Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Bled a radiator last night and heating not working now

  • 29-07-2020 8:16pm
    #1
    Registered Users Posts: 112 ✭✭


    Hi. I bled a radiator last night when the heating was on. Today the heating isn't working. I'm guessing I caused an airlock or something. Are radiators not supposed to be bled when the heating is on? I have an outdoor Firebird Envirogreen. Does anyone know if I can fix this problem or would I need to call a plumber? When I turn the heating on now, I can hear gurgling like it's on but no radiator heats up.


Comments

  • Closed Accounts Posts: 1,662 ✭✭✭Duke of Url


    I did this before. Called a plumber out who told me I was supposed to open a water valve somewhere in the hot press when bleeding the radiator. I had left it closed and let too much water out of the system. He opened the valve and bled the system which fixed the issue.


  • Registered Users Posts: 112 ✭✭newaccount2017


    I just checked the hot press where all the heating stuff is and there's a dial with a black hand pointing to zero and a red hand pointing to 2.5. I wonder if that means anything.


  • Closed Accounts Posts: 1,662 ✭✭✭Duke of Url


    I just checked the hot press where all the heating stuff is and there's a dial with a black hand pointing to zero and a red hand pointing to 2.5. I wonder if that means anything.

    I have no idea. I just called a plumber as I knew I funked up. He told me exactly what I had done over the phone and he called out and fixed it.


  • Registered Users, Registered Users 2 Posts: 9,474 ✭✭✭TheChizler


    Black dial indicates there's no water pressure in the heating system. You need to open that filling loop valve until there's pressure on the system, normally at least 1 bar for most boilers. I'm surprised so much pressure was lost by bleeding the radiator, do you have an expansion vessel?

    https://www.google.com/search?q=expansion+vessel


  • Registered Users, Registered Users 2 Posts: 9,341 ✭✭✭CoBo55


    You’ve let the pressure out of the system which is indicated by the black hand, you need to find the water filler and let water into the system until it’s showing about 1 bar when it’s cold. The red hand is just a marker you can move by turning the outside surround of the gauge.


  • Advertisement
  • Registered Users Posts: 112 ✭✭newaccount2017


    Yeah, I have one of those expansion vessels.


  • Registered Users, Registered Users 2 Posts: 3,960 ✭✭✭jimf


    its also possible you have tripped the high limit stat on your boiler

    as advised above already you need to bring the system up to I bar pressure on the black hand then bleed your rads until you have water from them

    check pressure again and adjust back up to .75 to 1 bar pressure

    https://heatingpartswarehouse.co.uk/product/imit-tlsc-dual-thermostat/?gclid=EAIaIQobChMI8ena65_z6gIVGODtCh08fQm4EAQYASABEgK_rvD_BwE

    this is a pic of your boiler stat unscrew the little black cap and press button underneath to reset hl stat


  • Closed Accounts Posts: 1,662 ✭✭✭Duke of Url


    TheChizler wrote: »
    Black dial indicates there's no water pressure in the heating system. You need to open that filling loop valve until there's pressure on the system, normally at least 1 bar for most boilers. I'm surprised so much pressure was lost by bleeding the radiator, do you have an expansion vessel?

    https://www.google.com/search?q=expansion+vessel
    CoBo55 wrote: »
    You’ve let the pressure out of the system which is indicated by the black hand, you need to find the water filler and let water into the system until it’s showing about 1 bar when it’s cold. The red hand is just a marker you can move by turning the outside surround of the gauge.

    I agree with these 2 lol


  • Registered Users, Registered Users 2 Posts: 3,960 ✭✭✭jimf


    TheChizler wrote: »
    Black dial indicates there's no water pressure in the heating system. You need to open that filling loop valve until there's pressure on the system, normally at least 1 bar for most boilers. I'm surprised so much pressure was lost by bleeding the radiator, do you have an expansion vessel?

    https://www.google.com/search?q=expansion+vessel


    possibly low anyway before he bled it

    you would think 1 rad been bled wouldn't cause the issue


  • Registered Users Posts: 112 ✭✭newaccount2017


    jimf wrote: »
    its also possible you have tripped the high limit stat on your boiler

    as advised above already you need to bring the system up to I bar pressure on the black hand then bleed your rads until you have water from them

    check pressure again and adjust back up to .75 to 1 bar pressure

    https://heatingpartswarehouse.co.uk/product/imit-tlsc-dual-thermostat/?gclid=EAIaIQobChMI8ena65_z6gIVGODtCh08fQm4EAQYASABEgK_rvD_BwE

    this is a pic of your boiler stat unscrew the little black cap and press button underneath to reset hl stat

    I just checked and I don't seem to have that boiler stat. I'm going to take a few photos of what I have and upload them. Thanks everyone for the help so far.


  • Advertisement
  • Registered Users Posts: 112 ✭✭newaccount2017


    These are the pics I took:
    https://imgur.com/a/5GWrDr4


  • Registered Users, Registered Users 2 Posts: 3,960 ✭✭✭jimf


    I just checked and I don't seem to have that boiler stat. I'm going to take a few photos of what I have and upload them. Thanks everyone for the help so far.

    that stat will be out at your boiler


  • Registered Users Posts: 112 ✭✭newaccount2017


    jimf wrote: »
    that stat will be out at your boiler

    You were right. I found it outside when I opened up the boiler. I unscrewed the black cap and pressed the button underneath but nothing happened.


