How to correctly install heat pumps so that they work properly and efficiently

Comments

  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    Heat geeks have been saying that for a long time too. It does tie in with the no zoning ethos too, always allowing the heat pump to run at best efficiency

    it makes sense, heat a buffer and that heats house vs using the heat directly.



  • Registered Users, Registered Users 2 Posts: 2,489 ✭✭✭SD_DRACULA


    Interesting read, I was contemplating a HP but I think that 99% of installers don't have a clue how to calculate the size of the pump based on the property specifics and they couldn't care less about your bills if they got it wrong and your pump ends up working overtime - once they get paid you're SOL and they take 0 accountability.



  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    This problem is compounded by the newer pumps which are called variable speed HPs leading to oversizing because they cant be arsed doing the design

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 2,489 ✭✭✭SD_DRACULA


    They say your pump needs to be running almost all the time (the less times the compressor restarts the more efficient it is)

    Unfortunately I don't see pumps working with storage batteries (20kwh will be nowhere near to run the pump and the house in one day), it will just drain that very quickly and then you're being scalped at day rates.

    Now I don't know what the pump consumption is once it gets to temp but from the mad values of kwh used per day by HP in the HP thread, I don't see batteries mixing with HPs unless you have 50kwh worth of them, maybe it works for @unkel so like 1 in 5 million 🤣



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    I guess it very much depends how well insulated and airtight the house is. A passive house for example could have a 5kW or smaller HP. From spring to autumn it wouldn't come on if a big enough solar array and eddi was part of the setup.

    How does having the heat pump off for 6 months affect the longevity of the unit? Instinctively I'd say it would increase the life of it but maybe not if sitting idle.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,489 ✭✭✭SD_DRACULA


    Can you get HPs that give you instant hot water like a combi boiler would?

    I don't agree with heating a big tank of water that you may or may not use - wasted heat.

    That way you'd have it during the year but I guess that's the opposite way that HP work as they have to do slow and low heat.



  • Registered Users, Registered Users 2 Posts: 1,542 ✭✭✭DC999



    Another option is go down the air con mini split route. That’s still an air to air heatpump afaik so supposed to have decent COP. And costs wayyyyy less than a normal heat pump. Cost is closer to gas boiler price afaik.  Heats and cools air only, not water. Not connected to rads, and not connected to hot water (so won’t heat water). So same setup as the air con in apartments in europe. Compressor out the back which connects to one of more wall mounted units inside. Plus handy for the (seldom) warm weather in Ireland to reduce the temp at night. We live beside a busy road so can’t open the windows at night (for noise more than fumes).

    I’ll likely look into that when the gas boiler dies or is close to it. Won’t cover the whole house but the remainder could be electric rads. Need a lot of battery capacity for any electric heating so not running on expensive day rate.

    Was a good Heat Geek video but can’t find it now. They did one on air con which I didn’t watch. But they did a follow up with an air con guru to correct some of their misconceptions. Difference is heating companies don’t fit them as air con uses refrigerants, not  gas mains, and there are no water pipes. So need to be refrigerant qualified afaik. Heat Geeks fella didn’t realise air con = air to air heatpump, nor did I.

    This fella got one to supplement his other heating and raves about it. He’s electric rads in places and replaces his oil boiler. Toshiba Air to Air Heat pump (A2A) - Probably one of the best heating systems you can install - YouTube

    Seems a decent setup if you’re ok to have more than 1 type of heating (which I would be as using electric rads in parts of the house for 1st time this year as well as gas boiler).

    @unkel, did you get a mini split air con unit last year? Think I remember you saying you might or where looking at it



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    I don't believe there is a HP on the market that can give you instant hot water.

    Just realised an error in my original post. The HP would be needed to heat the cylinder to provide hot water for the taps/showers on the days the array isn't providing sufficient power via eddi to heat the tank.

    While I see your argument about wasted energy heating a tank, that energy isn't necessarily wasted in a passive house. The heat loss from the tank will contribute to space heating which in theory could reduce the space heating burden on the HP.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    I looked at a similar system - albeit water based - from Panasonic. An ASHP connected to a cylinder for hot water and a fan assisted radiator for space heating. For passive or NZEB houses 1 fan assisted radiator could do the job depending on the size of the home. It too can work in reverse in the summer to provide cooling.


    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    even in a normal house its not wasted either.

    Although the heat loss on the new cyclinders is very little, even at high temperatures. Theres more loss from the pipework coming out of the tank



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,542 ✭✭✭DC999



    Interesting. Never saw that type of rad before. Looks like an electric one but is water rad with 4 speed fans. Fan assisting would help boost the convection. So even at the lower temp the rad runs, it would be getting moving more hot air upwards from the rad. And says it can cool too.

