Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Earth size for trunking

Options
  • 28-05-2020 12:20am
    #1
    Registered Users Posts: 12


    Doing a flat rewire and ran a new 16 T&E to a new outdoor meter cabinet. I ran it down the inside of the external wall which is battoned out, in 50mm steel trunking and bonded the trunking with a 10mm earth from MET, but wondering should it be bonded with a 16mm earth?


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,596 Mod ✭✭✭✭2011


    10 mm is fine for bonding the trunking.


Advertisement