Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Garden lights - how many on a "string"?

Options
  • 12-02-2021 6:52pm
    #1
    Registered Users Posts: 28,404 ✭✭✭✭


    Got these Garden Lights that are a mix of AC 110-240v 9 watt and 85-265v 12 watt


    How many of a mix of these can I put in a string i.e. connected successively, safely, that I'd be plugging into an outdoor socket fed from the board in the house, if it matters the plug would have a 13 amp fuse in it?


    Thanks for help in advance


Comments

  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,596 Mod ✭✭✭✭2011


    vicwatson wrote: »
    Got these Garden Lights that are a mix of AC 110-240v 9 watt and 85-265v 12 watt


    How many of a mix of these can I put in a string i.e. connected successively, safely, that I'd be plugging into an outdoor socket fed from the board in the house, if it matters the plug would have a 13 amp fuse in it?


    Thanks for help in advance

    Quite a few, 50 would only be 600W. How may do you want to connect?

    A plug isn't a great permanent solution.


  • Registered Users Posts: 28,404 ✭✭✭✭vicwatson


    Thanks for reply, about 25

    What’s the issue with a plug into an outdoor socket connected to mains rcd?

    Appreciate the help


  • Registered Users Posts: 3,689 ✭✭✭...Ghost...


    vicwatson wrote: »
    Thanks for reply, about 25

    What’s the issue with a plug into an outdoor socket connected to mains rcd?

    Appreciate the help


    Outdoor sockets are really only for very temporary connections, like plugging in the mower, or power washer etc.


    You should have a permanent connection from the board for the garden lights with an indoor switch ideally.

    Stay Free



  • Registered Users Posts: 1,583 ✭✭✭alan4cult


    vicwatson wrote: »
    Thanks for reply, about 25

    What’s the issue with a plug into an outdoor socket connected to mains rcd?

    Appreciate the help
    Because if the outdoor socket trips out the RCD you lose all sockets on that RCD.


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    alan4cult wrote: »
    Because if the outdoor socket trips out the RCD you lose all sockets on that RCD.

    A lot depends if they're 2-wire or 3-wire , presumably 2 ? which is less troublesome for RCD trips

    If be taking a close look at the fittings for safety issues before buying a quantity of they're being bought from the grey market

    If it as my own place if be considering 10mA protection but you can't cascade that with 30mA ,.needs to be separate too.


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,596 Mod ✭✭✭✭2011


    Gestureapo wrote: »
    A lot depends if they're 2-wire or 3-wire , presumably 2 ? which is less troublesome for RCD trips

    What do you mean?
    If it as my own place if be considering 10mA protection but you can't cascade that with 30mA ,.needs to be separate too.

    You could connect two RCD's in series (cascade) but I'm struggling to see why you would bother.


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    2-wire no earth, RCD trips lot less likely


    You wouldn't cascade them, no.You wouldn't fit 10mA either if you were contracting


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,596 Mod ✭✭✭✭2011


    Gestureapo wrote: »
    2-wire no earth, RCD trips lot less likely

    Not really, no.

    Just because a device / appliance / light fitting is double insulated does not mean that an RCD is less likely to trip. Remember that at any point along the circuit there could be a phase to earth fault or a neutral to earth fault. Either of these scenarios would cause an RCD to trip. In addition the ingress of moisture to a double insulated light fitting could cause an RCD to operate.

    An RCD is designed to operate if there is a small fault current flowing to earth, you can have this without having an earth wire.


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    2011 wrote: »
    Not really, no.

    Just because a device / appliance / light fitting is double insulated does not mean that an RCD is less likely to trip. Remember that at any point along the circuit there could be a phase to earth fault or a neutral to earth fault. Either of these scenarios would cause an RCD to trip. In addition the ingress of moisture to a double insulated light fitting could cause an RCD to operate.

    An RCD is designed to operate if there is a small fault current flowing to earth, you can have this without having an earth wire.

    Disagree that double insulated fitting is not less likely to trip RCD

    As you say there is still the potential for tripping at poorly made joints


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,596 Mod ✭✭✭✭2011


    Gestureapo wrote: »
    Disagree that double insulated fitting is not less likely to trip RCD

    Do you agree that an RCD could trip due to an issue anywhere along the cable feeding a device (even if it is a 2 core cable)?

    Also do you agree that ingress of moisture to double insulted lights can cause RCD's to trip?

    Because both of the above are factors that need to be considered for garden lights far more than for most other lights.


  • Advertisement
  • Closed Accounts Posts: 61 ✭✭Gestureapo


    2011 wrote: »
    Do you agree that an RCD could trip due to an issue anywhere along the cable feeding a device (even if it is a 2 core cable)?

