Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Two Inverters

  • 28-01-2023 2:14pm
    #1
    Registered Users, Registered Users 2 Posts: 436 ✭✭


    Who here has two inverters?

    I have my install taking place in February (16 x 380w panels) and a Solis inverter. This setup is via an Seai approved installed and will avail of the grant.

    Separately I’m going to undertake a DIY install (14 x 405w panels) and a Sofar 6000EP hybrid inverter with batteries arriving from PWOD.

    I plan to install both inverters side by side in my garage.

    Is there anything i need to consider with having multiple inverter setups?

    I may try be a little cheeky and ask the installer of the first system to run the electrical consumer connection for the Sofar when they doing the install of the 16 panel system. If not I’ll source an electrician



«1

Comments

  • Moderators, Home & Garden Moderators Posts: 6,309 Mod ✭✭✭✭graememk


    Should just work without Issue.

    The sofar will need (ideally) a cat6 cable going back to the meter cupboard, or the main consumer unit.

    Are you tying into the power already in the garage or running a new cable for the solis inverter?..

    Maybe get a new (large) supply cable ran to the garage and run everything from that. eg 10mm2 at least.



  • Moderators, Sports Moderators Posts: 19,197 Mod ✭✭✭✭slave1


    Agreed, run a 10sq, I ended up running two SWA runs as two inverters need a large single cable and 6sq not enough

    Bit obvious but ensure the first setup neatly leaves room for the next inverter and switches



  • Registered Users, Registered Users 2 Posts: 2,396 ✭✭✭SD_DRACULA


    As long as you don't put two hybrid inverters (of different brands) on the same supply.

    I mean you can but just connect batteries to only one of them.



  • Registered Users, Registered Users 2 Posts: 436 ✭✭jasgrif11


    I have SWA running from main house consumer unit out to my Garage where I have another fuseboard. Can everything we wired into this?

    I also have Cat6 in my garage and a router.

    However I thought cables had to go back to the main consumer fuseboard? If not then it will be much simpler for the install overall.



  • Moderators, Home & Garden Moderators Posts: 6,309 Mod ✭✭✭✭graememk


    Doesnt have to go back to the main consumer unit, If the SWA to the garage is heavy enough. SWA can be 1.5mm2, or 16mm2+ there is a huge difference. (

    The Cat6 is for CT's It cant be used for Data at the same time, so it needs to be a separate cable



  • Advertisement
  • Registered Users Posts: 52 ✭✭Sligobuck


    Why not....I run a Solax X1 Hybrid 5K Inverter with 16Kw of batteries and a separate Sofar HYD 6000-EP with 56Kw of (Seplos 280Ah Mason 52v x 4) batteries on the same supply!

    I could not get Solax to provide an upgrade path to increasing battery storage so I gave up on them and added the Sofar HYD 6000-EP with 56Kw of batteries recently. There was no point in de-commissioning the Solax and batteries since they are good quality LFP high voltage packs (3 batteries).

    All runs fine with night rate charging (Time of Use) setup to charge both battery banks in separate time slots.

    Solax gets full power 5Kw of charging from 11pm and is done by 2am and remains on Time of Use till 8am. Solax has 6Kw of panels and has feed-in but I tend to feed very little to the grid even during the summer with excess to water heating.

    Sofar gets 500 watts of charging from 11pm till 2.30am and then switches to 5Kw charging until 8am, it generally is done by 5am or later if the heat pump is working hard during freezing days. Sofar has Anti-Reflux (no feed-in) switched on.

    All of the above is in the attic.



  • Moderators, Home & Garden Moderators Posts: 6,309 Mod ✭✭✭✭graememk


    kWh!! kWh!!

    I thought myself and @unkel were OTT with 40kWh 😂

    How do you prevent them from "fighting?"

    Who get priority to discharge first?

    Why does it take longer when the heatpump kicks in?



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    @Sligobuck - you charge your Seplos / Mason 56kWh with 500W from 11PM until 2:30AM then with 5kW until 8AM. That's 1.75kWh + 27.5kWh = 29.25kWh, only using half your capacity? Or am I missing something here?

    That seems a waste, did you buy too much battery capacity or are you planning to get a beefier inverter that can charge your battery quicker?


    You have 6kwp of PV on your other inverter, how much do you have on this one?



