Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Netatmo knocks of the power to my Gas Boiler

  • 25-03-2020 7:16am
    #1
    Registered Users Posts: 2


    About two years ago I availed of the free Netatmo offer by switching to Energia. The Netatmo device works perfectly fine. Several months later I got my boiler serviced by Bhord Gais and the guy who serviced it said " The power to your boiler is turned off, it should always have power on, the led light display panel should be lit up ".
    What's happening is, when Netatmo is activated it switches the boiler on and you will here the boiler starting up and when Netatmo switches off you can here the boiler switch off. Apparently the boiler should always have power going to it.
    My wife recalled that before the Netatmo was installed you could see by the display there was always power going to it. I did ring Energia but kind of got fobbed off so I gave up. Has anyone else experienced the same issue regarding Netatmo powering off your boiler. I am told the warranty on boiler is void if there is no constant power going to boiler. Boiler is 3 years old and is a Vaillant Eco Tech plus 634 boiler.


Comments

  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    So basically the netatamo is a thermostat/switch....

    It would be set up like this for an oil boiler but not gas.
    Well shouldn't be of course.....

    Just needs to be wired in correctly.


  • Registered Users, Registered Users 2 Posts: 2,045 ✭✭✭Cerco


    Get back the people who installed the Netamo.
    Seems to me the permanent line (live) is being switched instead of the switched line or maybe both.


  • Moderators, Home & Garden Moderators Posts: 6,305 Mod ✭✭✭✭Wearb


    So basically the netatamo is a thermostat/switch....

    It would be set up like this for an oil boiler but not gas.
    Well shouldn't be of course.....

    Just needs to be wired in correctly.

    As above. They should come back and wire it correctly.

    Just fyi, lots of oil boilers also need a permanent live.

    Please follow site and charter rules. "Resistance is futile"



  • Registered Users, Registered Users 2 Posts: 24,644 ✭✭✭✭punisher5112


    Wearb wrote: »
    As above. They should come back and wire it correctly.

    Just fyi, lots of oil boilers also need a permanent live.

    Yes but that tends to be on the frost protection thermostat.

    Old school ones anyway.


  • Moderators, Home & Garden Moderators Posts: 6,305 Mod ✭✭✭✭Wearb


    Yes but that tends to be on the frost protection thermostat.

    Old school ones anyway.


    Also for pump over-run and also some with post purge.

    Please follow site and charter rules. "Resistance is futile"



  • Advertisement
  • Registered Users Posts: 2 crunchyfriday


    So basically the netatamo is a thermostat/switch....

    It would be set up like this for an oil boiler but not gas.
    Well shouldn't be of course.....

    Just needs to be wired in correctly.

    Thank you so much for your advice. I will get back in touch with provider.