Garden Office Wiring Safe Electric Certificate

  • 09-10-2022 10:15am
    #1
    Registered Users, Registered Users 2 Posts: 4


    Hi all,

    I've just bought a garden office and it's been built. I've paid an electrician to run armored cable to a fuse box in the shed, and leave a length of armored cable for the garden office company to wire up the garden office. I've also paid my electrician to certify the connection to the house which is done in the fuse box in the shed after the office is built.


    They checked the wiring in the garden office the other day before connecting to the house and have found that the wiring in the garden office is not up to standard and they have now asked for a Safe Electric Certificate for the wiring in the garden office. The garden office company refuse to provide a Safe Electric Certificate.


    What do I do now?


    Can I legally get a refund on the garden office because they refuse to provide a certificate for the wiring?


    Any help with this is appreciated.



Comments

  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Dunno on the cert but the contractor can't sign off on non complaint work anyhow that's a given

    It appears these sheds anyhow are being wired by handymen so no way are they certifiable, not the first time this issue has arisen

    See it in a lot of other areas too , bathroom refurbs and kitchen fitouts , handymen instead of a rec doing the work



  • Registered Users, Registered Users 2 Posts: 17,190 ✭✭✭✭Sleeper12


    An office is a commercial building. I'm not an electrician but I didn't think you had to be a REC to do electrical work in commercial building.

    Happy to be corrected but I thought RECI were domestic only

    Obviously none of above excuses unsafe work



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    The definition would be installation as against building

    So it would be a domestic installation with an office out the back would be my interpretation



  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    My interpretation would also be domestic and should be certified accordingly


    o.p if you contact safe electric you’ll get a definitive answer

    let us know what they say.



  • Registered Users, Registered Users 2 Posts: 7,035 ✭✭✭zg3409


    The wiring needs to be fixed before it can be connected. If garden office company refuse to fix wiring to standard then bring them to small claims court to cover the cost. Get an estimate to get it fixed and they can pay that or get someone to fix it. Try get a list if the issues with photos etc and why it is unsafe.



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Its been apparent as an issue

    Suppliers/manufacturers selling cabins as pre-wired



  • Registered Users, Registered Users 2 Posts: 4 damorton


    Luckily they have agreed to hire a REC to provide a Safe Electric Certificate and do whatever work is necessary.


    Although they did send their electrician to do some work beforehand, not sure what the extent of the work is but they did disconnect the power line and put a plug on the outside of the office?


    Either way I'll be getting a Safe Electric Certificate for the office and for the connection to the house, I hope. Will update when it's finally complete.



  • Registered Users, Registered Users 2 Posts: 230 ✭✭JL spark


    Great to hear ,

    too many of theses company’s out there doing this work , and no paper work,



  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    That’s fair enough so.



  • Registered Users, Registered Users 2 Posts: 2,360 ✭✭✭Antenna


    What issues with the wiring were found to be "not up to standard"



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 4 damorton


    32amp rated armored cable connected directly to 3x 2.5mm cables running to 3 fuses, 16amp, 16amp, 16amp. No main protective device/consumer box/fuse box.


    Blue wire used as live in light switch.


    Earth cables running to led spotlights not connected together.


    Armored cable not earthed in office.


    Spotlights had no fire protection on the back, where installed in "attic" of the office with insulation.


    None of the wiring was labelled and was generally untidy.


    I'm not an electrician, this is straight off the report, so if you don't agree then call an electrician to learn more.



  • Registered Users, Registered Users 2 Posts: 4 damorton


    Still waiting on a REC to call, was expecting a call to arrange time last week.



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Main protective device ? There has to be an isolator in shed to switch off , if not that's a major fail

    Armoured cable not earthed could be irrelevant too if it's earthed at the main board

    Spotlights not fire rated - think that falls under building regulations, don't think that's necessarily a fail anyway

    Overall sounds like a disaster DIY job

    What it needs is these COs getting fined to put a stop to it

    Will mean these sheds cost more though



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    I presume what's happening here is that the sheds are mostly being connected long after the REC is gone

    There's a loophole there leaving supply cables out for sheds and stuff



  • Registered Users, Registered Users 2 Posts: 4,828 ✭✭✭meercat


    If the rec(or his employees)didn’t wire this then they’re not permitted to certify it. Chances are that the company doesn’t have a rec to wire it in the first instance and I’d be surprised if a rec would certify it now.



  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    This is a bit of a gray area. When it is wired it can be considered “packaged equipment”. Therefore some will argue that it is just like any other piece of equipment where the REC simply connects up to it and what happens inside is nothing to do with the REC. I don’t agree with this approach but I seem to spend much of my time dealing with these types of issues at work. We have multiple packages of equipment including completed switch rooms with MV and LV switchgear landing on site that we have to integrate into the site. Some of these originate in other countries which have very different electrical rules. Some are very well built, others are not. None have completion certificates.



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    I'm not a REC now but I thought the idea was that the rec got a cert from the shed contractor

    If cables are being left out and hooked up after ,well that bypasses the procedure anyhow

    You'd think at least they'd have a designer for the electrics, no need for blues at switches and bad labelling and cpcs left loose



  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    How can it be certified by the shed contractor if it is built and wired offsite? Earth fault loop impedance will depend on the supply it is connected to. A most tests can be carried out, but not all.



  • Registered Users, Registered Users 2 Posts: 8,073 ✭✭✭10-10-20


    I'd assume that a serialised compliance sheet should be provided showing the test applied and values obtained. A bit like if I receive a PDU off a supplier, I'll see the test sheet with values for resistance and earth fault tests applied with a summary as well as the tester's name, etc. But I suppose that stands for nothing unless you have a Safe Electric Cert for the whole installation.



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Ya they can't if they don't connect

    I thought this was the procedure in relation to items of equipment like treatment systems that they would be connected by sub contractor supplying the equipment and a cert handed to main contractor



  • Advertisement
  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    I wish it was that simple 🙂

    I just know from my own work there is no standard procedure. I am working on a large biologics phara project in Ireland at the moment but what I describe is what I have experienced first had over many different sectors for well over a decade. Multiple packages all being connected together on site by multiple mech & elec contractors. We agree on the VDR (Vendor Documentation Requirements) during the tender process (inclusive of electrical testing, ATEX certification, CE certificates etc...) however when the kit lands this has often been ignored. As some packages are single source we have to accept whatever is offered 🤕



  • Registered Users, Registered Users 2 Posts: 230 ✭✭JL spark


    Problem is , you don’t have to be a reci to work commercially,

    domestic yes , so anything connected to a domestic installation needs certification



  • Moderators, Home & Garden Moderators, Technology & Internet Moderators, Regional East Moderators Posts: 12,641 Mod ✭✭✭✭2011


    In reality all electrical contractors working on a large industrial installation can't even tender unless they are properly registered. Ultimately everything is much more thoroughly tested and documented. The problem is that we have to sort issues out on site that should have been boxed off before the kit landed.



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Shed contractor agrees supply needed beforehand ,and connects and hands sub-cert to REC

    Ideally i reckon but sure it's all easily bypassed if job is finished and a shed is connected later

    What it needs is these co's being inspected and fined



  • Registered Users, Registered Users 2 Posts: 4,957 ✭✭✭kirk.


    Probably shouldn't be SWA cables being left out either for unknown stuff to be connected later