  • Registered Users Posts: 52 ✭✭Sligobuck


    Mea Culpa....lazy with the kWh and I am likely to make those mistakes again :-)

    They do not fight, I am no electrical engineer but I guess whichever inverter has a slightly higher voltage gets to deliver the power to the loads.

    There are no priorities setup for discharge on either from 8am.

    The Solax seems the leader here with it delivering most of its battery power during the day from 8am on with the Sofar adding to any loads over 5kW during that time, once the Solax runs out of juice the Sofar seamlessly takes on the load.

    When the weather gets down around freezing the Nibe Air to water heat pump becomes much less efficient and pulls much more power on those days so the Sofar batteries get pulled lower and take longer to get back to full charge.

    Hope that makes sense and I am learning as I go along....Will and Andy have been my main resources for learning.



  • Registered Users Posts: 52 ✭✭Sligobuck


    Future planning with the excess on batteries, ROI was not used in the calculation and decided to go all in now so an electric car and such can be factored in later. I also do not trust the state of the grid for the next few years so if rolling cuts are ever rolled out I will be well covered.

    I will be adding solar panels to the Sofar soon but only about 6 x 400 watt for now, I have other ideas for ground mount but not just yet.



  • Advertisement
  • Moderators, Home & Garden Moderators Posts: 6,309 Mod ✭✭✭✭graememk


    Good to know they get on well.

    You lucked out there, it's not voltage it's whoever detects and reacts first, it could be the solax has a slightly faster response time, and the sofar just never gets the chance to get going.

    Also the CT on the sofar could be trimmed too.(but I wouldn't touch yours as it's already working fine) it could be that the sofar runs on a slight import,

    Have you ever pulled more than the solax limit, I suppose the sofar kicks in then?

    With averaging 30-40kwh a night, your not too much over 2000 night units on the Energia ev tariff.

    Any plans for summer to use the excess battery power?



  • Registered Users Posts: 52 ✭✭Sligobuck


    I should also mention that I have setup for a second Sofar beside the current one so I can split to 2 packs on each.

    I have applied for the upgrade to an enhanced 16kVa so hopefully get that completed soon.



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    @graememk - "With averaging 30-40kwh a night, your not too much over 2000 night units on the Energia ev tariff."

    That's just his batteries charging. There is a lot more use during night rate hours than that 😂

    In my case like charging all the EVs, heating a big cylinder of water, heating the house, running dishwasher / washing machine / dryer plus of course the base load of the house

    I went over 900 over the 2000 night unit limit last bill



  • Moderators, Home & Garden Moderators Posts: 6,309 Mod ✭✭✭✭graememk


    There is a way to wire up the CTs on the sofar to give one priority of the other, need 3 cts in total.



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Isn't that all making things unnecessarily difficult for yourself? I'd say if you add a smart car charger (like a zappi) and / or a smart water heater (like an eddi), you could find yourself in trouble with two battery inverters

    That's the very reason why I want to upgrade my 5.5kW Sunsynk hybrid to a 8.8kW Sunsynk hybrid inverter (single phase). It can charge at 190A, say 9kW. That means it can fill 9 hours * 9kW is over 80kWh of battery during night rate.

    I have 2 other dumb PV inverters, you can have as many of those as you like, they don't interfere with each other.



  • Registered Users Posts: 6,185 ✭✭✭championc


    Dare I ask, what is consuming so much power ???



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    He kinda answered that. Future planning, getting an EV and not trusting the grid going forward so wanting plenty of backup.

    Not dissimilar to @graememk and myself having a big battery. Both of us are planning to replace our fossil fuel heating with a heat pump in the near future, which we plan to run as much as possible on renewables / night rate electricity.

    We would also like to upgrade our electricity supply, if it wasn't so damn expensive. This is mostly future planning as well. Now we have a 9 hour cheap electricity slot, but if / when we eventually and inevitably go to smart meters, that slot could well be reduced to 2-3 hours, so maximum battery loading and night use would then be essential with all the power you have. 20kW o'clock would be better than 15kW o'clock 😁



  • Registered Users Posts: 52 ✭✭Sligobuck


    I regularly pull more than the Solax and the Sofar provides that additional load (green)



  • Registered Users Posts: 52 ✭✭Sligobuck


    Fair point @unkel and if that turns out to be the case then I will look at the larger inverter option. Hopefully the industry will have them readily available by then.

    The difficulty of trying to purchase large off the shelf batteries during 2022 with money in hand is what drove me down the buying cells and building batteries at less than half the cost so I decided to go large with the savings.

    The changeover to heat pump drove me to the bigger batteries, I realised big savings over oil but the energy companies took some of that away recently after doubling the cost of electricity.

    I expect as you say that once a large percentage of people swap over to electric cars then the cheap night rate hours will diminish and bigger battery banks will be handy to have. Having the batteries built and in place now gives a lot of satisfaction as they open up lots of options, mainly for the winter months when there is not much solar available.



  • Moderators, Sports Moderators Posts: 19,197 Mod ✭✭✭✭slave1


    Diminishing of the night rate hrs will be a kick in the balls alright, still a few yrs out though I reckon



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Last year was a pretty decent year for buying cells from AliExpress alright. Given that a lot of stuff had gone up in price, particularly shipping from China. You bought the EVE 280Ah cells from PWOD official store? What made you decide on buying the Mason / Seplos cases instead of what most of us did, just buy the cells (most of use use CALBs) and stick them together in large numbers with 2, 3 or even 4 in parallel, just using a single BMS for the lot? Do you remember what a single case cost you, including shipping (without cells)?



  • Registered Users Posts: 52 ✭✭Sligobuck


    @unkel bought the cells from OYE and they came in from Germany. The cases cost $600 each incl shipping with BMS in each and these came in from Poland. You have to purchase cables as well since they have the quick disconnect design which are very useful, and finally the cheap adaptor for the PC.

    Following Andy from Off Grid Garage and Maddy on the Digital Mermaid I was happy to go down the route of the prismatic cells and the Seplos kit. I bought 2 of the bases as well from Seplos and these are great for wheeling around 2 packs on each at over 200Kgs on each base.



  • Registered Users, Registered Users 2 Posts: 436 ✭✭jasgrif11


    Is it essentially a case with integrated BMS? Will it work with the 200AH 3.2V Lifepo4 Battery? Really nice clean solution, but a bit on the expensive side



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Well that's the one thing I don't understand. You said you have all in your attic, so I presumed nice looking cases and being able to roll them around added near zero value? Obviously Andreas in the off grid garage wants them to look good as he is looking at them every day (and so are his viewers 😂) and he needs to move them around his garage, to connect them up to different systems, use them for tests, etc.

    €600 incl tax and shipment for those huge boxes is not bad considering they come with a built in €200 BMS too. But you would have saved over €2000 if you hadn't gone for them and put your batteries on some big planks across your rafters in your attic, with a single BMS



  • Registered Users, Registered Users 2 Posts: 100 ✭✭Dave_D_Rave


    Apologies guys new to forum; Can somebdy tell me How to subscribe without commenting ?



  • Registered Users Posts: 6,185 ✭✭✭championc


    Hit the STAR button at the top



  • Registered Users, Registered Users 2 Posts: 22,236 ✭✭✭✭ELM327


    Anecdotal experience from myself and others online would point to some inverters "playing better with others" compared to the rest. For all the flaws of my solis I have no issues running multiple small dumb inverters alongside it. In time, hopefully this year, I'll be adding another inverter and 8kWp more. I've been talking with an irish victron installer who is going to help me as he's interested in my off grid project. Probably end up with a main victron based system but keeping the solis.



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Big difference between hybrid / battery inverters and dumb inverters. The former need to know what they are supposed to do, so need at least CT clamps. But if two of them are supposed to do the same thing, they could conflict

    Dumb inverters on the other hand, are simple devices that just convert DC to AC and are connected to your house / the grid. You can have as many as you like, there can be no conflicts.



  • Registered Users, Registered Users 2 Posts: 6,869 ✭✭✭Alkers


    I am considering pulling the trigger on a pre-made seplos mason battery pack and looking for a few clarifications.

    We have an existing array with a non-hybrid 2.5kW inverter, in the attic.

    I want to leave this as is so realise I'll need a stand alone inverter for the battery pack, which needs to be wired back to my distribution board.

    If I go with this setup, how do I arrange for my solar excess to go into the battery pack as opposed to manually charging it when it's sunny and programming it to charge overnight?



