Solis inverter settings

11516182021

Comments

  • Registered Users, Registered Users 2 Posts: 4,409 ✭✭✭...Ghost...


    Question Please.
    I connected my DIY Seplos battery to my Solis Hybrid 5kW yesterday. All was working fine.

    Last night I was adjusting the settings so it would charge the battery at night. I was winging it mostly and accidentally set it to off-grid. In a momentary panic, trying to restore to self-use, I hit “reset” on the data logger. I managed to get everything working OK, except the inverter was showing as offline on the APP. I did a 15 second data logger reset this morning and both inverter and data logger are showing offline. The inverter and battery are working fine otherwise.

    What do I need to do to bring it back online? I’d like to see what’s happening especially since the battery just got installed.

    Current view.

    Stay Free



  • Moderators, Home & Garden Moderators Posts: 7,006 Mod ✭✭✭✭graememk


    You'll need to get the hotspot that the WiFi logged puts up and re enter your own WiFi information again



  • Registered Users, Registered Users 2 Posts: 4,409 ✭✭✭...Ghost...


    This is done physically at the inverter, yes? Thanks. I’ll try that later. What stumped me is the logger was connected last night, but the inverter wasn’t showing. Otherwise I’d have put it down to a wi-fi connection or settings issue.

    Stay Free



  • Registered Users, Registered Users 2 Posts: 4,409 ✭✭✭...Ghost...


    1 of 2 working. I connected to the DL Wi-Fi and connected it to my router.

    So, the Data Logger is connected again, which brings me back to where I was this morning before I did the data logger reset.

    The inverter is still showing as offline.

    Stay Free



  • Registered Users, Registered Users 2 Posts: 4,409 ✭✭✭...Ghost...


    What I am noticing is the orange "net" light is not staying lit. It is fast flashing for a couple of seconds and going blank for a few seconds before trying again. So it is not communicating with the inverter. The red power light is lit and the green Wi-Fi light is lit. No luck finding an answer online, so have emailed the installer to see if there is a solution.

    Do these loggers fail often?

    Stay Free



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 1,933 ✭✭✭keith_d99


    Hi all - I got a Zappi installed a number of months back. During my EV window, the Zappi will charge at around 7KWH

    The Solis app only tracks some of that load though which is frustrating - meaning my Grid import stats are pretty useless.

    Attached is last night's EV window for reference … this had the EV charging, the Battery charging and the Eddi also heating for a period.

    The Solis is reporting 19kw import for today when in reality it is 36KWH (reading from MyEnergy App)

    Any ideas why?

    I understand the inverter can only output 5KW at any one time …. but surely the grid clamp should be reporting up to 12kwh? (Or am I incorrect)



  • Registered Users, Registered Users 2 Posts: 456 ✭✭munsterfan2


    Is the zappi connected 'outside' the CT clamp for the grid, ie - connected to the main esb box before the connection to the consumer unit ?



  • Registered Users, Registered Users 2 Posts: 1,933 ✭✭✭keith_d99


    Yep at the meter box … and I am pretty sure the grid clamp for the Solis is at my fuseboard (not 100% on that though)



  • Registered Users, Registered Users 2 Posts: 456 ✭✭munsterfan2


    That makes sense, the solis clamp isnt seeing the electricity flowing to the zappi. Not certain if possible, but you would need the solis CT clamp to be before the zappi connection



  • Registered Users, Registered Users 2 Posts: 1,933 ✭✭✭keith_d99


    Yeah it's s strange one - when it's just the Zappi on - the Solis clamp is registering 4KWH of the 7KWH load



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 10,370 ✭✭✭✭Hurrache


    Query on the overcharge SOC, my understanding was this is the limit as to which the battery will discharge. Self use mode is on and. I have my overcharge SOC set to 15% with the force charge set at 10%. However my battery is currently at 10% and as of right now the load is .301 with .259 coming from the grid and .041 coming from the battery.

    Shouldn't it have stopped discharging at 15% or thereabouts?



  • Registered Users, Registered Users 2 Posts: 4,409 ✭✭✭...Ghost...


    No. The overdischg SOC is what you need to set to 15%. The overharge SOC I have set to 95% and my battery tends to stop charging at 98.5% and I get no battery OV Alarm. I had it at 100% and I was getting battery OV Alarm. You also need to set the force charge feature, usually 5% lower than the discharge level??

    My own probably needs a bit more tweaking, but here is how mine is set up. I should have my Battery capacity at 315Ah for example, but it's doing OK and the inverter will be changed soon (Warranty issue) so I will leave as is.

    Stay Free



  • Registered Users, Registered Users 2 Posts: 10,370 ✭✭✭✭Hurrache


    Ah, just read back over my post, I had meant to say my overdisharge SOC is at 15%.

    I monitored it last night and it didn't drop below 15% so not sure what was happening the previous night. Maybe because I had just made the over discharge SOC and force charge updates and they didn't take effect until a refresh or something.

    I haven't looked at what my overcharge SOC is, what's that do, the max the battery will charge to?



  • Registered Users, Registered Users 2 Posts: 819 ✭✭✭conor_mc


    I had one evening where my charge dropped below the Overdischarge SOC but I think it may have been related to a high draw from a heat-pump dryer at the time. Forcecharge even kicked in a little below the value I'd set there too. So it did what was needed, but was little lazy going about it!