    Heat Geeks did something on that afaik. Normal rad with fans at bottom to try cool a room. Did sfa as far as I recall, but was only half paying attention. But was a very cheap and cheerful stab at it. They did it in a small bathroom.

    For cooling how would it work? Put cool water in rad and then it that 'radiates' into the room colling the warm air? But if a rad takes up a tiny % of volume in a room, I struggle to see how it’s gonna do much. Not being critical, just don’t get how it’s supposed to work. Difference with an air con unit is the amount of air it pushes out per min would be higher. And if it cools from the roof down, the air at the top causes a cool convention of air dropping downwards.   



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    I haven't looked into the technology behind it but do recall reading an additional condensate pipe was needed for the cooling function to work.

    Snip below with further detail. I was wanting to go for it but the Mrs wanted a polished concrete floor and I feared without underfloor heating the screed would feel cold plus the plumber looked at me like I had two heads when I suggested it lol.


    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    That is interesting. Good if your space contstrained re Rad size.

    Have you seen the heat geek where they did a DIY of that, Said condensate is something to be very wary of, Esp if running under the dew point.



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    No I haven't. The cooling function wouldn't be something I'd be too worried about anyway. Getting the heating right a lot more important.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users, Registered Users 2 Posts: 66,122 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    I've already completely dismissed the idea of installing a full heat pump system. Lots and lots of money wasted on labour (and profit) retro-fitting. Then you end up with a system that will cost you more to run than gas / oil, if we end up paying 50c day rate electricity.

    No way Jose, I'll have 45kWh of batteries within the next couple months, but even that simply isn't anywhere near big enough for heating on a cold day (never mind the rest of my electricity needs) On new (passive) houses and on very well insulated / retrofitted houses, it's a no brainer. For the rest of us not so much



  • Registered Users, Registered Users 2 Posts: 66,122 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    @DC999 - not yet, but it's my most likely install when I have to replace my condensing gas boiler, that is nearly 10 years old now. Two large mini splits in the 2 biggest rooms on the ground floor. Then far IR panels in shed and attic (as I use now) and perhaps in the bathrooms. That will be it. I already heat all water with electric.



  • Registered Users, Registered Users 2 Posts: 1,542 ✭✭✭DC999


    +1 for me on that. Our leaky gaff was 'born' in 1940s. So heatpump 'readiness' is wild money. I'd love an A rated new build, but that's not what we have :) We're using a mix of far IR panel, electric rads and gas boiler at mo. And house is at perfect temp in each room and we've halved our gas usage V last winter. So we're trying stuff and finding what works. It's a little clunky as don't just have a single Nest app to change the heating. But works for us



  • Registered Users, Registered Users 2 Posts: 66,122 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    Snap. Trying to settle in this winter, see what works best, the far IR panels are new here. It's a combo of gas and electricity. Using a lot less gas than in the past and the electricity for heating is coming almost entirely from night rate (and some from solar)



  • Registered Users, Registered Users 2 Posts: 2,489 ✭✭✭SD_DRACULA


    It would be very hard for me to move away from the comforts of a combi boiler, for the likes of instant (and fresh) hot water for showers.

    This https://sunamp.com/en-gb/products/thermino-ipv/ will do very nicely for pv/boiler/cheap night rate combo but installers in Ireland don't have a clue about the tech.

    I was thinking about something like this alright https://www.buyitdirect.ie/p/multi-split-27000-btu-smartapp-wifi-inverter-wall-air-conditioner-with-3x-9000-btu-indoor-units-to-a-single-outdoor-unit-iqool-3ms9k9k9k but the A2A COP is way worse than A2W and I think you'll need two of these for the whole house probably but it will give you true zoned control and also help for those 2 scorching weeks we get once a year 😂

    Each unit can pull 3kw so 18kw o'clock easily from these.



  • Registered Users, Registered Users 2 Posts: 4,103 ✭✭✭monkeybutter


    this seems like nuts power useage no? More than 45kwhs per day?

    What kind of multiplication factor are people actually getting and does it make more sense with water to water?

    The only people I know who fitted did go water to water because of this



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    What is the COP of what are referred to here as "far IR panels"?

    Are there such things as "near IR panels"?

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 3,205 ✭✭✭cruizer101


    The near and far just refers to the wavelength of the infra red light, near is closer to visible light its not in relation to at what distance the panels are effective or anything like that. Link here with some more details https://www.scottishenergysaving.co.uk/whats-the-difference-between-near-mid-and-far-infrared-heat/

    Re COP, its just 1, electric heaters convert 100% of electricity to heat. That said they potentially can be more efficient than a convection heater in that you may not need the same output to feel as warm as the convection heater has to heat all the air in the room the panel just heats you. I've no direct experience but have looked into them a bit as considering one for my home office for heating during the day.



