Steeltech shed earthing

Options
  • 24-06-2021 3:02pm
    #1
    Registered Users Posts: 2,998 ✭✭✭


    If a steel shed has power going to it with a number of sockets and lights installed inside, do you need to have the shed itself connected to the earth wire? Shed is bolted down to a concrete slab.


Comments

  • Registered Users Posts: 16 throwaway657yf


    xabi wrote: »
    If a steel shed has power going to it with a number of sockets and lights installed inside, do you need to have the shed itself connected to the earth wire? Shed is bolted down to a concrete slab.

    i would assume that the swa coming from the house board earth rod to to shed would be satisfactory


  • Registered Users Posts: 24,644 ✭✭✭✭punisher5112


    Yes the shed would need an earth...


  • Registered Users Posts: 2,998 ✭✭✭xabi


    Hypothetically if a live wire touched the shed would the RCBO in the house that the SWA is connected to trip?


  • Registered Users Posts: 24,644 ✭✭✭✭punisher5112


    It should yes, running the SWA and then fitting its own board in shed would be how I'd do it.


  • Registered Users Posts: 209 ✭✭Bruthal.


    If a sub board is being fitted in the shed, you wont want the supply to it connected to the house RCD.