Wi-fi immersion timer: spec ok?

Options
  • 03-05-2020 2:07pm
    #1
    Posts: 0


    Hi folks - with a bit of time on my hands I'm thinking of replacing our old immersion timer with a new wi-fi model.

    I have my eyes on this one: https://www.amazon.co.uk/gp/product/B07T7N9LFJ/ref=ask_ql_qh_dp_hza

    It's rated for 20A. We have 2x 3kw heaters in the tank and our current timer is a Horstmann Quartz E7. No sink/shower switches etc; just the Horstmann unit.

    Any problems or am I good to go?

    Thanks a million.


Comments

  • Registered Users Posts: 835 ✭✭✭autumnalcore


    Well straight off the bat 2 x 3000w is more than 20A

    Secondly that is some random bit of rebadged chinese junk with a chinese junk relay. Who knows what the duty cycle / continuous rating for the relay is or the thickness of the copper / size of the traces on the board, quality of soldering etc.

    I wouldn't connect it to anything near 20A in my house but you could I suppose connect it to a relay / contactor from a respectable manufacturer.


  • Closed Accounts Posts: 168 ✭✭Loozer


    Well straight off the bat 2 x 3000w is more than 20A

    Secondly that is some random bit of rebadged chinese junk with a chinese junk relay. Who knows what the duty cycle / continuous rating for the relay is or the thickness of the copper / size of the traces on the board, quality of soldering etc.

    I wouldn't connect it to anything near 20A in my house but you could I suppose connect it to a relay / contactor from a respectable manufacturer.

    Only 1 heater can operate at a time, so it'll be 3kw max

    You have to leave the horstmann there and fit the controller before it, if you're going using it


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Well straight off the bat 2 x 3000w is more than 20A

    13 amps is the most it will be at a time. Unless someone has connected both together.


  • Closed Accounts Posts: 168 ✭✭Loozer


    Bruthal wrote: »
    13 amps is the most it will be at a time. Unless someone has connected both together.

    They're separate heaters so you could i suppose with 2 supplies but the horstmann obviously only takes a single 16/20 supply and switches between the 2

    Biggest issue is people swopping them out for these controllers which don't isolate supply


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Loozer wrote: »
    They're separate heaters so you could i suppose with 2 supplies but the horstmann obviously only takes a single 16/20 supply and switches between the 2

    O yes, ill have to start looking at posts properly


  • Advertisement
  • Registered Users Posts: 2,320 ✭✭✭Chet T16




  • Registered Users Posts: 311 ✭✭leinster93


    Chet T16 wrote: »

    I have one for immersion and one for central heating installed a year now. Work well without any issues. Works only with 2.5GHz on router - not the 5 GHz which took ages to figure


  • Closed Accounts Posts: 168 ✭✭Loozer


    Bruthal wrote: »
    O yes, ill have to start looking at posts properly

    That wi-fi controller isn't to going work properly inline before that hortsmann timer anyhow

    The hortsmann isn't suitable for having the supply interrupted like that, would be ok with a regular dual-immersion and switch.

    You would need to set it up differently for wi-fi control, prob be better off the way it is tbh


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    If using a wifi controlled setup, you dont want the timer there at all.


  • Closed Accounts Posts: 168 ✭✭Loozer


    Bruthal wrote: »
    If using a wifi controlled setup, you dont want the timer there at all.

    No you're right, I should have seen that before before posting first off

    WiFi controller +replace the hortsmann with a standard immersion switch for changeover and isolation might do i suppose


  • Advertisement
  • Registered Users Posts: 34,013 ✭✭✭✭listermint


    WiFi control on feed into normal switch. Bath or sink and on off.

    That's it.


  • Closed Accounts Posts: 168 ✭✭Loozer


    listermint wrote: »
    WiFi control on feed into normal switch. Bath or sink and on off.

    That's it.
    It will work but

    If it's an all electric apartment/home it might be a pain as you may want the fixed on period overnite to provide a full cylinder of hot water every morning

    In that case you would be better with a separate supply for the WiFi and top heater


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    Loozer wrote: »

    WiFi controller +replace the hortsmann with a standard immersion switch for changeover and isolation might do i suppose

    Yea that's the usual setup. Contactor probably recommended as well.


  • Registered Users Posts: 25,461 ✭✭✭✭coylemj


    I've researched this in the past and there appears to be no timer available in this part of the world which can handle a dual element system and give you full control over both of them. The situation in the UK appears to be that a two-channel or dual-element (Sink/Bath) timer will only activate the Bath element during 'Economy 7' off-peak hours.

    For example, the instructions for the Sangamo POWERSAVER DUAL FLEXI says the folllowing....

    .... this controller is not freely programmable, you can minimise the program times within your off peak period but not go outwith it,


    The net effect is that you cannot set the timer to activate the Bath element during the day and the 'Boost' button only activates the Sink element. If you have two separate elements that operate independent of one another and you want full control over both of them, you need two timers.

    I have the power feed going into this timer unit and then into a standard Sink/Bath switch. I rarely use the Bath element so it fulfills my requirements. It talks to my house Wi-Fi so I can control it from anywhere, there are Android and iOS versions of the app.

    3051.jpg

    https://www.timeguard.com/products/time/immersion-and-general-purpose-timeswitches/wi-fi-controlled-fused-spur


  • Registered Users Posts: 10,952 ✭✭✭✭Stoner


    https://www.boards.ie/vbulletin/showthread.php?p=104541361

    The timeguard option has been tracked well here.

    It has an advantage that it is in a UK box and it's fused like a standard UK and Irish spur so you can remove the fuse to isolate it. It's also UK made and rated for continuous load.

    Again the manual switching to sink or bath is required

    Some people are using the 16Amp sonoff in the same way although I'd question the continuous load capabilities, cable connections and you'd need to add a fused spur to isolate and fuse down the 20 amp MCB most likely feeding it.

    However I'm pretty sure we'd a recent poster who found a unit on Amazon, with one input and it could switch and interlocked output. I can't remember but have a search. I'd a quick look already. Or else try the iot forum


  • Posts: 0 [Deleted User]


    Thanks for the input, folks. Shall weigh up the options.