Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Buried cables regulations

  • 01-08-2020 8:16pm
    #1
    Registered Users, Registered Users 2 Posts: 17,679 ✭✭✭✭


    Whats the regs on buried electrical cable?

    I've chased about 5 cm deep - and knackered so don't wanna have to go deeper if I don't have to

    Found some British regs but are they the same as Ireland

    Basically is it deep enough or will I need a conduit and should it be plastic or metal?


Comments

  • Registered Users, Registered Users 2 Posts: 7,463 ✭✭✭Leftyflip


    Chased into a wall? Or dug into the ground?


  • Closed Accounts Posts: 119 ✭✭Frankx


    There's a few

    Generally cables go horizontally or vertically to a switch etc

    And they should be at least 50mm back from the other side of a wall

    There's a few more but mostly you will stick to the standard runs above


  • Closed Accounts Posts: 119 ✭✭Frankx


    If youre dropping to a socket etc you only need plastic

    You actually don't want to go in to deep if it's a thin wall as you might be out too far towards the other side


  • Registered Users, Registered Users 2 Posts: 34,111 ✭✭✭✭listermint


    fritzelly wrote: »
    Whats the regs on buried electrical cable?

    I've chased about 5 cm deep - and knackered so don't wanna have to go deeper if I don't have to

    Found some British regs but are they the same as Ireland

    Basically is it deep enough or will I need a conduit and should it be plastic or metal?

    It should be in conduit and min 750mm.


    What are you installing?


  • Closed Accounts Posts: 119 ✭✭Frankx


    450mm for SWA buried in a domestic garden or driveway


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 31,142 ✭✭✭✭Lumen


    listermint wrote: »
    It should be in conduit and min 750mm.
    I assume since he got knackered by going 5cm deep it's not in his garden. :D


  • Registered Users, Registered Users 2 Posts: 31,142 ✭✭✭✭Lumen


    Frankx wrote: »
    450mm for SWA buried in a domestic garden or driveway

    I believe ET101 states, from bottom to top:

    - 100mm sifted soil or sand
    - SWA
    - 150mm sifted soil or sand
    and then 450mm comprising:
    - Cable tile
    - Warning tape
    - Backfill

    So effectively you have to start by digging a trench of depth 700mm+cable diameter.

    But this isn't what the OP was about. :D


  • Closed Accounts Posts: 119 ✭✭Frankx


    Lumen wrote: »
    I believe ET101 states, from bottom to top:

    - 100mm sifted soil or sand
    - SWA
    - 150mm sifted soil or sand
    and then 450mm comprising:
    - Cable tile
    - Warning tape
    - Backfill

    So effectively you have to start by digging a trench of depth 700mm+cable diameter.

    But this isn't what the OP was about. :D

    I'd say he's on about a wall chase


  • Registered Users, Registered Users 2 Posts: 17,679 ✭✭✭✭fritzelly


    Sorry, its in a wall for a light switch


  • Registered Users, Registered Users 2 Posts: 34,111 ✭✭✭✭listermint


    If your 5cm deep your half though the block. Too deep :)


  • Advertisement
  • Registered Users, Registered Users 2 Posts: 17,679 ✭✭✭✭fritzelly


    Block is about 120mm, I'm probably more 40 mm than 50


  • Registered Users, Registered Users 2 Posts: 3,892 ✭✭✭chooseusername


    fritzelly wrote: »
    Block is about 120mm, I'm probably more 40 mm than 50
    I think it's something like 1/3 of block thickness for vertical chase,
    so about 35mm.
    and half that for horizontal chase.


  • Registered Users, Registered Users 2 Posts: 12,595 ✭✭✭✭Calahonda52


    522.6.4 :4th edition 2008 the distance measured horizontally between the wring and the reverse side of the wall is not less than 50 mm

    +all the stuff about horz and vertical distances

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 2,851 ✭✭✭tech


    500mm would be best


    cover with some gravel and then some yellow warning tape incase someone comes digging in years to come


  • Registered Users, Registered Users 2 Posts: 31,142 ✭✭✭✭Lumen


    This thread is like a reading comprehension test.


  • Registered Users, Registered Users 2 Posts: 17,679 ✭✭✭✭fritzelly


    All done and I didn't kill myself
    Looking pretty good with new wallpaper and new switches