Advertisement
If you have a new account but are having problems posting or verifying your account, please email us on hello@boards.ie for help. Thanks :)
Hello all! Please ensure that you are posting a new thread or question in the appropriate forum. The Feedback forum is overwhelmed with questions that are having to be moved elsewhere. If you need help to verify your account contact hello@boards.ie
Hi there,
There is an issue with role permissions that is being worked on at the moment.
If you are having trouble with access or permissions on regional forums please post here to get access: https://www.boards.ie/discussion/2058365403/you-do-not-have-permission-for-that#latest

Parasitic Capacitance.

  • 12-12-2023 9:14pm
    #1
    Registered Users, Registered Users 2 Posts: 2,766 ✭✭✭


    On some PV installations there can be intermittent tripping of the rcd/rcbo when it rains or when condensation levels are high. This occurrence is usually only with single phase, transformerless inverters.

    The pv panels themselves become conductive in the moisture and half of the grid amplitude can arrive at the panels.

    You have the panel mounted on a grounded frame and when the voltage arrives on the conductive panel it can store charge like a capacitor. The alternating voltage changes the state of charge of the capacitance and this gives rise to a displacement current proportional to the capacitance and the applied voltage.

    This "leakage" current is seen as an imbalance at the inverter and beyond at the rcbo causing the nuisance tripping.

    This is my understanding of the phenomenon after reading up a little on it. I believe the fix is to add a 150 nf compensation capacitor to the circuit via a 4 pole rcd/rcbo.

    Just looking for a sanity check on this before proposing the fix to someone having the issue.


    ****, sunny ****.

    Post edited by allinthehead on


Comments

Advertisement