Heat Pumps - post here.

Options
15960626465119

Comments

  • Registered Users Posts: 690 ✭✭✭bamayang


    No the quotes are identical, I’m happy with the second provider. But does €11k sound about right for putting in a HP to replace an oil fed system?

    from some of the comments above, it seems v high.



  • Registered Users Posts: 6,213 ✭✭✭Ubbquittious


    The heatpumps that are designed as drop in replacement for oil are nearly 10k by themselves. It really depends on what exactly they are planning to put in



  • Registered Users Posts: 11,394 ✭✭✭✭the_amazing_raisin


    Has anyone got a heat pump with cooling on normal rads? I'm wondering how well it performs without any forced air circulation (my guess is badly)

    I've a long term plan for doing a house renovation and installing an upgraded heat pump and mhrv. I'd really like a heat pump that can do cooling as well for summer months when the house is way too hot


    It's probably best to integrate with the mhrv system but it does make the job a lot bigger.

    I'm wondering if radiators or those fan assisted radiators would be a better idea

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 12,419 ✭✭✭✭Calahonda52


    chilling UFH coils can lead to condensation/damp in our humid summers, as when you drop the temp, the RH goes up

    http://www.dpcalc.org

    chilling in the MHVR is a better option but make sure you fit a condensate drain pipe and chill it down far enough

    Real aircon drops the air temp right down to dump the moisture and then mix in some unconditioned air.

    If you only chill it down, but not far enough to dump the moisture, the RH goes up and house becomes quite uncomfortable.

    Was discussed here years ago with PHs beside lakes in summer.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users Posts: 3,398 ✭✭✭randombar




  • Advertisement
  • Registered Users Posts: 2,205 ✭✭✭mel123


    Currently doing a full renovation (have not lived in the house yet), not going for the full retrofit grant but will go for the grant for heat pump.

    Im waiting on a few quotes at the moment, but anyone i ring are telling me that im better off doing under floor heating upstairs and downstairs, and no rads, thats A2W works more efficiently with underfloor heating. Is this true or are they trying to sell me the more expensive option?

    Any other advice while I am at this stage?



  • Registered Users Posts: 12,419 ✭✭✭✭Calahonda52


    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users Posts: 12,120 ✭✭✭✭KCross


    A2W works more efficiently with underfloor heating

    That is true

    UFH is also more comfortable.

    But it doesnt mean you cant use rads as long as the rads have been assessed and are adequately sized for the house.


    So, its a financial decision really. If you are stripping the house and pulling up floors anyway you should probably do it but if you are strapped for cash and have adequate radiators already for a HP system, then needs must.



  • Registered Users Posts: 2,205 ✭✭✭mel123


    Thanks Kcross perfect answer



  • Registered Users Posts: 3,398 ✭✭✭randombar


    I'm not sure if I asked this previously but has anyone looked at the low profile stuff?

    If the floors are adequately insulated would it be more straightforward to just put the low profile UFH on the concrete without having to take up floors?



  • Advertisement
  • Registered Users Posts: 1,758 ✭✭✭funnyname


    Looking to upgrade an old gshp in Clare, currently got two quotes which are about the same price, one for a water furnace and one for a heliotherm. Anyone have experience of those and also can anyone recommend some companies for more quotes before I pull the trigger?



  • Registered Users Posts: 118 ✭✭simpsimp


    We did a deep retrofit of a 1930s house and have UFH downstairs and low temperature rads upstairs. It would have been a lot of intervention to install UFH upstairs (I shudder to think of the disruption) and they're working out fine for us.



  • Registered Users Posts: 118 ✭✭simpsimp


    @the_amazing_raisin - actually, one thing I would change in the low temperature rad installation would be to add more zones.

    The guidelines that the installer followed was to put one thermostat in the master bedroom - this faces South, while the two other bedrooms face North.

    So the thermostat can warm up from the sunshine even on a cold day, which leaves the North facing bedrooms a tad under-heated.

    So, if I were doing it again, I'd have a second thermostat for the North facing rooms.



  • Registered Users Posts: 11,394 ✭✭✭✭the_amazing_raisin


    Yeah we've a similar problem, thermostat is in the north facing room while the south facing rooms can end up being overheated

    TRVs are supposed to fix this to a point but I agree that having more zones would be better

    Do you use the heat pump for cooling as well? If so, how's it going with the rads?

    I was looking at the Daikin brochure and it looks like all their fan assisted radiators or convectors have condensation drains as well

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 118 ✭✭simpsimp


    For some weird reason, I had thought that you didn't install TRVs as well as room thermostats, but now that you mention it, that makes sense to get the balance right!

    We don't use the heat pump for cooling, no.



  • Registered Users Posts: 12,419 ✭✭✭✭Calahonda52


    I think they are zone stats, not room stats, so when the stat reaches the set point, the whole zone shuts down.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users Posts: 11,394 ✭✭✭✭the_amazing_raisin


    Our rads have TRVs except for the main bedroom where the upstairs thermostat is, and hallway/bathrooms

    Tbh the TRVs aren't much use in our case since they're all set to full power

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 12,419 ✭✭✭✭Calahonda52


    TRVs, stuck behind curtains etc, in my view are load of... each room requires its own wall mounted stat at the right level away from curtains doors windows wall vents.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Moderators, Home & Garden Moderators Posts: 6,090 Mod ✭✭✭✭graememk


    What is the right level? Height? For a thermostat?

