Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Quick Electrical Question - 1.5mm T&E cable socket spur- do I need a fuse?

  • 30-06-2020 6:28pm
    #1
    Registered Users, Registered Users 2 Posts: 343 ✭✭


    Hoping somebody can help me. I recently ran a spur from a main power socket upstairs in my house. This spur feeds a socket in the attic (unused, just fixed it up there whilst I was doing the job) and a socket for a TV mounted high on a bedroom wall.

    I've recently realised that I used 1.5mm twin and earth cable instead of 2.5mm. The spur leaves the socket vertically into the attic behind plasterboard. It feeds the non-used attic socket, a TV and a Roku streaming stick.

    I believe I should add a 13A fuse before the first socket to make this fully safe, is that correct? Replacing the cable with 2.5mm T&E is not an option anymore due to access.


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,603 Mod ✭✭✭✭2011


    Any cable needs to be protected by an overcurrent protective device (such as a fuse or MCB) that will disconnect it before the the current reaches a level that the causes damage. Most likely your socket circuit is protected by an MCB rated at 20 amp or more. This is beyond what a 1.5 mm sq. cable is rated for. As such it would be safer to fuse it down to 13A or less. Wiring any socket in 1.5 mm sq. cable even when protected by a fuse like this is considered bad practice but it would be significantly better than leaving as is.


  • Registered Users, Registered Users 2 Posts: 343 ✭✭frankled


    2011 wrote: »
    Any cable needs to be protected by an overcurrent protective device (such as a fuse or MCB) that will disconnect it before the the current reaches a level that the causes damage. Most likely your socket circuit is protected by an MCB rated at 20 amp or more. This is beyond what a 1.5 mm sq. cable is rated for. As such it would be safer to fuse it down to 13A or less. Wiring any socket in 1.5 mm sq. cable even when protected by a fuse like this is considered bad practice but it would be significantly better than leaving as is.

    Perfect thanks for that. I'm glad I copped it.


  • Registered Users, Registered Users 2 Posts: 343 ✭✭frankled


    2011 wrote: »
    Any cable needs to be protected by an overcurrent protective device (such as a fuse or MCB) that will disconnect it before the the current reaches a level that the causes damage. Most likely your socket circuit is protected by an MCB rated at 20 amp or more. This is beyond what a 1.5 mm sq. cable is rated for. As such it would be safer to fuse it down to 13A or less. Wiring any socket in 1.5 mm sq. cable even when protected by a fuse like this is considered bad practice but it would be significantly better than leaving as is.

    To give you an update, I wasted both of our time as it is actually 2.5mm sq. cable I used after all! Apologies and thanks again.