    Also do you agree that ingress of moisture to double insulted lights can cause RCD's to trip?

    Because both of the above are factors that need to be considered for garden lights far more than for most other lights.


    I could answer your points and then i'd counter with mine and so on..

    Maybe some other input would help decide


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,596 Mod ✭✭✭✭2011


    Gestureapo wrote: »
    I could answer your points and then i'd counter with mine and so on..

    :D:)


  • Registered Users Posts: 1,583 ✭✭✭alan4cult


    Just a few points of my own on the discussion.

    I don't think an RCD tripping less is a useful feature of an RCD. At the the extreme of it never tripping is equivalent to not having one at all!

    With regards to 2 wire vs 3 wire, yes this does remove the neutral to earth wire fault but it doesn't remove a live/neutral to earth fault when the human is the earth.

    Agreed if something is perfectly insulated then why bother having an earth, but I can snip a wire accidentally (think hedge trimmer) and I'd much rather have the earth wire present despite the device being doubly insulated between plug and handle.


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    The first point, the rcd doesn't need to trip in use once the test button is pressed monthly and it trips.

    The 2nd point is hard to understand

    The 3rd point makes no sense at all to me


  • Registered Users Posts: 6,233 ✭✭✭Ubbquittious


    In theory you could connect about 200 anyway. The inrush current might be high, but dont think its too bad with leds. Just aa little capacitor to fill in each bulb


  • Registered Users Posts: 28,404 ✭✭✭✭vicwatson


    Gestureapo wrote: »
    A lot depends if they're 2-wire or 3-wire , presumably 2 ? which is less troublesome for RCD trips


    They are 2 wire lights


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    vicwatson wrote: »
    They are 2 wire lights

    Well I would inspect before buying on bulk

    The main considerations are the ;

    Quality of the fittings ,

    Type and safety of wiring from cable joints to lights,

    Control of lights

    And jointing


  • Registered Users Posts: 28,404 ✭✭✭✭vicwatson


    Gestureapo wrote: »
    Well I would inspect before buying on bulk

    The main considerations are the ;

    Quality of the fittings ,

    Type and safety of wiring from cable joints to lights,

    Control of lights

    And jointing

    Am happy with all that


  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,596 Mod ✭✭✭✭2011


    alan4cult wrote: »
    With regards to 2 wire vs 3 wire, yes this does remove the neutral to earth wire fault but it doesn't remove a live/neutral to earth fault when the human is the earth.

    Exactly and a human could make contact with the phase or neutral anywhere along the cabling.
    Agreed if something is perfectly insulated then why bother having an earth, but I can snip a wire accidentally (think hedge trimmer) and I'd much rather have the earth wire present despite the device being doubly insulated between plug and handle.

    .....and in the case of garden lighting the one of the most suitable cable types would be SWA with the armour earthed. I would think that the greatest risk is from the cabling as it may be partially or completely buried so a spade or similar implement could be put through it.

    It is also important to have a CPC within the cable so that if double insulated lights were changed to something requiring an earth at some point in the future an earth it is available.


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    2011 wrote: »
    Exactly and a human could make contact with the phase or neutral anywhere along the cabling.



    .....and in the case of garden lighting the one of the most suitable cable types would be SWA with the armour earthed. I would think that the greatest risk is from the cabling as it may be partially or completely buried so a spade or similar implement could be put through it.

    It is also important to have a CPC within the cable so that if double insulated lights were changed to something requiring an earth at some point in the future an earth it is available.

    CPC is a regulation

    Didn't think we were dicussing shock risk here?


    SWA is completely safe having cut through 3P SWA in the rain with a hacksaw in my hand and other times in my careless workout days I can attest


  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,596 Mod ✭✭✭✭2011


    Gestureapo wrote: »
    CPC is a regulation

    It sure is.
    Didn't think we were dicussing shock risk here?

    When installing garden lights it is a very important consideration, as is RCD protection.
    SWA is completely safe having cut through 3P SWA in the rain with a hacksaw in my hand and other times in my careless workout days I can attest

    It is great cable alright as it provides a high degree of mechanical protection which also provides great screening.


  • Closed Accounts Posts: 61 ✭✭Gestureapo


    2011 wrote: »
    It sure is.



    When installing garden lights it is a very important consideration, as is RCD protection.



    It is great cable alright as it provides a high degree of mechanical protection which also provides great screening.

    Shock risk is important as I mentioned in the considerations

    I'm relation to RCD trips no I hadn't included shocks as this is a lesser occurence percentage wise( in fact very low)


Advertisement