Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Part F Compliance

  • 09-02-2024 9:22pm
    #1
    Registered Users, Registered Users 2 Posts: 1,869 ✭✭✭


    Hi

    Just finishing a deep fit renovation and looking like an A2 Rating.

    Ventilation is via decentralised HR units.

    In checking compliance with Part F 1.2.3.2b calculation is the air supply from just each HR unit totalled and compared with required air supply on basis of 0.3L/M2.

    For example if house size is 200m I need 60L/S for entire house.

    If HRUs can supply a combined 50L/s but there is an 5 wet room extract vans supplying a max 100L/s is that counted?

    Thank you



Comments

  • Registered Users, Registered Users 2 Posts: 39,671 ✭✭✭✭Mellor


    Extract fans don’t supply air. They count towards extract volume.

    You need 60L/s supply total AND 60L/s extract total. supply and extract volumes should be balanced with each other and each be proportional to the volumes of the rooms.



Advertisement