Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

What's the difference here?

Comments

  • Registered Users, Registered Users 2 Posts: 8,565 ✭✭✭K.Flyer


    There is no difference, both radiators are the same.
    If you look at the specifications for the Stelrad radiator on Stelrad's website you will see that they state the btu/hr output for that radiator as 8273 btu at Delta T.50. When you look at the specification info on the best heating site for the radiator at Delta T.50 its the same, but they also quote the higher btu output at Delta T.60.


  • Registered Users Posts: 367 ✭✭teflon


    K.Flyer wrote: »
    There is no difference, both radiators are the same.
    If you look at the specifications for the Stelrad radiator on Stelrad's website you will see that they state the btu/hr output for that radiator as 8273 btu at Delta T.50. When you look at the specification info on the best heating site for the radiator at Delta T.50 its the same, but they also quote the higher btu output at Delta T.60.

    Thanks for that. Is it possible so to achieve the higher btu?


  • Registered Users, Registered Users 2 Posts: 3,563 ✭✭✭John.G


    It is, just about, the specified deltaT is the mean radiator temperature minus the required room temp (generally accepted as 20C).
    So the normal DeltaT.50 would require flow/return temps of 75/65C, mean of 70C, minus 20C = 50C.
    DeltaT.60 would require flow/return temps of 85/75C, mean of 80C, minus 20C = 60C.