  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    John.G wrote: »
    If I connect a L & N to RCD/RCBO but connect nothing on the load side will they trip if I press the test button?

    It will, if you connect phase and N to either side.


  • Registered Users Posts: 24,644 ✭✭✭✭punisher5112


    GreeBo wrote: »
    LOL, you were both wrong, while there was a loose neutral, but the actual problem was a dodgy RCBO!

    Rcbo was fine.... Was loose neutral, hence why I said this happen a lot


  • Registered Users Posts: 3,514 ✭✭✭John.G


    RCBO was fine??, Greenbo said the problem was a dodgy RCBO??


  • Registered Users Posts: 24,644 ✭✭✭✭punisher5112


    John.G wrote: »
    RCBO was fine??, Greenbo said the problem was a dodgy RCBO??

    Yeah they tighten loose neutral and it worked


  • Registered Users Posts: 3,514 ✭✭✭John.G


    He replaced the RCBO with a new one, see post #27.


  • Advertisement
  • Registered Users Posts: 24,644 ✭✭✭✭punisher5112


    John.G wrote: »
    He replaced the RCBO with a new one, see post #27.

    Sorry didn't see that, possible it damaged it then.


  • Registered Users Posts: 27,176 ✭✭✭✭GreeBo


    #itsstillworking! :)


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    We could make up an example, independent of the thread here, but similar circumstances, as an RCD with a loose connection to it also. Shower is not working.

    RCD is replaced, now the shower works perfectly. Was the RCD faulty in this made up example?


  • Registered Users Posts: 3,514 ✭✭✭John.G


    I would examine failed RCD/RCBO for any signs of heat damage, if none connect via a 13A plug and cable and close the switch, press test button, if it operates, connect say electric kettle (full of water) to load end which will give some loading of 8/10A then repeat test with loaded RCD. While the above doesn't prove that the RCD will operate at ~ 40A, it will give some indication, but would not re use it if RCBO because of doubt that it will trip in o/load/short circuit conditions.


  • Registered Users Posts: 27,176 ✭✭✭✭GreeBo


    Bruthal wrote: »
    We could make up an example, independent of the thread here, but similar circumstances, as an RCD with a loose connection to it also. Shower is not working.

    RCD is replaced, now the shower works perfectly. Was the RCD faulty in this made up example?

    But this ignores that I first fixed the loose connection, but the issue still occurred...

    In your example there is no way to know as not enough testing was done.


  • Advertisement
  • Registered Users Posts: 3,514 ✭✭✭John.G


    If you still have the RCD can you carry out a test like I suggested avove or just connect up a supply and see if it trips and has continuity through both neutral and live.


  • Closed Accounts Posts: 13,422 ✭✭✭✭Bruthal


    GreeBo wrote: »
    But this ignores that I first fixed the loose connection, but the issue still occurred...

    In your example there is no way to know as not enough testing was done.
    It was a point in general.


  • Registered Users Posts: 27,176 ✭✭✭✭GreeBo


    John.G wrote: »
    If you still have the RCD can you carry out a test like I suggested avove or just connect up a supply and see if it trips and has continuity through both neutral and live.

    It was dumped I'm afraid.