  • Registered Users, Registered Users 2 Posts: 4,409 ✭✭✭...Ghost...


    The inverter does some funny things. I've already had a couple of head scratching moments and it's only in recently.

    The overcharge SOC will stop charging the battery once it reaches the percentage of charge set. More important for Li+ than LiFePO4 batteries, the former not being happy at high charge rates for any period of time.

    Stay Free



  • Registered Users, Registered Users 2 Posts: 1,682 ✭✭✭Mad_Mike


    Quick question regarding priority feed-in

    My dad recently had a Solis inverter installed with 14 panels and it was on self use mode, but about 2 weeks ago he added a 15kw battery to the system. He has been on to Energia last week and is waiting for the new tariff to kick in, so I was experimenting with the settings and think I have it sorted for night charging now and then priority feed-in all day

    Today is the first day I let it run fully, but I see the battery shows discharging .027kw on every single timestamp. Adds up to feck all over the day, but just curious why it doesn't actually sit at zero usage all day?



  • Registered Users, Registered Users 2 Posts: 931 ✭✭✭tommythecat


    Is it at 100% when this discharging happens? Battery's don't like to sit at 100% so the BMS will discharge a bit and then recharge over the course of the day.

    4kwp South East facing PV System. 5.3kwh Weco battery. South Dublin City.



  • Registered Users, Registered Users 2 Posts: 1,682 ✭✭✭Mad_Mike


    No, that's what I don't understand. Think it was at about 91 when pv started producing and it has dropped to maybe 89 despite the solar keeping house going all day. Not a big deal really but was just wondering if this is the way it's working for others.

    [Screenshot added]



  • Registered Users, Registered Users 2 Posts: 819 ✭✭✭conor_mc


    My Solis does that 0.027 trickle from 100% lots of the time too.



  • Registered Users, Registered Users 2 Posts: 1,682 ✭✭✭Mad_Mike


    Thats great thanks. All I needed to hear really! Was afraid with all the messing around with settings that I had missed something 😂



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 119 ✭✭guano_jim


    I have a S5-EH1P5K-L inverter, 4.3kWp of PV panels and 5.3kwh battery, EDDI, and notice that every​ night between midnight and about 6am there is a 15%-20% loss of SOC (see graphic) from what appears to be a constant 100w drain
    increasing two or three times to a 230w drain - even though there is no load​ from the home and minimal power is flowing to/from the grid.

    Is this normal? what are other people getting? Installer saying that some battery charge/discharge is needed to keep the battery "awake" - 800w over 6 hours seems unlikely? what should the inverter use when not actually doing anything?



  • Registered Users, Registered Users 2 Posts: 9,201 ✭✭✭con747


    Mine uses anything from 100w to 125w per hour just to function with nothing else drawing a load. A fridge or freezer motor kicking in is most likely the extra load.

    Don't expect anything from life, just be grateful to be alive.



  • Registered Users, Registered Users 2 Posts: 931 ✭✭✭tommythecat


    There is always load it's just the app doesn't show it below a certain level.

    4kwp South East facing PV System. 5.3kwh Weco battery. South Dublin City.



  • Registered Users, Registered Users 2 Posts: 198 ✭✭Warrior011


    Hey everyone, recently got PV and solis inverter installed with 5kW battery. Have it set up to charge the battery on overnight rate, noticed this morning that it used up the battery (about 50% of it) between 7am and 8am when the heat pump was working for a shower, is there a way to set the inverter to prioritise using electricity from the grid to power the house between 2300 and 0800, at the moment it is set to charge the battery during these hours on the night time rate.



  • Registered Users, Registered Users 2 Posts: 931 ✭✭✭tommythecat


    If the battery is set to charge until 8am it shouldn't kick in at 7am. That's unusual. I would check the settings again. Do you have a discharge rate set by any chance? Just for example I charge my EV between 2-6am and my battery is set to charge between these hours also and even if it is fully charged before 6 it will not kick in and start charging the car. So it should work for you. I have the same inverter.

    4kwp South East facing PV System. 5.3kwh Weco battery. South Dublin City.



  • Registered Users, Registered Users 2 Posts: 196 ✭✭soram


    check the inverter time is set properly. It is probably on European time and an hour off!



  • Registered Users, Registered Users 2 Posts: 198 ✭✭Warrior011


    Ok so check again. Time on inverter is correct, but it seems that it had changed the time of grid use back to 6am somehow, Ive reset it to 8am and I'll see what the morning brings. Thanks!



  • Registered Users, Registered Users 2 Posts: 1,682 ✭✭✭Mad_Mike


    Also just make sure all the other charge/discharge slots are set from 00:00 to 00:00



  • Registered Users, Registered Users 2 Posts: 198 ✭✭Warrior011


    So, an update, didn't discharge this morning, think the time setting being changed back to 8am did the trick, charge/discharge slots set 00.00 to 00.00 too



  • Advertisement
  • Registered Users, Registered Users 2 Posts: 931 ✭✭✭tommythecat


    Sounds like all is well now. Enjoy the new system.

    4kwp South East facing PV System. 5.3kwh Weco battery. South Dublin City.