    With the retro fitting of smart TRVs and also low power wireless thermostats, having a stat in every room is possible.. although expensive.

    The tado smart TRVs are decent, and for sure are better than the traditional ones. The room temperature reading is decent.

    Although having them set at full defeats the point of them, maybe back at 3 and see if that's enough



  • Registered Users Posts: 11,394 ✭✭✭✭the_amazing_raisin


    Tried it, ended up with the kids nearly freezing to death in their bedrooms because the heating was so low

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Advertisement
  • Registered Users Posts: 4,483 ✭✭✭BoardsMember


    Two really stupid questions.....doing a renovation of a 20s house, including UFH downstairs, new windows and doors, attic insulation.

    Any concerns or experiences re high cost of running heat pump with above scenario?

    Hot water for showers - presumably this add to the cost of running the heatpump, ie having to get water hot enough for showers. 5 people in house, plan to get a large cylinder.

    Seems like our retrofit is perfect for heatpump, as in, should have well insulated house with decent airtightness apart from some 1 open fireplace. Some people seem anti heat pumps, telling me they cost so much to run. Not sure what to believe.



  • Registered Users Posts: 1,789 ✭✭✭PowerToWait


    I think a lot of Irish people treat them like traditional gas or oil fired systems, “boosting” or otherwise raising the temp if there’s the slightest chill. Turning them on and off, especially with UFH.


    There’s a bit of a learning curve I reckon. Also I think people forget it replaces oil and gas so the electricity bill will reflect that.



  • Registered Users Posts: 11,394 ✭✭✭✭the_amazing_raisin


    A well designed heat pump installation will give you a warm house, plenty of hot water and do it all very efficiently


    A badly designed system will give you a cold house, lightning fast showers and cost a fortune


    There were many horror stories years ago of heat pumps being installed by people who hadn't a clue and botched the whole system


    My advice is to ensure whoever designs the system is a well respected installer with plenty of prior experience. Ideally I'd try to find someone who is certified by the heat pump supplier, so you know they're qualified with that particular system

    Heat pumps are a bit different to regular boilers in that they're best used to supply a steady input of low heat, rather than an hour or two at full blast


    For example I've got my heating and hot water set to always on and I just use thermostats to control the temp. The house is well insulated so the heat pump only kicks on a few times a day

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users Posts: 118 ✭✭simpsimp


    I would second what @the_amazing_raisin says.

    We started a renovation on a 1930s house, then realised that we could make it more sustainable, and turned it into a deep retrofit, essentially.

    In order to qualify for the heat pump grant, we engaged the services of a technical advisor. He was super, and reviewed the existing renovation plan, advising on where to increase or adjust insulation to give us a better result.

    SEAI won't allow an application for the grant unless a technical advisor has reviewed the insulation plan, so that's your insurance that running costs should not be excessive. See: https://www.seai.ie/grants/home-energy-grants/heat-pump-systems/

    The cost for the consultancy was really reasonable, and he basically walked us through the steps to go from a D3 to an A3 BER on the house.

    DM me if you'd like details, the company are Dublin based. To be honest we only chose them because their office was 500m away! But we found their services very good. But there's a list of approved companies at the above link.

    Either way, we found it great to have a 3rd party opinion, someone who could review the plans of the architect, builder, plumber, renewable energy company, and give us expert advise to improve the overall result.



  • Registered Users Posts: 12,419 ✭✭✭✭Calahonda52


    The TA is more than an opinion, its a SEAI grant related requirement

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users Posts: 2,175 ✭✭✭Paul Kiernan


    Can you please PM me the details of your TA? Thanks, Paul



  • Registered Users Posts: 2,205 ✭✭✭mel123


    Anyone offer any words of wisdom/advice/knowledge on monobloc Vs split pump?

    Im out to get quotes and a lot of companies are coming back with quotes for monobloc and ive really only been researching the traditional air to water type, unit outside unit inside etc.



  • Registered Users Posts: 75 ✭✭Punchin A Keyboard


    In my extra ordinary lack of knowledge as i have been pondering a heat pump for a while, the main difference is that refrigerant goes through the wall to the inside unit in a split and only water goes through the wall in a mono. So much harder to plumb a split and more likey to leak at some point. Also most splits are dealing with R32 which i personally am guessing the EU will ban at some point and the newest monos are using R290 propane which apparently is more efficient. Now if one of those leaks you should be ok provided your not smoking a fag beside it



  • Registered Users Posts: 75 ✭✭Punchin A Keyboard


    I would be asking how good is the flow rate calcs. Have at look at some heat geeks vids on YouTube. They have some good stuff including a recent tet a tet with a somewhat skeptic Roger from skillbuilder known for his rants on heat pumps



  • Advertisement
  • Registered Users Posts: 11,394 ✭✭✭✭the_amazing_raisin


    Monoblocs are generally simplest to install as you don't need any specialist to fill the system with refrigerant. The advantage is that you're pumping water outside so you need antifreeze valves or glycol in you heating water (apparently this reduces performance)

    I think the split systems are popular where you're using air to air systems. I guess they also offer some more flexibility regarding the outdoor unit

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost