Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi all! We have been experiencing an issue on site where threads have been missing the latest postings. The platform host Vanilla are working on this issue. A workaround that has been used by some is to navigate back from 1 to 10+ pages to re-sync the thread and this will then show the latest posts. Thanks, Mike.
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Sofar ME3000 alongside solis hybrid inverter

  • 29-11-2023 10:02pm
    #1
    Registered Users Posts: 238 ✭✭


    My system has 2 inverters, solar only on main house and hybrid in the garage with battery. Was looking at ways to increase the charge rate of the battery and the cheapest option seems to be to set up a Sofar ME3000 next to the solar inverter in the main house with a separate battery. Would this create an issue having two separate battery inverters? Like could one system charge the battery of the other and vice versa or is there a way to set the sofar to avoid this?


    Only other option I can think of at the moment is to replace the Solis with a sunsync but that's a bit more expensive.



Comments

  • Moderators, Home & Garden Moderators Posts: 6,309 Mod ✭✭✭✭graememk


    Simplest option is the sunsynk by far.

    Me3000 is doable but need to consider "fighting" but the me3000 does have a CT offset so it should be able to allow it to back off when demand is reached.



  • Registered Users Posts: 238 ✭✭insular1


    Cheers. I'm in no rush anyway. I'll see how the winter goes with just the Solis and see what makes sense next year.



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Have you a smart meter? If so, exporting to the grid is always the most lucrative, provide you have enough in your battery to last you until the next night rate

    You could get a second hybrid inverter, simply not hook up a CT to it and then use it to just charge the battery (on night rate)

    But as @graememk said, it is easier, more future proof and won't cost any more to sell the Solis and buy a 9kW Deye / Sunsynk hybrid. Except you might need your cabling upgraded to be able to take the extra current



  • Registered Users Posts: 238 ✭✭insular1


    Yeah, I'm definitely leaning towards the Deye. Problem is at this rate it's looking like I'll need to upgrade the house supply to really maximise the 3 hour window but that's thousands so really hard to justify. Have the 16kVa supply which maxes out at 70amps but has a 63amp trip. Even without a full electric car yet i am hitting 15kW almost consistently over the 3 hour Pinergy window between the plug in hybrid, battery charging, heat pump and dishwasher/washing machine.

    Think it's 3-4k to upgrade the supply though so very hard to justify unfortunately.



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    If you are hitting 15kW constantly, I will hazard a guess that you are only on a 12kVA connection. Same as myself. And yes I use full whack for the 3 hours myself too, and I am nearly running out every night in the last few nights, probably will run out several times until the days are getting longer again with more PV towards the end of next month.

    I wish I had a 16kVA connection, then I would be laughing all year round. The upgrade from 12kVA to 16kVA costs just over €2k incl. VAT



  • Advertisement
  • Registered Users Posts: 238 ✭✭insular1


    No definitely 16kVa. Had it confirmed with ESB recently. Standard for 16kVa is 80amp main fuse protected by a 63amp breaker. I was quite annoyed at this as assumed I'd be able to run closer to the full 80amps but seems this isn't the case. Really doesn't seem like much of an upgrade over the 12kVa supply.

    I could probably push higher than the 15kW but would be afraid of tripping the main breaker.



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    @insular1 - "Standard for 16kVa is 80amp main fuse protected by a 63amp breaker"

    No, that is standard for a 12kVA connection. I have the same.



  • Moderators, Home & Garden Moderators Posts: 6,309 Mod ✭✭✭✭graememk


    A 16kva is a 100 amp main esb fuse with an 80amp consumer MCB



  • Registered Users, Registered Users 2 Posts: 1,487 ✭✭✭DC999



    So what happens if we go over the 63 amps? '80amp main fuse protected by a 63amp breaker'. Gonna be a lot more people hammering the short night rate in time. And it's something I don't best understand.

    I know it was explained before but can’t recall. Do ESB need to call to reset something meaning you’ve no juice to the house? Or is the risk to damage or fire?

    I get running it close to the limit for hours is pushing a lot of heat through the wiring. Is fire the risk?

    I know people said it seems to allow a little above the breaker limit for a short time. As in unexpected spikes within some tolerance are ok. 



  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Fuses don't pop until they go a bit over their rating. 63A * 230V = 14.5kW (on a 12kVA connection). You can run this continously without the fuse in your CU popping

    And should it pop, then any electrician can replace it for you. The ESB fuse is 80A and won't pop at any time, unless there is something else dodgy going on (like people replacing their 63A consumer unit fuse with a much higher rated one and then drawing more current than they are supposed to). You'd be in trouble if the ESB fuse popped...