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    The new inverter will do all this for you. It has a CT clamp on your mains incomer, so it will know when you are about to export, it will charge the battery instead. It can also be programmed to charge overnight. It would not have to be a stand alone "AC side" battery inverter. It can also be a "DC side" hybrid inverter. You can then attach more PV strings to this new hybrid inverter if you expand your solar system in the future

    Any link to where you plan to buy that pre made battery pack?



  • Registered Users, Registered Users 2 Posts: 6,869 ✭✭✭Alkers


    Many thanks, any recommendations for such an inverter? I have limited roof space to fit any more panels so happy for the two systems to be seperate.

    Would any sparks be happy to wire in this kind of setup?

    It's on a Facebook group which I assume many here are members of. Hands off! :L



  • Registered Users Posts: 8 SE Galway


    Hello folks.

    I've been reading this post with great interest, as I am in a similar situation where I would like to add a second inverter to expand our Solar PV system.

    Our existing solar PV system is south facing producing 5.5 kilowatts in good sunshine and is run using a Solax hybrid inverter which is connected to a 6.3 kilowatt hour battery. This PV system feeds into a sub-fuse board located in the utility room. The sub-board is connected to the main fuse board with a 16 square wire. The hob, oven, dish washer, kitchen and living room lights and sockets are wired from the sub-board - just providing this information incase it's relevant to my questions below.

    I plan to add a second inverter which will either be a Solax inverter or a basic string inverter with two string inputs, the size of this inverter will be approximately 3.5 to 5 kilowatts and the solar panels supplying the second inverter will be West and East facing. The sum of the two systems working together could produce 9 - 10kw on a good day.

    I don't know anything about installing solar systems so I have a number of questions I'd like information on just so I'm aware and have an understanding while speaking with the installer.


    Questions:

    (1) I've been doing some reading online and any of the things I've seen in relation to the installation of a second inverter they talk about wiring the inverters together in parallel or in series. Is it necessary to install or wire the two inverters together in parallel or series or can they be wired independently to the same fuseboard or as it is in my case the sub-fuseboard?


    (2) The existing inverter has a CT clamp on the mains wire coming in so it can determine if we're exporting or importing, is it necessary that the second inverter would also have a CT clamp on the mains for the same reason to see if we're exporting your importing?


    (3) Should the inverters be connected together in some way so they can communicate with each other (this may not be possible I imagine if the inverters are different e.g. Solax for the existing system and Hypontech for the second inverter)?


    (4) When both inverters are generating power will they both send power to the house to satisfy the load while the excess goes to the battery and rest (if any left over) exported to the ESB network or could they inhibit each other in anyway?


    Apologies for the long post and questions but any advice you can offer or answers to my questions would be greatly appreciated.

    Thanks in advance and I look forward to your reply.


    Kind

    regards,

    SE Galway



  • Registered Users Posts: 6,185 ✭✭✭championc


    So long as the second inverter is a standard string non-hybrid, it will seamlessly fit in. It will feed the battery first seamlessly, then export.

    But exporting is now capped at 5kW



  • Registered Users Posts: 6,185 ✭✭✭championc


    As for DIY, super easy. Panels are daisy chained, with the cable from each end plugged into inputs in the inverter. All connectors are MC4's. They all just click together.

    The AC side needs to be connected to it's own breaker on the board (or subboard). No CT's needed



  • Registered Users Posts: 8 SE Galway


    Hello Champion,

    Thanks for your replies and information.

    In relation to the 5kw export, so once my battery is full and the house load is met the most that my system is permitted to export to the grid at a given time is 5kw, is this correct?

    Is it the case that the largest inverter I can install is a 5kw inverter?

    Thanks again

    Regards.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 7,044 ✭✭✭con747




  • Registered Users Posts: 6,185 ✭✭✭championc


    So yes, officially, the sum of all inverters should not exceed 25A



  • Registered Users Posts: 8 SE Galway


    Hello folks,

    Many thanks for all your input it's much appreciated. I've learned a lot through this and earlier posts on this thread.

    Thanks for sending link to regulations.


    Kind regards,

    SE Galway



  • Registered Users, Registered Users 2 Posts: 2,848 ✭✭✭Buffman


    To answer your Qs:

    (1) The new grid-tie inverter should be wired independently back to it's own MCB (or correctly sized RCBO if required).

