutral in your old stat was/could be probably used in conjunction with a indicating ON LED from the switched live.


  • Registered Users Posts: 34,013 ✭✭✭✭listermint


    Ideal time to replace with sonoff TH16 and a sonoff temp sensor.


    Remote control , Google assistant control , scheduled timer setups