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 65,741 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Oh and for anyone interested, I did the break even calculation on the 12kVA to 16kVA upgrade. It would take me 3 years of maxing out the extra current available every single day between 2AM and 5AM, for it to have paid for itself. At my current very generous delta between 5c night rate and 27c FIT, which is not guaranteed. No thanks. I am hoping there will be a rollout of free or much cheaper upgrades over the next few years as the country transitions from using fossil fuels to renewable energy.



  • Registered Users Posts: 238 ✭✭insular1


    We're in a relatively new build and this is also what I thought. However I contacted the ESB about it only a few weeks ago as finished building my DIY battery and wanted to be sure I wasn't going to damage anything drawing higher loads at night. They told me 80amp was standard and put me on to the local office who did our installation who confirmed the same. We can't actually see the main fuse as it's in a fully enclosed box.

    Do you have a source for the info on the 100amp as I feel fairly hard done by having paid for the upgraded service and would love to go back to them on this and make them upgrade my fuse.



  • Moderators, Home & Garden Moderators Posts: 6,309 Mod ✭✭✭✭graememk



    https://www.esbnetworks.ie/docs/default-source/publications/national-code-of-practice76cf7c6b-4890-4c39-87fc-a2d6692ef2d3.pdf

    If you have an 16kVA supply, confirmed by ESBN, Maybe your electrician just put in the standard 63amp consumer unit and thought nothing more about it.

    My parents do have a 16kVA supply, ive seen it on letters from ESBN, But still only a 63 amp MCB/fuse.

    We didnt change it to 80 as they were still on 16mm2 tails. (possibly was a legacy thing.. possibly when the transformer went on fire when esb done nothing about complaints about brownouts...)



  • Registered Users Posts: 238 ✭✭insular1


    Thanks a million. I already have a copy of that second document but I thought the 80A was in reference to the main ESB fuse? Is this actually referencing the MCB?

    I'm gonna get on to them again after lunch with this!



  • Registered Users, Registered Users 2 Posts: 1,487 ✭✭✭DC999


    Ta for explaining. An electric shower alone can be close to 10kW when the incoming water is cold. Add a kettle and tumble dryer on at the same and you're at 15kW.

    Going off topic but in our 80 year old ex council house, they had probably 1 socket per room when built. Mad how far we've moved on but house power supply is now lagging.



  • Moderators, Home & Garden Moderators Posts: 6,309 Mod ✭✭✭✭graememk


    It's the consumer protection, the one that we own,



  • Registered Users Posts: 238 ✭✭insular1


    Waiting for call back now from local office so will let ye know how it goes. Will definitely make sense to jump to a sunsynk hybrid if I can get that 100A main fuse. Thanks for the help all!



  • Registered Users Posts: 238 ✭✭insular1


    Just to update this thread in case anyone else is having the same problem. ESB have agreed to upgrade my 80A fuse to 100A. Initially local office said 80A was all I'd get for a 16kVa supply but after getting in contact with the New Connections department and discussing the documents @graememk linked above the local office capitulated and I'll have a technician out in a couple of days to upgrade the fuse. Thanks for all the help!



  • Moderators, Sports Moderators Posts: 19,197 Mod ✭✭✭✭slave1


    Did they visit you for the 12 to 16kVa upgrade?



  • Registered Users Posts: 163 ✭✭johndoe11


    I'm the same, 16kva with an 80A fuse. Just contacted them.



  • Advertisement
  • Registered Users Posts: 238 ✭✭insular1


    They are coming out on Friday to replace the fuse. Local office never actually admitted that they should have put in the 100A originally but agreed to come replace it so I'm counting that as a win.



  • Moderators, Education Moderators, Home & Garden Moderators Posts: 8,217 Mod ✭✭✭✭Jonathan


    Get them to fit an isolator if there isn't already one so your sparks doesn't have to work live.



  • Registered Users Posts: 163 ✭✭johndoe11


    As an update, ESBN changed out my 80a fuse for a 100a fuse last week.



  • Registered Users Posts: 238 ✭✭insular1


    Great news! Same for me the week before. I'm waiting on electrician to see if my tails need to be upgraded before upgrading MCBs.

    On a separate note my Deye inverter arrived Tuesday from China. I was not expecting it for another month or two so now have to get to work upgrading my battery and inverter cables.