  • Registered Users, Registered Users 2 Posts: 1,542 ✭✭✭DC999


    Spot on description of infrared heater. I’ve one for the WFH room and I like it. For me it’s more comfortable than other forms of heating including oil filled electric rad. It heats me, not the air. They really supplement heating, not replace it. Start from around €120 euro for the basic ones, more depending on the wattage and bells and whistles.

    Uses a little less electricity than an oil filled electric rad in the WFH room. It’s a cold room with old windows that doesn’t see any solar gain and loses a lot of heat. Means I don’t need the room to be as warm as I’m in the line of the heat. And drafts don’t affect it. I can even open the window a crack and still be warm – which takes getting used to 😊

    I got a 350W one and it’s fine. That’s likely on the small size for some but ok for me as it’s on the wall close to me.

    Mine is on or off only, can’t adjust the wattage. But it does turn off when reaches the temp you set. Thermostat on it is a very crude. It’s not the temp it thinks it the sensor is on the side of it (so it’s hotter than the room). But once you work out the ‘offset’ it’s ok. I wanted a small wattages one as have solar but no battery so wanted to use the solar excess for heating.

    They work for places you stand or sit at – as in you’re not moving so in the line of the heat. Only other place we could use one would be the sitting room. But would need to be roof mounted over the sofa due to the room setup. That’s the most efficient setup some manufactures suggest, but need to run a cable down the wall to a socket or get a spark to add a spur.

    Some have them in the bathroom to replace the mirror over the sink. But that wouldn’t heat our shower area, so no gain for us there.



  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    Thank you both for the comprehensive and helpful replies, such a rarity here.

    Have seen them roof mounted in a warehouse in Dublin, hot water fed, as you say heat the person not the air

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 3,205 ✭✭✭cruizer101


    You can already get fans that can be added to existing radiators to increase the output, radfan and speedcomfort are 2 I've come across. I've looked into them a bit but havn't been able to find any decent figures on the output increase.

    There are already stats on how the output decreases with lower deltaT, image below shows it.

    It would be great to be able to see the increase based on forced convection. Lets say you have a rad with 2kW output at 50deltaT running off a conventional boiler than heats the room more than sufficiently. You want to put in Heat pump but the lower running temp means you have only a deltaT of 20 so the output is 600W, not enough for the room. What if using fans you could bring that back up to 1.2kW. That might be enough heat for the room without having to get a bigger rad if you run it constantly instead of cycling at 2kW. It could make Heat pumps much more attractive if you didn't have to replace the radiators.

    I did try see how much of a difference it would make but trying to find the heat transfer coefficients for free convection and force convection is hard as I think the radiator geometry would come into play. Best way would probably be experiment measuring the temp in and temp out of radiator with a fixed deltaT and flow rate with fans and without. Bit much for me to bother but easy enough setup for a business or university with an interest in it.



  • Registered Users, Registered Users 2 Posts: 1,642 ✭✭✭THE ALM


    Interesting read, thanks for sharing.

    Is an area we are looking at at the minute as we are looking to replace the boiler.

    Reading various forums and trying to educate myself it seems the main gripe is the design and installation of a heat pump so it makes you wonder if you get someone in have they designed it properly. If anyone can recommend someone then let me know.

    I have carried out some heat loss calculations so will be interesting to see how they compare.



  • Registered Users, Registered Users 2 Posts: 12,425 ✭✭✭✭the_amazing_raisin


    Tbh I don't think that it's a case they aren't arsed, the installers aren't heating engineers, they're not really qualified to do the design to any degree of depth


    From what I've seen, they seem to have a basic cookie cutter system design that they put into all houses. Bigger houses, scale the system up a bit, etc.

    The manufacturers seem to try and support this, they make standard systems and fairly simple online calculators that just spit out a system spec


    The problem is without someone qualified double checking the system, it can end up pretty poorly optimised. Installers could probably get away with this back in the days of oil and gas. You can kind of balls up an oil boiler to some degree but if it's putting out water at 70C then the house will be warm regardless and the customer probably won't know any better

    With heat pumps, having an efficient design is critical. I think this has led to some pretty terrible design decisions and bad installations

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    I wonder how many people actually realised how much energy is being used to keep the house warm? Actually seeing the electric bill, vs getting 2-3 fills of oil a year. Which has doubled in price also..



