Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie

Domestic Solar PV Quotes 2022 - No PM requests - See Mod note post #1

Options
1195196198200201

Comments

  • Registered Users Posts: 1,454 ✭✭✭DC999


    Apples V apples: When getting quotes, ask for the wattage on the solar panels so you can compare the cost per kW (or 1000watts). Also ask for the inverter size in kW. 

    I agree you don't need a battery. Reason is 1) a small battery will do less as you've high usage - using 32kWh a day (averaged 12000kWh over the year, but in reality winter will be higher). 

    2) Move the EV charging and household stuff like washing machine, dishwasher, immersion... to cheap night rate on your smart meter. Then get paid FIT for unused units and buy cheap power at night. You can always get a battery at a later stage. 



  • Registered Users Posts: 587 ✭✭✭aisling86


    @DC999 thank you! I’ve 3 companies all the same panels & inverter now so it’s just down to price next.



  • Registered Users Posts: 397 ✭✭ellee


    I've had three quotes and they are all much higher than what people are saying they are getting on this thread.

    1. 3kw system + 2.4Kwh battery = after grant 6,350.
    2. 3kw system + 2.4Kwh battery = after grant 7,450
    3. 4Kw system + 5Kwh battery = after grant 11,746!!!!! (I do appreciate I am getting maybe a good bit more here)

    I'm in Dublin, does that make a massive difference???

    We weren't going to bother with a battery but one of the companies is maintaining that you can fill it with cheap electricity at night and then use that to start your day which did make some sense I thought. But am I spending a lot to save pennies????



  • Registered Users Posts: 760 ✭✭✭PGL


    Hi folks.

    I was active-ish on this thread a few years ago when I got quotes on two different occasions to get solar panels installed on the roof of my semi-d home in Dublin. I regret not pressing go back when i first obtained quotes as prices shot up for the next few years after that, and I decided to park the idea until costs came down. I intend to get a series of quotes early in the new year, and hopefully get them installed in March/April when the brighter weather returns.

    Back when I got my first set of quotes (approx. 2.5/3 years ago), the rough rule of thumb I was told on this thread was your price was reasonable if you paid roughly €1000 per kW (excluding batteries, and taking account of grants). What is the equivalent rule of thumb these days, and have prices reduced in recent times?

    Thanks a lot folks!



  • Registered Users Posts: 6,404 ✭✭✭con747


    A calculator here http://davidhunt.ie/solar/ to give you a rough guide. Just beware the grant drops by €300 in January. More info in the stickies here https://www.boards.ie/categories/renewable-energies

    Don't expect anything from life, just be grateful to be alive.



  • Advertisement
  • Registered Users Posts: 19 505315


    Hi guys


    This is the quote I got from **** for a Solar PV installation and a new boiler with a hive zoning system. I'm not sure if this is a good price overall for the job and as I understand it this is after a couple of discounts they applied seeing as we are getting so much done together with them. Would love some honest feedback. We've been dealing with some crazy bills for the last couple of years so I'm pretty tempted to go with these guys to get the entire job done in one go unless the prices are absolutely ridiculous. If it is as outlandish as I suspect it would be greatly appreciated if some tested and trusted alternative installers can be recommended. We're located in Portlaoise so any local people or even people with experience with these guys your feedback would be greatly appreciated. Thanks


    Post edited by 505315 on


  • Registered Users Posts: 33 kevinr7213


    Hey the general rule of thumb these days seems to be around the €1200 mark per kW. Just get plenty of quotes. I was in much the same position as you. Two years ago I had recieved alot of quotes but unfortunately we discovered a leak in the roof. To make a long story short, eventually got it sorted. Started the whole process of looking for quotes again 4 weeks ago. There were huge variations in prices for similarly spec'ed systems. Finally settled on a local installer (cork) who was able to hit the €1000 per kW. 5.66kw system, E/W split, hybrid inverter, BER included. The price of pannels have dropped dramatically this year, you should be able to find a competitive quote no problem. Some good advice on this fourm, and if struggling for competitive quotes there are some very helpful Solar PV groups on Facebook. Best of luck with it.



