Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

New circulation pump.

  • 23-02-2021 9:25pm
    #1
    Registered Users Posts: 406 ✭✭


    Hi
    We have a duel system (oil, solid fuel) heating the house, started the fire with back boiler on Saturday evening and noticed after an hr that the rads were not heating up, the water in the tank was very warm, had a look in the attic, it was full of steam.

    I changed out the circulation pump as per advice from a plumber, the other was 12 yrs old and I had changed it back then with no problems, done the same today, turned everything back on, rads heated up for about an HR then went cold again, I bled the pump again and noticed there was no water coming out, went back up the attic and it was full of steam again...... anyone have an idea what's wrong before I pull the plug and get a proper plumber in..

    The new pump is a dab evosta 2


Comments

  • Registered Users, Registered Users 2 Posts: 3,960 ✭✭✭jimf


    is it working ok with the oil

    if yes having ruled out the pump are you sure the stat operating the pump is working

    or you possibly have a non return valve issue

    just to add im not a plumber just little bits i have learned over the years around here


  • Registered Users Posts: 406 ✭✭denlaw


    jimf wrote: »
    is it working ok with the oil

    if yes having ruled out the pump are you sure the stat operating the pump is working

    or you possibly have a non return valve issue

    just to add im not a plumber just little bits i have learned over the years around here
    Working fine with the oil, stat is operating, think I could have a non return valve problem , I'll have another look at in the morning.
    Thanks..


  • Registered Users, Registered Users 2 Posts: 3,563 ✭✭✭John.G


    Even though probably not the problem, the DAB2 is a very powerful pump (almost 7M) and the traditional "fixed speed" curve 2 is 5.4m which can cause venting, speed 3 is higher again at 6.8M, would suggest changing to (constant pressure) CP mode 2 (3.8M) and see how you get on. (CP3 is 4.8M)


  • Registered Users Posts: 406 ✭✭denlaw


    John.G wrote: »
    Even though probably not the problem, the DAB2 is a very powerful pump (almost 7M) and the traditional "fixed speed" curve 2 is 5.4m which can cause venting, speed 3 is higher again at 6.8M, would suggest changing to (constant pressure) CP mode 2 (3.8M) and see how you get on. (CP3 is 4.8M)
    would you recommend that setting for 13 rads in the house?


  • Registered Users, Registered Users 2 Posts: 3,563 ✭✭✭John.G


    Difficult to answer that, it depends on the installation, pipe manifold sizing etc but on CP2 the DAB will maintain a constant 3.8M head up to 25 LPM, CP3 will give up to 17LPM at 4.8M head and then fall gradually to 3.8M between 17LPM and 25LPM.
    I have 10 rads and a 3M head gives me all hot rads. What mode/setting is/was the DAB on just now?.

    What was the old pump make/model/setting? or/and the OF boiler make/model/setting and that will tell a lot.


  • Advertisement
  • Registered Users Posts: 406 ✭✭denlaw


    John.G wrote: »
    Difficult to answer that, it depends on the installation, pipe manifold sizing etc but on CP2 the DAB will maintain a constant 3.8M head up to 25 LPM, CP3 will give up to 17LPM at 4.8M head and then fall gradually to 3.8M between 17LPM and 25LPM.
    I have 10 rads and a 3M head gives me all hot rads. What mode/setting is/was the DAB on just now?.

    What was the old pump make/model/setting? or/and the OF boiler make/model/setting and that will tell a lot.
    the old pump was a heat merchant, it was set to the number three setting.

    I set the new one to the highest output, guess I blew the non return valve.


  • Registered Users, Registered Users 2 Posts: 3,563 ✭✭✭John.G


    That old heat merchants was possibly a HM 4-7 which was a relabeled Dab Evosta 4-7 with almost exactly the same head/flow as your new pump on full speed. NRVs can take ~ 6 times the head generated by any circ pump so couldn't really damage it, it's possibly stuck or partially blocked with sludge especially if its of the spring loaded type in which sludge can easily build up in the valve guides.


  • Registered Users, Registered Users 2 Posts: 3,960 ✭✭✭jimf


    if its the old europa spring type valve i would be having a good look at it before you go any further

    change it for the flap type instead


  • Registered Users Posts: 406 ✭✭denlaw


    Update on circulation pump.

    found the problem, when the old pump failed, i went up into the attic to check if i had water in the expansion tank, i had to rip off the insulation that i had over the tank to take a peek, a little piece of tape had fallen in the tank, it had got stuck in the feed hole which was why the pump wasn't getting any water, pulled the tape out and its been working like a dream since, in fact, its the first time in about 10 yrs that all the rads have been working properly.

    Thanks again to all for the input.