  • Registered Users, Registered Users 2 Posts: 12,425 ✭✭✭✭the_amazing_raisin


    Absolutely, people tend to compare the price of fuel but they don't compare the consumption. One person might be using 20l of oil a day and think it's fine until they see someone using 10l per day for a similar type of house


    I'm starting to subscribe to the idea that the best thermal store is the house itself. There's a lot of stuff in the house which can absorb thermal energy, furniture, concrete flooring as well as the structure of the house itself

    That should provide a reasonable buffer if the house is well insulated.

    It's interesting how a buffer tank is supposed to stop the heat pump cycling but has been shown to actually increase it


    I still think there's value in using a buffer that you can zone out using valves for a heating system that can't provide heating on demand, like solar. That'll give you the ability to store energy when it's abundant and you can cut it off from the heat pump when it isn't needed

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 66,122 ✭✭✭✭unkel
    Chauffe, Marcel, chauffe!


    When I tried to heat the house purely with electric (and trying to avoid the peak rates), the cold snap put my face right into the numbers. Which are a lot higher than I thought they were. With gas / oil being like 3-5c per kWh like they were for years up to about a year ago, you didn't really notice it. But you do know

    I've already heard from several people around me with modest houses having got a €1000 gas bill the last time. And electricity bills not far off (before the govt subsidy)



  • Registered Users, Registered Users 2 Posts: 12,425 ✭✭✭✭the_amazing_raisin


    100% agree, people would often say that gas is more cost effective that electric for cooking. It's easy to say that when the fuel is just really cheap, no reason to be efficient then


    I suspect a lot of those folks with the huge fuel bills are not switching providers and are getting f!cked at the standard rates


    I cannot understand people not doing that. I've known people who would drive across town for cheap petrol but won't spend 20 mins finding a cheaper energy tariff and switching

    There's really a lot of disinformation around this. I remember a colleague of mine from India was complaining about the electricity bill in the house share he was in. I asked why they didn't switch provider and he said the landlord told them it would cost €300 to change

    It's BS like that which keeps Electric Ireland and Bord Gais in business 🙄

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Moderators, Home & Garden Moderators Posts: 6,634 Mod ✭✭✭✭graememk


    Gas bills are every 2 months, like electric?

    1000 euro is a shock bill.

    I thought my last electric bill of 330ish was bad(before the gov credit)

    Although short cycling on a heatpump can be very detrimental to efficiency. And with a buffer might mitagate it a bit, but then controlling it properly is the issue.

    I can understand the heat geeks ethos not to zone on a condensing boiler or a heatpump to get the return as cold as possible.

    .. have the number for a company that does the cavity insulation must get in contact with them.



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    I'm continuously shaking my head when I see new builds with insulated plasterboard fixed to the inside face of a cavity wall. It shows a real ignorance towards the thermodynamic properties of a building.

    Put whatever insulation you need into the cavity to achieve the necessary u value and just plaster with sand cement and a skim the inside face of the wall. That way you get a thermal store, a more comfortable room - as it won't heat up and cool down rapidly - and the air tightness task is simplified significantly.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    Perhaps but chasing external walls for sockets etc and making the back of sockets airtight is a lot of work.

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    chasing is not bad if you have the correct equipment and airtightness is easy and quick with the use of airtight paint.

    Plasterboard on the other hand is notoriously difficult to make airtight as heat can escape from a multitude of places.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    Valid points, Not arguing with you, just teasing out the issues :)

    I sand and cement the wall even when using a pb service cavity.

    I can't remember which way the dial is moved in a BER when all external walls are PB (light) vs block (heavy) when doing the thermal mass calc

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 1,786 ✭✭✭DownByTheGarden


    That would be dripping with condensation though



  • Registered Users, Registered Users 2 Posts: 899 ✭✭✭ColemanY2K


    i'm afraid i can't claim to know the answer regarding the BER comment but to install pb on to cavity wall construction of a new build would negate the thermal store. This would in turn reduce the energy efficiency of the house, consequently putting more load on the heat pump in order for it to maintain the set temperature. in my head it defies logic when i think about it.

    🌞 7.79kWp PV System. Comprised of 4.92kWp Tilting Ground Mount + 2.87kWp @ 27°, azimuth 180°, West Waterford 🌞



  • Registered Users, Registered Users 2 Posts: 12,425 ✭✭✭✭the_amazing_raisin


    I thought the idea then was to put the airtight layer on other side of the cavity to the plasterboard?