  • Registered Users Posts: 26 PCR


    Got a quote for 10 430w jinko solar panels and inverter.

    optimiser €600 (€60 per panel that will need an optimiser)

    ground rod (if it can’t be located) €300

    zappi charger incl vat €1500

    including grants total comes to €8300.

    EDIT: Eddi included

    this is coming out 2k cheaper than the quote I got from SSE Airtricity so I think it is good value.

    Am I on the right track price-wise?



  • Registered Users Posts: 6,404 ✭✭✭con747


    Seems very expensive to me for both systems. A lot of waffle in that quote as well.

    Don't expect anything from life, just be grateful to be alive.



  • Registered Users Posts: 797 ✭✭✭tonysopprano


    Davidhunt.ie/solar, this should be your starting point


    If you can do the job, do it. If you can't do the job, just teach it. If you really suck at it, just become a union executive or politician.



  • Advertisement
  • Registered Users Posts: 788 ✭✭✭staples7


    If you pull it back to panels and take off the 2400 of additional items you're at about 5.9k for 10 panels and inverter. ive been quoted 6300 for 17 inc BER, hybrid inverter.

    Its not the worst though



  • Registered Users Posts: 26 PCR


    Thanks. When I discount charger, optimizer etc. it’s just over the acceptable range but not extortionate, I’ll get one more quote and decide.



  • Registered Users Posts: 377 ✭✭SodiumCooled


    Hi All,

    I am just wondering if anyone could give me a rough guide on what I should expect to pay for a PV install on a new build (so no grant). I wasn't planning on getting the PV until a later date (e.g. an undecided time after being moved in) but my electrician has now asked if i'd be interested as he wants to get into PV installing and would be interested in getting a few under his belt along with the 0% VAT which may not last I am considering going ahead.

    I am waiting on his price and he has said he plans to more or less do it to break even (i.e. give me a good price) but I'd be interested to get an idea of what I should be paying. I will be going max number of panels (20 I think), installation, mounting hooks and whatever else goes with it. I also want a battery but how much battery would people be recommended 5Kwh more and price wise (house is approx 265 sqm, A2W, MVHR, no electric car currently and not planning one in the near/medium term).

    Basically a rough guide price on what anyone in the know would recommend I install. Scaffolding is still in place so no cost needed for access. Many thanks.



  • Registered Users Posts: 1,454 ✭✭✭DC999


    As the sparks is brand new to it, simplify the design and just get panels. 

    So no battery and no battery-ready inverter (called hybrid inverter). You can always get a battery at a later stage. If you’ve a smart meter you get paid for unused units (called FIT). A 5kWh battery is way too small to contribute towards your A2W, MVHR and run the house. Batteries take a lot of understanding to get working properly, and he’s new to it. That’s why I’d suggest ignore the battery for now.

    Don’t get a water heater either (like an Eddi). FIT makes them redundant cost wise.

    Track back here to see the costs for installs. Then you'll want your sparks to be a lot cheaper. He’s learning on the job! And get a few quotes which will help the cost conversation with your sparks. To compare, look at quotes for larger systems like 8kWp with 5.5kW inverters (which is the max you can get without paying the ESB €1000+ to upgrade your connection). Smaller installs tend to cost more per kWp due to labour costs being high for all installs.

    Unless you know and trust him, think twice about you being customer number 1. I know we’ve all to learn somehow. So it’s all a balancing act. That said, with just panels (compared to adding a battery too) there is way less to go wrong. 



