    Does the regs 4% volt drop rule apply to the size of the MCB on the circuit or the appliances on the circuit?

    For example when I calculate the below formula and get the resistance of the cable do I divide it by the size of the mcb (20amps) or do divide it by the overall load the circuit is pulling?



    The following is an example of a basic voltage drop calculation:
    Refer to Figure 36. Assume a load of 20 Amps is to be supplied at a distance of 25 metres using 2.5 mm2 conductors.




    The resistance of 50 metres ( phase and neutral in series ) of 2.5 mm2 must first be established.

    Resistance of conductor

    l
    R =
    a
     for copper is 17.2 mm ( 17.2 x 10-6mm )
    l is 50 metres ( 50 x 103 mm )
    a is 2.5 mm2 ( 2.5 mm2 )

    17.2 x 10-6 x 50 x 103
    R =
    2.5

    17.2 x 10-3 x 50
    R =
    2.5

    R = 17.2 x 10-3 x 20

    R = 344 x 10-3

    R = 0.344 Ohms


    The voltage drop across the cable can now be found as follows:

    Voltage Drop across Cable VD = IR

    VD = 20 x 0.344
    VD = 6.88 Volts
    This figure is less than the maximum of 9.2 Volts and so the cable is suitable for the load


Comments

  • Registered Users Posts: 2,567 ✭✭✭Risteard81


    Use the design current.

    However for a circuit supplying socket-outlets this will be the rating of the protective device.


  • Registered Users Posts: 9 Ninja1000


    Risteard81 wrote: »
    Use the design current.

    However for a circuit supplying socket-outlets this will be the rating of the protective device.

    Okay so if its a socket circuit does that mean you use 20amps in the formula? because socket circuits are protected by a 20amp MCB