  • Registered Users Posts: 112 ✭✭newaccount2017


    The heat is working now although the bar is still at 0. I don't know what happened but thank you everyone, it'll keep me going til I call the plumber. I don't trust it anymore though :(


  • Registered Users, Registered Users 2 Posts: 2,996 ✭✭✭Nigzcurran


    The heat is working now although the bar is still at 0. I don't know what happened but thank you everyone, it'll keep me going til I call the plumber. I don't trust it anymore though :(

    Have you a hot press or similar area with all your pipes?


  • Registered Users, Registered Users 2 Posts: 3,960 ✭✭✭jimf


    The heat is working now although the bar is still at 0. I don't know what happened but thank you everyone, it'll keep me going til I call the plumber. I don't trust it anymore though :(

    it sounds like your boiler etc is ok

    your system is low and has no water to circulate around to the rads


    your boiler is getting up to temp and cutting out until you sort the pressure you wont be able to run the heat


  • Registered Users Posts: 112 ✭✭newaccount2017


    Nigzcurran wrote: »
    Have you a hot press or similar area with all your pipes?

    Yeah, I have a hot press with all the pipes, they're in this picture:
    https://imgur.com/a/5GWrDr4


  • Registered Users Posts: 112 ✭✭newaccount2017


    jimf wrote: »
    it sounds like your boiler etc is ok

    your system is low and has no water to circulate around to the rads


    your boiler is getting up to temp and cutting out until you sort the pressure you wont be able to run the heat

    What's weird is that my hot water in the kitchen sink tap just dribbles out at times. I've been meaning to call a plumber and get all of these issues fixed but now I'm thinking that there's a connection between that and my central heating. The bathroom taps are fine, it's just the kitchen sink hot water tap.


  • Registered Users, Registered Users 2 Posts: 73,478 ✭✭✭✭colm_mcm


    B67-BAC0-B-3793-4120-8465-66210-D426-EFF.jpg

    See the black knob to the left, pointing downwards?


  • Registered Users Posts: 112 ✭✭newaccount2017


    Yeah, should I turn it? When the heating is on?


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 73,478 ✭✭✭✭colm_mcm


    I’m not a doctor, but I’d turn it while the heating is off.


  • Registered Users Posts: 112 ✭✭newaccount2017


    I turned it earlier when the heating was off but it didn't seem to do anything to the black pressure gauge, that was still at zero. So I just readjusted the black knob back to the way it was first then.


  • Registered Users, Registered Users 2 Posts: 73,478 ✭✭✭✭colm_mcm


    You may need to wait for it to go above zero. You should also be able to hear water moving through.


  • Registered Users Posts: 112 ✭✭newaccount2017


    Ok, I'll try that in the morning. Thanks for your help, much appreciated. I'm afraid to try it now because the heat is working and I want to heat the house as much as possible now in case it konks again.


  • Registered Users, Registered Users 2 Posts: 73,478 ✭✭✭✭colm_mcm


    It’s a bit silly running it when you know it’s got low pressure.


  • Registered Users, Registered Users 2 Posts: 3,960 ✭✭✭jimf


    when you pressed the little button at the boiler earlier had you the heating turned on inside at timer


  • Registered Users Posts: 112 ✭✭newaccount2017


    colm_mcm wrote: »
    B67-BAC0-B-3793-4120-8465-66210-D426-EFF.jpg

    See the black knob to the left, pointing downwards?

    I had the black knob loosened today for a few hours but it made no difference to the pressure gauge.


  • Registered Users, Registered Users 2 Posts: 9,474 ✭✭✭TheChizler


    Should only be for a few seconds, never leave it open unattended. Did you open it all the way? You should be able to hear water flowing and the pressure should shoot up


  • Registered Users, Registered Users 2 Posts: 3,960 ✭✭✭jimf


    those valves can go faulty

    if you overfill the system your safety valve will pop

    time for a plumber me thinks


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 3,563 ✭✭✭John.G


    The lock nut can be slackened and the adjusting spindle screwed down clockwise very very slowly with the black knob open, if no rise in pressure then either no or low mains pressure available, or maybe supply is from the cold water storage tank which should still give ~ 0.5 bar, ensure black knob closed afterwards before leaving as advised above.


  • Registered Users Posts: 112 ✭✭newaccount2017


    Thanks everyone for all the help. I think I'll call a plumber and hopefully it'll be sorted then. It's due the yearly service. I'm glad it went during summer and not winter!


  • Registered Users, Registered Users 2 Posts: 9,341 ✭✭✭CoBo55


    You're so close..don't chicken out now!! Open the locknut and turn the centre screw slowly clockwise until the water starts flowing, have your hand on the black knob ready to turn off the water as soon as it reaches 1 bar as it will rise quickly. I'd say the valve is stuck like them all, they're a dreadful bloody invention they always give trouble. Remember to leave the black knob closed when your finished otherwise water will keep entering the system driving the pressure sky high and as was said earlier lifting the 3 bar safety valve or bursting the expansion vessel.


Advertisement