    So the cross section from outside to inside of a timber frame would look a bit like this


    Cladding (blocks or render) -> External cavity -> OSB with vapour barrier -> Structural timber with insulation in between -> Insulation panels -> Airtight barrier -> Services cavity with thin studs -> Plasterboard and plaster

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Registered Users, Registered Users 2 Posts: 12,425 ✭✭✭✭the_amazing_raisin


    I think the theory behind timber frame houses is that they don't have much thermal mass to retain heat and instead use insulation to lower the heating demand

    Hence the old saying that timber frame houses heat up quickly but also lose heat quickly compared to block houses

    How well that theory works is a bit debatable, having less thermal mass gives you less storage but you also don't have to heat up that thermal mass in the first place

    FWIW, I kinda agree that insulated plasterboard isn't the right approach. I'd almost be in favour of insulating the cladding instead and having the timber frame inside the insulated space. Probably better for the house's structure overall, keeping the frame relatively thermally stable

    "The internet never fails to misremember" - Sebastian Ruiz, aka Frost



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 2,489 ✭✭✭SD_DRACULA


    I would agree with insulating on the outside but to do a full house is very silly money even with "grants"

    The house already had interior insulation but it was that white crap they used in the 90s (before kingspan) stuck to plaster board (60mm or so) and then stuck to the wall with 2-4cm blobs of tile adhesive or something (max cowboys), no wood studs or anything (except in batrooms), which I'm sure for air circulation the empty space behind the pb helped but house was an igloo once the heating off and you could hear the wind.

    Replaced it with kingspan and it made a big difference for sure.



  • Registered Users, Registered Users 2 Posts: 12,888 ✭✭✭✭Calahonda52


    The main improvement is due to getting rid of the dot and dab and closing that gap which was fed with air from wall vents as the wall vents were not fully sleeved all the way through.


    I oversaw the remediation of 200 houses in Dublin back in the day just by using airtight tape to close the gap between the pb and the wall.

    I did 2 houses, produced a little video and the residents took it on to help each other. Good community based project.

    Tape was 23 a roll per house

    ..

    aero board is 0.035

    kingspans between 0.025 and 0.033

    so not a massive difference

    “I can’t pay my staff or mortgage with instagram likes”.



  • Registered Users, Registered Users 2 Posts: 5,965 ✭✭✭creedp


    I have a GSHP in a 2011 build house (A2 rated) all block build (internal & external walls) with concrete slabs on 1st floor Its a 12kw HP which is on all year but only heats the water from May to Nov. I have a meter attached and just checked it there and it has used 551 units in total over the last 36 days (av 15kw per day) all of which were used at night rate. I have ufh throughout and only have 2 stats, one on each floor. I think thermal mass is essential with HPs as you can heat the house overnight and it will pretty much last all day. I have no other heat source in house except for a log stove which I lit probably 5 evenings this winter to-date and that was only for the added comfort late in the evening. As for heat loss from hot cylinder, I have a 500l cylinder in the attic which has been kitted out as a large 'hot press'. I heat the tank every night to 50 deg c, which from memory only takes about 3 units of electricity (must check that again), and this lasts all day for all hot water use incl showers. The minor heat loss works great to keep the area 'aired' so I don't consider it to be heat lost.

    So for me the HP has been a great success but the system was designed and installed as part of the new build by a guy who obviously knew what he was doing - unfortunately he's out of the game now so I woudnt even know where to start looking for someone to install a system. A couple of neighbours, who were very skeptical of HPs when I was installing given the high installation costs, are now considering retrospectively installing a HP given the low running costs of my set up but I have cautioned against simply drop kicking a HP into an older house with rads. It simply wont work as well and they will be hugely disappointed when the expected savings wont materialise.

    Btw thats some battery capacity you have, I wouldnt mind drop kicking some of those into my ever degrading Leaf!!



  • Registered Users, Registered Users 2 Posts: 1,542 ✭✭✭DC999


    Fair play to you for explaining your setup. 15kWh a day for heating a whole house is amazing when it’s this cold!! Summary - GSHP works a charm for you in a 2011 build house (A2 rated) with UFH concrete slabs on 1st floor. Which means new builds with UFH are very suitable for heat pumps with low running costs.

    Old houses are a different beast. For us to get concrete slab UFH in an 80 year old small 2 up 2 down old Dublin council house would mean literally digging the solid floors out of the house to drop them down for UFH. That’s a mechanical digger inside the house I'd guess. Just not a runner unless getting work done where we’re leaving the house anyway, even ignoring the huge cost. I'd love an A rated house with a HP for comfort and low running costs. Need to buy that lotto ticket I think :)



  • Registered Users, Registered Users 2 Posts: 12,425 ✭✭✭✭the_amazing_raisin


    Anyone want to learn how to install a heat pump?

    Unfortunately I think you have to be a UK citizen to get it for the discounted price 😭