  • Registered Users Posts: 788 ✭✭✭staples7


    Id be wondering if getting a string inverter now instead of a hybrid is good advice..... Surely you'd want to spend a little extra and go hybrid to cover yourself for batteries down the line. Just my 2 cents



  • Registered Users Posts: 6,719 ✭✭✭deezell


    Hybrid inverters are string inverters, they are capable of input for seperate sets of panels (strings). Better to call the non hybrid, er, non hybrid or non battery to avoid confusion. A hybrid optioned inverter could cost 5-600 more for the same power capacity. The 20 panels mentioned would not be able to output in full on a grid tied inverter,, so be aware that the potential 10KW they produce will not be available on grid, as this is limited to 5kw by regulations. Oversizing will extend your low season output though. An inverter with a partial off grid load can split the output between on and off grid, your electrician could wire a section of your house to be off grid, but fed by the mains (or a battery) during dark or power cuts. Sungrow make such models, with about 2+kw to the off grid circuit, (lights, ring main, fridge etc but not kitchen or heavy current outlets). A new build is an ideal opportunity for learning! Get the tilers to put in the hooks.



  • Registered Users Posts: 377 ✭✭SodiumCooled


    Hi, thanks for the feedback and advise. I appreciate the fact he is doing it for the first time but he is very competent and has the support of who is supply him who he has said already are very helpful in getting him up to speed. I also thing he will take his time and make sure its done right a thing i would question looking at some of the installs done by established people around my area (e.g. a system oriented north for no reason at all).

    While I get what you are saying on leaving out the battery I don't think its worth doing without battery (nor does my sparks) and I feel that's the general consensus nowadays so from what you are saying I should be looking at 10kwh of battery back up and the inverter to go with it. Also if I was to get the battery later I wouldn't get 0% VAT if I understand the scheme correctly.

    I will look back through the thread at other pricing but just for comparison I should be looking at 10Kw systems + battery/inverters to match what I described?

    As for the hooks, unfortunately this conversation only stared half way though first fix so house was long roofed but my roofer has already agreed to come back to fit the hooks so a bit more work but the fact scaffolding is still there makes it more straight forward.



  • Registered Users Posts: 2,554 ✭✭✭wexfordman2


    Of you don't get a battery, then you will lose out on the 0% vat element of the battery when you go to install one or upgrade later.


    If you have no medium term plans in an ev, then I would certainly go for a bettery, and prob 10kwh worth.


    The point about batteries now as much as anything else, is the ability to offset your usage, especially with the advent of smart metres and smart tarrifs.


    For example, some inverters are very smart, they can link in to your ESB tarrifs, and decide when to charge or discharge based on that (ie, reserve battery power for your peak hours between 5 and 7).


    Another features is predictive generation, so your inverter will decide in whether to charge.yoir battery from the off peak grid based on how much solar is predicted to be generated next day.


    Not all inverters offer those kind of features though.


    I have those, but only a 5kwh battery and am seriously.considering upgrading with another 10kwh.


    If you don't go for a battery, and you really really should imho, IF you are based nearby and IF your electrician is up for it, I would happily pay you for your 0% vat battery (if it is same brand as well). Way too many ifs I know, and I partly say it in jest :-)



  • Registered Users Posts: 2,554 ✭✭✭wexfordman2


    Oh yeah, run a cat6 cable to your inverter, for its internet connectivity,.try not to go wifi!



  • Moderators, Home & Garden Moderators Posts: 6,087 Mod ✭✭✭✭graememk




  • Advertisement
  • Registered Users Posts: 2,554 ✭✭✭wexfordman2


    The one for CT'S would I assume be part of the overall solar install, the one for internet would be seperate to avoid wireless connectivity if he could.



  • Registered Users Posts: 377 ✭✭SodiumCooled


    Aside from bathrooms - the utility where the batteries would likely sit is the only room in the house not to have at least 2xCAT6 cables 🙈. Should be possible to still run one or two though will say it to the electrician. Ideally I would put the batteries in the garage but don't think it's a runner as he said they will need to sit near the consumer unit where the cable from the panels will also be routed to which is all in the utility.

    A bit of an aside but I know the batteries and panels don't work in a power cut. I will be getting a change over switch installed and I was wondering do the panels/batteries sit on the consumer side of the switch i.e. will the genie fool them into operating during a power cut?