    (2) The existing mains CT clamp from the current Hybrid inverter will see all import/export so no need for another one.

    (3) The grid-tie will work independently of the hybrid so no need to data connect them.

    (4) They will work as you've described, complementing each other, especially in the '3 string' South + East&West configuration you've described which is pretty much the sweet spot.

    Under the free Mirco-Generation scheme it's now 25A as mentioned already.

    If you pay ESBN a €977.85 fee under the Mini-Generation scheme, they can 'upgrade' your connection with the click of a computer mouse to take up to 72A on single phase or your Max Import Capacity (MIC), whichever is lower.


    FYI, if you move to a 'smart' meter electricity plan, you CAN'T move back to a non-smart plan.

    You don't have to take a 'smart' meter if you don't want one, opt-out is available.

    Buy drinks in 3L or bigger plastic bottles or glass bottles or cartons to avoid the DRS fee.



  • Moderators, Sports Moderators Posts: 19,197 Mod ✭✭✭✭slave1


    But 6kW for pre tightening of rules, OP may have a 6kW NC6 filing?????



  • Advertisement
  • Moderators, Sports Moderators Posts: 19,197 Mod ✭✭✭✭slave1


    Careful on that interpretation of the NC7, that is just an application fee, capital works may be required at your expense and the €977.85 is non-refundable. Check out capacity from your local transformer, in my case it is maxed on supply so I would not receive higher connection, it's quite mirky waters and we are all waiting here to see how it actually pans out



  • Registered Users, Registered Users 2 Posts: 6,948 ✭✭✭SouthWesterly


    I've a non hybrid inverter. Am I correct in my reading that I can only get another non hybrid for more panels in a separate string?

    I assume I could then get a storage inverter to connect to either one and batteries to the storage inverter.



  • Registered Users, Registered Users 2 Posts: 1,341 ✭✭✭Nelbert


    If anything, ideally you'd get a hybrid which would monitor overall export and throttle back if / when necessary and connect the batteries to that.



  • Registered Users, Registered Users 2 Posts: 2,848 ✭✭✭Buffman


    What's your MIC? It'll say on your connection documents in kVA. As you say, I'd definitely do the research first before paying anything. You can check if it's possible to upgrade your MIC by getting a quote with this process.

    You could put in a separate 'new' hybrid with your exisitng grid-tie and they would work independantly of each other. If you're upgrading a grid-tie system to hybrid, most people in that situation would just replace the grid-tie inverter with a hybrid inverter that can do everything you want in one go.

    Just another thing on the 25A limit, it should be possible to program your existing hybrid to only allow a max export of that. So, if you size your new grid-tie inverter at 25A or under, you won't go over 25A total as the hybrid will throttle back if it's done charging the battery and house demand is being met.

    FYI, if you move to a 'smart' meter electricity plan, you CAN'T move back to a non-smart plan.

    You don't have to take a 'smart' meter if you don't want one, opt-out is available.

    Buy drinks in 3L or bigger plastic bottles or glass bottles or cartons to avoid the DRS fee.



  • Registered Users Posts: 1,046 ✭✭✭Mr Q


    @Buffman the 25A limit doesn't allow for software limits. So if you have an inverter or more with a combined total of over 25A they wont allow it on the NC6.



  • Moderators, Sports Moderators Posts: 19,197 Mod ✭✭✭✭slave1


    Only the expensive NC7 allows export limiting



  • Registered Users Posts: 6,185 ✭✭✭championc


    Just to clarify a point slightly - a storage inverter doesn't link to anything. It simply monitors power being exported, and grabs it.

    So it can be anywhere at all within your home setup. It can be out in a shed, garage or barn, nowhere near the PV inverter. It can even be connected to a sub-board, while PV is connected to the main board



  • Registered Users, Registered Users 2 Posts: 6,948 ✭✭✭SouthWesterly


    So having a hybrid and non hybrid inverter isn't an issue.



  • Registered Users, Registered Users 2 Posts: 1,341 ✭✭✭Nelbert


    Well.... As per ESB you shouldn't export more than 25A and that should be the max cumulative output of all inverters......

    The hybrid will see any and all export and could limit some or all of its output (or pump it in to a battery) is my point.



  • Registered Users Posts: 6,185 ✭✭✭championc




  • Advertisement
Advertisement