  • Registered Users Posts: 2,554 ✭✭✭wexfordman2


    Typically the batteries can be set to run a small number of sockets in the event of a power cut, so even if you are putting in agenie and changeover switch I would still plan for the batteries to run say your broadband/wifi and a tv with at least one downstairs socket for charging phones etc.


    What make of diverter is he proposing ?



  • Registered Users Posts: 6,404 ✭✭✭con747


    Both batteries and panels can work in a power cut, I have a change over switch to power the whole house and had the fireman switches removed so the panels work in a power cut. Since you are not going through the SEAI there is no reason for the fireman switches as it's only required if getting the grant. They don't use them in the north or the UK.

    Don't expect anything from life, just be grateful to be alive.



  • Registered Users Posts: 6 chatb0x1


    Thats seems to be a very high price. Im getting the same inverter - no bat and 9 435 JA double glass panels(slightly cheaper than Jinko) eddi for less than half that.

    I must have got 10 quotes all lower than that.



  • Registered Users Posts: 377 ✭✭SodiumCooled


    No specifics discussed really as yet apart from saying glass glass (I think) panels are more expensive but the best and we would be going for these. Other than that just measuring etc and discussing the hooks.



  • Registered Users Posts: 74 ✭✭ParaHappyman


    Hi everyone, looking for thoughts and advice please. Considering either of the following two options from a recent quote:

    Option #3 - 7.29 KWP connected to Renac 5KW Inverter

    18 x REC Premium 405W Monocrystalline Twin Peak 5 modules

    Bisol Mounting system

    1 x Projoy Fire Safety Switch

    AC Switchgear

    Renac 5kW String Inverter

    Costing

    €8,000 Final Cost



    Option #4 - 7.29 KWP connected to Alpha Inverter with 10.1KW Battery

    18 x REC Premium 405W Monocrystalline Twin Peak 5 modules

    Bisol Mounting system

    1 x Projoy Fire Safety Switch

    AC Switchgear

    Alpha 5kWp Inverter kitted to 10.1kWh storage capacity

    Costing

    €13,000 Final Cost


    Is this a good price? Are 405w panels a bit low and should I be aiming for 430w etc?

    New to all of this and looking for advice. Grant not applicable as it is a new build. Thanks



  • Registered Users Posts: 20,055 ✭✭✭✭Cyrus


    Just been thinking about it (as have bought a shelly em and am looking at our usage) re whether getting a battery makes sense.

    In the winter, before any car charging, we are using around 45KWh per day split 30 day and 15 night, when the car is charging that is more like 105 split 30 day 75 night .

    Summer general usage will be a lot lower as the heatpump wont be in use so much.

    But in reality is a 5 KWH battery worth my while? itll only run the house in winter for a few hours if i charge up on the night rate, that would be longer in summer but youd generate plenty of solar anyway and could sell the rest to the grid....



  • Registered Users Posts: 1,454 ✭✭✭DC999


     

    I’d agree with your own thought process based on your usage. No, a 5kWh battery isn't worth it based on 45kWh a day in winter ex the EV. It’s too small to make any contribution. Ignore the battery for now.

    Step 1 is load shift what you can to night-rate as save cash that way.

    How? If you’ve UFH you can move the heatpump to run a lot on night rate (see the heatpump thread here). Heat the hotwater tank on the heatpump during the night rate (assuming it’s a well insulated tank it won’t lose much heat). Load shift dishwasher, washing, drying... to night. Keep up the good energy monitoring to track progress!

    Get paid FIT for unused solar.

    Btw, your EV stats aren’t right unless you only charge the EV once or twice a week. But that won't impact your logic as EV will be on cheap night rate.

    Step 2 - in time… look at the option for a large DIY battery in time (see another thread here on that).

     



  • Advertisement
  • Registered Users Posts: 20,055 ✭✭✭✭Cyrus


    Thanks!

    yes i only charge once or twice a week (big battery 86.5KWH)

    heatpump is currently set to heat water at night, unfortunately my dishwasher doesnt have a time delay but will move as much as i can to night rate.



This discussion has been closed.